Please Recommend a Charge Controller for my Application
PlantGuy
Registered Users Posts: 4 ✭
I need a charge controller that I can set to only power the load during daylight hours. All of the ones I've seen (even the ones with "timer capability") are designed to mainly power the load at night or all of the time. For my application, I don't need the load powered at night. To keep the aesthetic footprint to a minimum I'm only using a 10W panel and a 7AH battery. This is a 12V system. The battery will power the load most of the night, but the next day the panel has to charge it for about 4 hours before the load side is active again, and that is the primary time when I really need the system to be working.
Can anyone recommend a charge controller that could be set to only power the load side during daylight hours? Thanks.
Can anyone recommend a charge controller that could be set to only power the load side during daylight hours? Thanks.
Tagged:
Comments
-
I am a little confused... Will the 10 Watt panel also be charging the 7 AH battery during the daytime?
Do you need the charge controller (or daylight switch) to specifically turn the load "on and off" during daylight hours?
It sounds like you really want to run the load 24 hours per day, and the solar charger to both "run the load" and charge the battery (at the same time) during the day.
If the second is true, any solar charge controller will do that just fine. Assuming your load energy (amp*hours per day) is capable of being powered by a 10 watt panel--Or roughly 9 months of the year in a sunny climate:- 10 watts / 17.5 volts Vmp = ~0.57 Amp Imp
- 0.57 Amps * 0.80 battery efficiency * 4.0 hours of average sun minimum per day = ~1.8 Amp*Hours per day maximum load
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I only need power to my device during the day. I'd like to have the load either automatically switch off at the end of the day, or be able to set up a window of time during the day when it would be on. 7:00 am till 7:00 pm for example. Yes the panel will be charging the battery during the daytime. I am located in Wichita Falls in north central Texas near the Oklahoma border. The load being powered only consumes about 200 mW, so the 10W panel has no problem in both powering it and charging the battery during the day. The problem is that without a way to automatically turn off the load at dark, the battery gets drained during the night. This system needs to run year round. The most important time frame to have power is from 7:00 am to 4:00 pm. I am currently using one of the inexpensive CMTP02-10A charge controllers. Thanks for your help.
-
Correction. I meant to say that the load only consumes 200 mA.
-
This is not a cheap solution, but it is a battery backed timer with ability to run AC or DC circuits:
http://www.solar-electric.com/fldctico.html
You can probably find something cheaper on EBay or other import site. Amazon has (it appears) a bunch:
https://www.amazon.com/MISOL-Controller-display-program-programmable/dp/B0090MTLFO
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Great idea! I had considered using a timer, but I'd always assumed that it would consume as much current as the load. This looks very promising. I'm going to order a couple of these:
https://www.amazon.com/DBPOWER-CN101-Digital-Programmable-17-times/dp/B00H4XP7QS/ref=pd_sim_60_3?ie=UTF8&dpID=411jYI6LX9L&dpSrc=sims&preST=_AC_UL160_SR160,160_&psc=1&refRID=N5B58G7NRBFPV964H8D7
I'll let you know how it works out. Thanks for your help.
-Benny
-
You are very welcome... By the way, watch the energy usage/battery state of charge:
- 0.2 amps * 12 hours per day = 2.4 Amp*Hours per day
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I just installed a new generation Intermatic electronic timer on a water pressure tank air pump.
They make several comprehensive digital timer models.
Ranch Off Grid System & Custom Home: 2 x pair stacked Schneider XW 5548+ Plus inverters (4), 2 x Schneider MPPT 80-600 Charge Controllers, 2 Xanbus AGS Generator Start and Air Extraction System Controllers, 64 Trojan L16 REB 6v 375 AH Flooded Cel Batteries w/Water Miser Caps, 44 x 185 Sharp Solar Panels, Cummins Onan RS20 KW Propane Water Cooled Genset, ICF Custom House Construction, all appliances, Central A/C, 2 x High Efficiency Variable Speed three ton Central A/C 220v compressors, 2 x Propane furnaces, 2 x Variable Speed Air Handlers, 2 x HD WiFi HVAC Zoned System Controllers -
One of the solar controllers I'm using is a MorningStar Sunlight-10. Regulates up to 10 Amps (120 Watts). It has a built-in 10A relay to control lights, with adjustable settings. What I've done is added an external 40A relay. I can then use this to turn on lights dusk to dawn, and turn off loads during that period. When the sun comes up, the relay drops out, turning off the lights, and operating the daytime loads.
Never need to adjust for time of year, no clocks to set. It constantly measures the output of the solar panel, and adds a 10 minute dwell time, it knows when it's daytime or nighttime. Very slick.
-
Old thread, but what about a simple photo cell, to turn off the load when there is no light?
Tony -
Photo cells pass current where there is light--So you need a relay (or electronics) to reverse the polarity ('on' when dark).
Could also get a small solar cell and a relay (relay or transistor/fet/etc. holds open when sun is up, closes when sun sets)....
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed