Outback fleximax 80
gav
Registered Users Posts: 10 ✭✭
Hi again can u lower the target voltage down for the bulk charging on the outback 80?
Comments
-
yep .. its called the absorb voltage2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
-
Thanks so it won’t go above absorb voltage point when in bulk charge?
-
When it gets to the absorb voltage setpoint (temp compensated), it will transition out of bulk to absorb. In absorb, voltage is held constant at the setpoint, and current drops off as the battery get closer to fill.
The bulk part of the cycle is defined as a constant current (limited by available solar or a controller setting) with voltage rising up to the absorb setting, so no, voltage shouldn't go above that in bulk.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Note that some controllers have a "bulk" and an "absorb" setting... I would presume that it could working something like--Charge to Bulk (current limited) to 14.9 volts. When Bulk is reached, to to absorb setting and charge at 14.7 amps for X hours (or until ~1-2% rate of charge is reached---Tail of charging current). Others just have an Absorb setpoint (battery is "bulk" charged to setpoint, and then held for X hours, or other like 2% rate of charge, etc.).
You will sometimes see separate Bulk and Absorb set points and current/voltage setpoints for batteries (there is a whole industry and tech speak for battery (DIN Euro Standards) charging that I am not familiar with at all). For example:
https://en.wikipedia.org/wiki/IUoU_battery_charging
In general, most battery Mfg. and tech talk assumes you have 24/7 (24 hours a day, 7 days a week) AC mains (and backup AC gensets) so that you can charge according to their "optimum" requirements.
With Solar Energy, the mapping of solar energy to batteries with a side of loads--The charging is rarely "optimum". And we fall back to "the way it has always been done" with solar...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Hi Gav,
I also have a Outback FM80. Basically (as has been said in different ways* in this thread) there is no "bulk" voltage to set. The controller will use MPPT to efficiently bulk charge your batteries in the morning, starting when the sun rises. It depends on the insolation, but typically I see bulk voltage appreciatively rise around 10:30am, a half hour or so before my system goes into absorb.
* eg: The bulk part of the cycle is defined as a constant current (limited by available solar or a controller setting) with voltage rising up to the absorb setting
Outback Flexpower 1 (FM80, VFX3048E-230v, Mate, FlexNetDC) 2,730watts of "Grid-type" PV, 370 AmpHrs Trojan RE-B's, Honda 2000 watt genny, 100% off grid.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed