Load amps vs battery charging amps
mountainman
Registered Users Posts: 442 ✭✭
With 400 watt array on pwm Why is it that I get 16 peak amps charging a 50% soc battery bank. and with a full battery 22-24 amp peaks running an inverted 250 watt heat light.
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
What is the absorb charging voltage when 16 amps and 50% soc?
What is the battery bank ah capacity? How do you know 50% soc?
If the charging voltage is around 14.75 volts and 16 amps (flooded cell lead acid), then possibly a sulfated battery.
1.172 sg 50% 208 amp hr 2 6 volt new batteries. 12.6 volts around 200 watts (14.1 308 watts 250 watt load) fla batt2kw array 6 345 q cells make sky blue 60 cc
18 amp accusense charger. 3650 champion -
Charging at 12.6 volts at the battery and 16 Amp in full near noontime sun?
I am not sure why. If you get 22+ amps from the charge controller at 14.1 volts under same sun conditions running a load, then charging should be the same maximum current from controller.
I'm not sure either. I'm assuming the current is being measured at a shunt on the controller output to battery? Voltage measured at the battery? So voltage at the battery posts goes up from 12.6 to 14.1 when you turn on the load? Does it go back down to 12.6 when you turn the load off, and back to 14.1 when you turn it back on (and so on. In other words, is the observation repeatable)?Off-grid.
I'm using rc meters on the battery 1 from controller cables to batt and 1 from batt to loads and yes it goes back down when I turn off the load at solar noon. My thoughts were internal resistance of the battery. But I'm new to solar battery charging.2kw array 6 345 q cells make sky blue 60 cc
Really need to know battery terminal voltage(s) and current flowing into the battery... I.e., was it 12.x volts @ 16 amps, or 14.xx volts @ 16 amps and 50% state of charge.
I am not quite sure I am clear on what is happening.