#4 wire splicer?
Seanadirondacks
Registered Users Posts: 20 ✭✭
Would these aluminum splicers be good for #4 wire with max 60 amps? Thanks.
Hi Sean,
The pic or Link did not make ..
What you are looking for on these types of devices is a marking that says: Cu-Al, or Al. There may well be a specified range of wire gauges that the device will accept.
Always use an anti-ox type compound, after burnishing the Al conductors, like NoAlOx (r).
FWIW, Vic
> @Vic said:
> Hi Sean,
> FWIW, Vic
Link is up now. Looks like ive got the right ones. Thanks for the info and advice! -
Sean, YES, those look fine. Thanks for the pic. VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
- 234 Forum & Website