gfp homemade
ws9876
ws9876 Solar Expert Posts: 453 ✭✭✭
If you want to make a 60 amp DC GFP from pieces on the cheap what would you need??
  • bill von novak
    bill von novak Solar Expert Posts: 892 ✭✭✭✭
    You would gang two breakers together.  One, the GFI breaker, would go from - to ground (usually) and the other, the load breaker, would protect the circuit (i.e. the array.)
    For example, if you could find a 1/4 amp breaker with the same rating and series as the 60 amp breaker, you'd gang them together.  Then if more that 1/4 amp of ground fault current flowed, you'd trip both breakers.
    Of course this doesn't work unless you can common ground and -.  Nor is it floating; you can't use it on transformerless inverters, for example.
    BB. Super Moderators, Administrators Posts: 33,734 admin
    And you would "gang" the breakers together (some breakers use a pin between the two handles, others use a clip that covers the two handles--Look at how their 240 Volt ganged breakers link the handles).
    Also, the ground trip breaker could be 1 Amp Rated....
    If you wanted to break two legs of power, then one 1 amp breaker+2x other 20-80 amp breakers (typical--depending on desired current rating)
  • ws9876
    so a 1 amp DC regular breaker physically tied to a 60 amp DC breaker, Midnite Solar?? That would be about 22 dollars,no?better than 50 dollars,yes??
  • bill von novak
    Well, they have to be gangable (which means same dimensions, calibrated trip force etc.)  You can't just get some cheap 1 amp breaker, put it next to a Midnite 60 amp DC breaker and have it work.