Wiring Inverter
Swhitney
Registered Users Posts: 3 ✭
I have an older 91 class A RV which never had an inverter option. I would like to get something to go off grid but not sure the best route is for my application.
I am looking to wire an inverter to the system, does anyone have advice/diagrams on how to do this? It would be really nice to flip a switch from inside the RV to turn everything on except AC of course.
Thank you,
Sean
Thank you,
Sean
Welcome Sean, first we need to know about the loads you want to power and the amount of time they will run and also if you will have more than 1 running at the same time..?
My idea is to run a 1300 watt microwave and a 1500 watt keurig for short stints of course these would not be ran at the same time.
I was looking at this one.
https://www.amazon.com/PowerTech-Technology-Terminals-Protection-PS1004/dp/B0131PZ9J2/ref=sr_1_2?ie=UTF8&qid=1476834062&sr=8-2&keywords=inverter+3000+w
What about lights and a water pump?
The cheapest and most effective way of powering those 2 power mongers IMO is a 2000W inverter type generator like a Honda... powering those loads with a 12 V setup is NOT recommended due to the massive Amperage draw from the battery bank. You might want to consider a 24 Volt bank at least or 48 volt. Just do the math and you will see the cost of wire will probably shock you...
The loads are high but for only a short periods of time, which a battery can do. A generator isn't as practical for night time when I just want to kick on the TV or heat up a cup of water.
When wiring an inverter I can keep it extremely close to the batteries which lowers cost of wire. The 120 side could be an extension cord or insulated house hold wire that has a 20 amp plug at the end.
Remember that some batteries take a serious dip in voltage under high loads, others not so much. For example:
- One type of 100 ah battery at 60% state of charge will drop to 11.8v with a 125 amp load. When that battery reaches 50% state of charge, the reading will be 11.4v.
- Another battery of a different type under the same conditions/load might be closer to 10.9v and 10.5v respectively.
Also, take into account that as the battery voltage falls, the current will increase because the inverter is pulling a constant wattage - compounding the problem.
Your approach is quite doable, if you plan for the above factors. Check the spec's for your battery.
Marc
- 227 Forum & Website
- 618 Discussion Forums/Café