Sizing
plongson
Solar Expert Posts: 115 ✭✭
I'm pulling a dummy moment and can't quite figure what I need here...panel size and battery.
I have a little device I call a "call tower" on our ranch that is essentially is an internet gateway (1/2 mile away) to control an entry gate from the main house.
Total power consumption of all the components in the control box is 8a 12v 24/7.
I have a left over 50w panel from another project installed and a brand new automotive battery (I know...wrong battery for the application, but it was free) that was sitting around running everything now and it's worked great all summer.
Now the days are shorter and sometimes cloudy, the little inverter shuts off on low battery voltage and the system goes down.
Without getting too crazy, how much battery and how much panel would you recommend to stay above 50% DOD for say 48 hours??
Zip is 84721
Do you have a calculator?
THANKS!! Paul
I have a little device I call a "call tower" on our ranch that is essentially is an internet gateway (1/2 mile away) to control an entry gate from the main house.
Total power consumption of all the components in the control box is 8a 12v 24/7.
I have a left over 50w panel from another project installed and a brand new automotive battery (I know...wrong battery for the application, but it was free) that was sitting around running everything now and it's worked great all summer.
Now the days are shorter and sometimes cloudy, the little inverter shuts off on low battery voltage and the system goes down.
Without getting too crazy, how much battery and how much panel would you recommend to stay above 50% DOD for say 48 hours??
Zip is 84721
Do you have a calculator?
THANKS!! Paul
3500w solar, 800AH with Rolls Surrette, Magnum inverter, Midnite charge controller, Kubota 21kW diesel genset...private well...and just recently connected to city power for additional options...nice to have options
Comments
-
You could try pvwatts.nrel.gov for local solar resource at various tilts, etc.
8a x 48hrs = 384 amp-hours ÷ 50% DOD = 768ah battery. In most areas, to recharge to full or close to it the next reasonably sunny day, you'll likely want about 1/10 of capacity charge rate, so ~75ish amps. Assuming 75% of STC rating output, 75a ÷ 75% x 14.5v charging = 1450w array.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Paul,
Here is the "relatively" conservative rule of thumb design (just like designing for an off grid cabin or small home).
First, your daily energy usage:- 8 amps * 12 volts * 24 hours per day = 2,304 Watt*Hours per day
So, my first question--Is there any way of reducing energy usage? Assuming not, to continue...
Flooded Cell Lead Acid battery, generally the optimum design is 2 days of "no sun" storage, and 50% maximum discharge (for long battery life):- 2,304 WH per day * 2 days storage * 1/0.50 max discharge * 1/12 volt battery bank * 1/0.85 fudge factor (DC to DC converter, battery is actually at ~13 volts and 8.5 amps, other issues) = 904 AH battery bank @ 12 volts
Anyway, to continue on... Next to size the solar array. Two calcuations, one based on battery bank AH capacity... 5% to 13% rate of charge typical solar. For "full time" off grid power, highly suggest >10%+ rate of charge (unless you live in a really sunny region).- 904 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 851 Watt array minimum (weekend/summer)
- 904 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 1,702 Watt array nominal
- 904 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 2,213 Watt array "cost effective" maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlSaint George Utah
Measured in kWh/m2/day onto a solar panel set at a 38° angle:
Average Solar Insolation figures
(Optimal winter settings)
Worst case "average" month is January at 4.63 Hours of sun per day (long term average)...Jan Feb Mar Apr May Jun 4.63
4.76
5.84
5.85
5.65
5.61
Jul Aug Sep Oct Nov Dec 5.33
5.51
5.91
5.92
5.11
4.67
- 2,304 Watt*Hours per day * 1/0.52 average DC off grid system eff * 1/4.63 Hours of sun = 816 Watt array minimum (January)
- 816 Watt array * 1/0.50 base load "derating" = 1,632 Watt array
Now, you need to figure out what is important to you... A 2x larger array (1,632 Watt vs 816 Watt) is ~$800 more (plus racking)--That could also dramatically reduce your need for a genset during bad weather (and keep your battery bank healthier).
I would guess this is a WAY LARGER off grid $olar $ystem than you initially planned. Those 24x7 base loads (radios, refrigerators, servers, etc.) are real "killers" for off grid power systems. Does laying a 1/2 mile of direct burial cable (or strung on a set of power poles) look more interesting?
You can send 1 amp @ 240 VAC (240 Watts) a 1/2 mile on 12 AWG wire with 3.3% voltage drop. That is something like $1,500 worth of cable from Home Depot (~$487 per 1,000 feet of 12/2 cable).
https://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=5.211&voltage=240&phase=ac&noofconductor=1&distance=2500&distanceunit=feet&eres=1&x=0&y=0
Voltage drop: 7.94
Voltage drop percentage: 3.31%
Voltage at the end: 232.06
I will stop here and let you pick your jaw up off the floor... Please ask your questions and challenge my math/estimates.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I`m the only one thinking some peace of information is missing here ?His claiming that 50w panel with automobile battery is enough during the summer . However that 50w panel cant bring more than 4a/12/h and he has constant load of 8a/12v . No matter how you turn it he will run out of power on the second day at most .@plongson do you have this as backup and normally it takes power from the grid and you use charger (or until there is a grid the panel charge the battery) ?
-
Drakyla, welcome to the forum.
And, yes, you are correct. 8 amp load sounds like it might be an overestimate/not clear specifications. Or other things happening.
The 8 amps may be the maximum current (radio transceiver + operating gate)... And the rest of the time just the radio transceiver at closer to 0.5 to 1.0 amps or so...
Plongson, have you measured the average current and/or actual AH used per day?
https://www.amazon.com/gp/product/B019CY4FB4 (DC Current Clamp DMM)
https://www.rc-electronics-usa.com/ (DC AH/WH meter)
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Holy crap guys! Sorry for the typo! The draw is 8 watts, not amps. What's that... like .66amps? Shucks, so sorry!3500w solar, 800AH with Rolls Surrette, Magnum inverter, Midnite charge controller, Kubota 21kW diesel genset...private well...and just recently connected to city power for additional options...nice to have options
-
There is a ton of great reading here and I need to absorb it. Thanks for all the feedback.3500w solar, 800AH with Rolls Surrette, Magnum inverter, Midnite charge controller, Kubota 21kW diesel genset...private well...and just recently connected to city power for additional options...nice to have options
-
Paul,
Try again with 8 Watt load:
First, your daily energy usage:- 8 Watts * 24 hours per day = 192 Watt*Hours per day
Flooded Cell Lead Acid battery, generally the optimum design is 2 days of "no sun" storage, and 50% maximum discharge (for long battery life):- 192 WH per day * 2 days storage * 1/0.50 max discharge * 1/12 volt battery bank = 64 AH battery bank @ 12 volts
- 64 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 60 Watt array minimum (weekend/summer)
- 64 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 121 Watt array nominal
- 64 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 157 Watt array "cost effective" maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlSaint George Utah
Measured in kWh/m2/day onto a solar panel set at a 38° angle:
Average Solar Insolation figures
(Optimal winter settings)
Worst case "average" month is January at 4.63 Hours of sun per day (long term average)...Jan Feb Mar Apr May Jun 4.63
4.76
5.84
5.85
5.65
5.61
Jul Aug Sep Oct Nov Dec 5.33
5.51
5.91
5.92
5.11
4.67
- 192 Watt*Hours per day * 1/0.61 average DC off grid system eff * 1/4.63 Hours of sun = 68 Watt array minimum (January)
- 68 Watt array * 1/0.50 base load "derating" = 136 Watt array
That is a much more reasonable system...
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Bill!! and all others...AMAZING HELP! THANKS so much for the feedback. I'm gonna go back and fully review the help. GREAT SITE! and great members and support.
Paul3500w solar, 800AH with Rolls Surrette, Magnum inverter, Midnite charge controller, Kubota 21kW diesel genset...private well...and just recently connected to city power for additional options...nice to have options -
Hey all...here's a couple of pictures of the setup. Pictures are always good, huh! Here you see the layout, the "cell tower" and the gate. We're all off grid, been so for about 8 years, and love it. look close and you can see the cell tower just above the right gabbion. I use all Ubiquiti enterprise grade components and it's all controlled via the internet security system (along with gate openers in the vehicles)...The Ubiquiti NanoBeam that shoots the signal from the house will actually transmit up to 15km. This is really cool stuff...Oh, the battery setup in the chicken shirt storage box was just for demo purposes...Much more permanent now.
Ubiuiti
3500w solar, 800AH with Rolls Surrette, Magnum inverter, Midnite charge controller, Kubota 21kW diesel genset...private well...and just recently connected to city power for additional options...nice to have options -
Neat. Always wanted a Ubiquiti system, but never really had a need for such equipment.
Depending on your power needs, up sizing the system with a pair of 6 volt @ 200 AH batteries would give you closer to 6 days of storage with relatively cheap and rugged golf cart batteries.
And if you ever needed some AC power, a 300 Watt Morningstar true sine wave inverter could bea nice option.
Of course, larger battery bank needs more solar panels...
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed