An open battery in a string- risks
solapawa
Registered Users, Users Awaiting Email Confirmation Posts: 1 ✭
We got 64 batteries of 12v 100ah in a string. 1 of the batteries seem to have the total string voltage on its terminal as 400V. what could be the cause of this
Comments
-
At this point, it is a failed battery. And needs to be replaced. Having ~400-768 VDC across a failed battery is just asking for risk of fire (strike/sustain an arc across the failed internal connection).
Longer term, have you been monitoring the battery bank (volt meter across each cell/battery to make sure all of the neighboring batteries are working correctly? If flooded cell batteries, have you been checking the specific gravity of the cells ~once per month (and electrolyte levels)?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed