Sunfrost RF-16 Fusing.

RF-16 refrigerator freezer has compressor starting amps of 7.5 @ 24vdc. What is the proper fuse amperage? Right now it has a 15 amp Bussman auto blade type fuse from previous owner so I am making sure this is within acceptable limits.
Comments
I am not a fan of automotive blade fuses. Some holders have overheated and just about caught fire when running well below rated current.
As long as the fuse and holder look good (no signs of getting hot), then it is probably fine for now (holder not near any flammable materials).
Longer term, you may want to replace witha good quality breaker or fuse holder assembly.
Bill
15 amps should be good. One fuse/breaker per 14 awg minimum wire to major load. Keeping separate branch circuits is nice. If one were to blow, the others will still work.
Bill