690.9(C) Informational Note - Overcurrent protection
akloudless
Registered Users Posts: 2 ✭
Looking for clarification from the experts. Q: Is the NEC 2017 code stating that the DC OCPD requirements are now the same for an unground and grounded inverter system?
Scenario:
Module max fuse series rating = 15a
16 strings(Paralleling 2 strings) - 8 string combiner input - Single input mppt ungrounded inverter.
My approach to this in the past would have been, + & - 15a fused Y connectors to a + and - 30a fuse for each string in the combiner.
Is it now code to install while eliminating fusing on either the + or - side of the DC circuits?
Thoughts?
On certain grid tie inverters that are transformerless such as the Sunny Boy TL series you must have breakers on both the positive and negative p.v. wires as they are not referenced to ground. I do not know of any requirements for grounded systems to have breakers on both positive and negative wires.2 Classic 150, 2 Kid, 5 arrays 7.5 kw total 2ea. 2S6P Sharp NE-170/NE-165, 1ea. 12P Sanyo HIT 200, 2ea. 4/6P Sanyo HIT 200, MagnaSine MS4024AE, Exeltech XP-1100, 2 Banks L-16 battery, Rolls-Surette S-530 and Interstate Traction, Shunts with whizbangJr and Bogart Tri-Metric, iCharger i208B dc-dc buck/boost converter with BMS for small form lithium 8S 16650 or LiFePO4,
- 234 Forum & Website