Hello,
The Suresine 115 volt inverter is rated at 300 watts with 600 watts surge capacity. According to the owners manual Morningstar states that a 100 amp fuse should be used on the DC side. I am under the impression that inverter fuses should be sized at 125% of the surge capacity, or 60 amps in this case. Can anybody explain why the larger fuse is recommended? BTW I have emailed Morningstar. Thanks, Mark
The Suresine 115 volt inverter is rated at 300 watts with 600 watts surge capacity. According to the owners manual Morningstar states that a 100 amp fuse should be used on the DC side. I am under the impression that inverter fuses should be sized at 125% of the surge capacity, or 60 amps in this case. Can anybody explain why the larger fuse is recommended? BTW I have emailed Morningstar. Thanks, Mark
Comments
-
Re: Fuse size
If you assume the inverter can operate down to 10.5 volts, is 80% efficient and the fuse should be sized to 125% of load:
600 watts 1/10.5v * 1/80% * 125% = 89.3 amps...
Round up to next standard size ~100 amps to also account for some other unknowns (like voltage drops through wiring and fuse block).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
-
Re: Fuse size
Bill,
Thanks for the input.......I've intended to follow the Morningstar recommendations from the start but like to have an explanation/understanding of the fuse ratings compared to the info I have read. Regards! -
Re: Fuse size
Mark,
I believe that I owe you an apology. I failed to see in your original post that you were inquiring about the rationale for a 100 A fuse, and I thought you were asking about what the fuse size should be.
The NEC Section 690.8 establishes the process for determining the rating for an inverter’s input fuse. The basic formula is [Rated Inverter Power / (Lowest Input Voltage x Efficiency)] x 125%. For your SureSine inverter, the calculation would look like this: [300 W / (10 V x 84%)] x 125% = 35.7 A. The next standard size fuse is 40 A.
WTF?? Well, the inverter contains three 40 A fuses. See manual page 13. I haven’t seen the schematic, so I don’t know why there are three fuses.
I suspect that Morningstar’s recommendation for an external 100 A fuse is some combination of a catastrophe fuse as well as protection for the inverter for when it’s operating at peak power (600 W, 10 minute limit; 10.5 V min due to 4 minute limit). For this scenario, the calculation would look like this: [600 W / (10.5 V x 70%)] x 125% = ~102 A. All things considered, a fuse rated for 100 A is probably “close enough”.
The low voltage values and the efficiency numbers were taken from the inverter’s data sheet. See: http://www.morningstarcorp.com/products/SureSine/info/SI_DataSheet.pdf
Regards,
Jim / crewzer -
Re: Fuse size
JIm / crewzer,
Thanks for the response and data. The NEC formula is certainly more precise, so 100 amps it is. Mark
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed