3 X 250w panels help
Please give us a little more information on what brands and models of components you are using. If you are using three 12V solar panels in series you have a 36 volt input. Most controllers would have no problem outputting 24V.
Hello alovella, welcome to the Forum.
Almost all 250 Watt PVs are 60-cell modules. They have a Vmp of around 30 volts. They are generally designed for use on Grid-connected systems, and are neither 12 V, nor 24 V PVs.
With a real MPPT Charge Controller (CC), these can work fine on a 12 V system (system voltage is determined by the battery and inverter voltage.
So, you have a 12 V inverter, so your two 12 V batteries would need to wired in parallel.
At 12 V, the "400 watt solar" rating of the CC might mean that it could be rated at about 30 Amps output maximum. The 12/24 V notation might mean that having PVs rated at about 30 V might well be OK, if the CC is really an MPPT type.
On a 12 V system, with three 60-cell PVs, you would probably really need to wire the PVs in parallel, with circuit protection (circuit breaker or fuse) on each of the PV. Customarily this circuit protection would be in a Combiner box, without knowing the specs on the Hybrid "controller"
My opinions, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.