Need help with my camper van conversion solar/ battery issues
Newworldorder
Registered Users Posts: 2 ✭
hi everyone thanks for your help, I’ll get right to it.
I have a 2014 cargovan high roof that I converted and I went with a 400 watt solar system, 2x 6volt AGM batteries each having 190 amp hours.
I have a 3000 watt inverter.
One thing I need help with is I was running a 900watt oil heater and I could see on my inverter that it was drawing 960 watts.
So if I have a 190 amp hour battery bank I could run that for hours. 900 watts/ 120 = 7.5amps. So 190 /7.5 = a hella long time. I only had my heater working for 15 min and then a low battery voltage shut it down.
I had 2 fully charged 6volt batteries in series so 12v and I am so confused why it wouldn’t run much longer. So it went from 12.9 down fast to 11.5 volts. Then when there was no load it went back to 12.1 volts
I have a 2014 cargovan high roof that I converted and I went with a 400 watt solar system, 2x 6volt AGM batteries each having 190 amp hours.
I have a 3000 watt inverter.
One thing I need help with is I was running a 900watt oil heater and I could see on my inverter that it was drawing 960 watts.
So if I have a 190 amp hour battery bank I could run that for hours. 900 watts/ 120 = 7.5amps. So 190 /7.5 = a hella long time. I only had my heater working for 15 min and then a low battery voltage shut it down.
I had 2 fully charged 6volt batteries in series so 12v and I am so confused why it wouldn’t run much longer. So it went from 12.9 down fast to 11.5 volts. Then when there was no load it went back to 12.1 volts
Comments
-
960w@12v = ~80a, a significant load. On a 190ah bank, that's almost C/2, so dead batteries in a couple of hours or less. 1amp at 120v = 10a at 12v (plus inverter and wire losses).
You shouldn't regularly take the bank below ~50%. 190ah x 12v = 2280 watt-hours, so discharging to 50% would mean running the heater for an hour or so. Deep cycle battery ah ratings are normally a 20hr rate of discharge. At a 2hr rate, the effective capacity will be less than at 20hr.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Also, a 3000w inverter is pretty big for a 12v system. Many take a significant amount of power just staying "lit" or with small loads, so you may want to consider keeping it turned off unless needed for a (brief) large load.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
And batteries are very easily damaged by over discharging, setting discharged for days/weeks/months at time (say less than 75% state of charge), and under charging...
So, make sure you follow the battery mfg's charging instructions and get them back full so they don't get damaged.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Ok awesome, so it would not be 960/120. Since I have a 12v battery bank it would be 960/12? Ok
so I am planning on getting a tv so if that watts used to power it is 29 watts then 29/12=2.41 amp hours.
Thank u guys for your help eh. I very much appreciate it -
Run the TV. Forget the oil heater.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
And get an appropriately sized inverter for your new load profile.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Realistically, an inverter of a few hundred Watts is "appropriate" for the size battery bank you have... Just to give you an idea of the math:
- 190 AH * 12 volts = 2,280 Watt*Hours of storage
- Say 5 hours a night, for 2 nights (assuming bad weather and no solar charging), and 50% battery discharge (for longer life):
- 2,280 WH * 0.85 AC inverter eff * 1/2 days storage * 0.50 max discharge = 484.5 Watt average load
https://www.solar-electric.com/morningstar-si-300-115v-ul-inverter.html
And don't forget your solar harvest. Note the following assumes the solar panels are mounted flat to your roof and your are up towards Edmonton Alberta... If you tilt the array (especially in the winter), you will get a better harvest--Likewise if your camping/traveling is more to the south:
http://www.solarelectricityhandbook.com/solar-irradiance.htmlEdmonton
Measured in kWh/m2/day onto a horizontal surface:
Average Solar Insolation figures
More or less, less than 3 hours of sun per day (long term monthly averages), you probably need a generator to keep up (winter camping). For example, say March through September for dry camping:Jan Feb Mar Apr May Jun 0.79
1.70
3.15
4.56
5.32
5.66
Jul Aug Sep Oct Nov Dec 5.56
4.76
3.14
1.85
0.99
0.48
- 400 Watt array * 0.52 off grid system eff * 3.14 hours of sun per day ( Sept) = 653 Watt*Hours of average AC power today.
- 190 AH * 14.4 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 355 Watt array mominal
Of course, your personal power needs, when and where, any AC shore/genset charging, etc. will need to be taken into account. The above is just a stake in the ground for discussion.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Newworldorder said:Ok awesome, so it would not be 960/120. Since I have a 12v battery bank it would be 960/12? Ok
so I am planning on getting a tv so if that watts used to power it is 29 watts then 29/12=2.41 amp hours.
Thank u guys for your help eh. I very much appreciate it
Note that this isn't including the power used to run the inverter. They may have peak efficiency of ~85%, but can be much lower, especially running small loads on big inverters. The big inverter might take more than the TV just being on. If left on 24x7, it might use (eg) 30w x 24 = 720 watt-hours ÷ 12v = 60 amp hours.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed