Max panel wattage per battery
LPhillippi
Registered Users Posts: 4 ✭
The batteries I have are sufficient for overnight use. I'd like to increase the number of panels but I don't want to add batteries.
I'm using 8 Crown Batteries rated at 260AH each. The guy at the battery store said the max charge rate is approx 1/10 of the 20 hr AH rating.
I'm estimating the max wattage per battery to be 26a x 13.9v=361watts per battery. 8 batteries x 361 watts = 2888 watts max (actual)
My panels operate at a max of about 80% of the rated power so 2888 / .8 = 3610 watts max (panel rating)
Is there a way to prevent the batteries from being charged to quickly if I add more than 3600 watts in panels?
I'm using 8 Crown Batteries rated at 260AH each. The guy at the battery store said the max charge rate is approx 1/10 of the 20 hr AH rating.
I'm estimating the max wattage per battery to be 26a x 13.9v=361watts per battery. 8 batteries x 361 watts = 2888 watts max (actual)
My panels operate at a max of about 80% of the rated power so 2888 / .8 = 3610 watts max (panel rating)
Is there a way to prevent the batteries from being charged to quickly if I add more than 3600 watts in panels?
Comments
-
You have to look up the battery specifications for the exact model/set you got... However, 13% rate of charge should be OK:
- 8x 260 AH * 14.5 volts charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 5,092 Watt array "cost effective" maximum
The Midnite Classic family of MPPT charge controllers does have the "Wizbang Jr." battery shunt, that when connected to the charge controller can limit charging current directly to the battery bank (i.e., you can have other daytime loads consuming power, but be part of the battery charging current).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 8x 260 AH * 14.5 volts charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 5,092 Watt array "cost effective" maximum
-
Thanks for the feedback. Very helpful. I wasn't entirely certain on how to perform the calculation.
I'm using an Outback FM-80 with battery temp sensor. -
You should be fine--Assuming those are 12 volt @ 260 AH batteries, the math should be OK...
If you wish to limit charging current, many MPPT type charge controllers (including Outback) can be programmed for less than full output current.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:You should be fine--Assuming those are 12 volt @ 260 AH batteries, the math should be OK...
If you wish to limit charging current, many MPPT type charge controllers (including Outback) can be programmed for less than full output current.
-Bill
Thanks.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed