How to size my breakers?
bc buck
Registered Users Posts: 59 ✭✭
I need to know what size breakers to order. I will be running 10 ga solar tray conductor from panels to CC. Then 6 ga THHN from 40 amp CC to battery bank. Was thinking 30a from panels and 50a from CC. Does this sound about right?
Comments
-
Can't answer your questions without more info... size of array and what controller? Also, how long are the runs from array to CC and from CC to battery?
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
What ever you think the max continuous current is, then multiply by 1.25x for breaker and wiring size, as a start.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
3 panels in series=450 w, 68 volts, 8.33 amps.
10 ga run to CC 25'
CC=Morningstar PS-MPPT-40 amp
6 ga out of CC 4' to battery . This is where I was thinking a 50 amp breaker.
A 30 amp breaker would protect the 10 ga conductor going to the CC but on the panel label says 15 A breaker. If you where to run these panels parallel you would need a fuse or breaker for each panel.
-
For you solar panels--You don't need a circuit breaker (only need breakers when you have 3 or more panel/panel strings in parallel, one 15 amp breaker per parallel string). In your case, a single 15 amp breaker is nice for a on/off switch (when you want to service the array/charge controller).
What battery bank voltage are you running (12/24/48 volts)?
What size Amp*Hour battery bank do you have?
Do you plan on adding more solar panels in the future?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
bc buck said:3 panels in series=450 w, 68 volts, 8.33 amps.
I think the 68 volts is Voc. You should use Vmp for your calculations. Your strings probably have a Vmp = 54 (3 panels in series).
You do not need a circuit breaker for safety between the array and the controller, but I recommend one because it will serve as the switch that you do need. A 15 amp breaker will serve your needs. 10 gauge is adequate.
Between the controller and the battery you must have a breaker for safety. You didn't mention your battery voltage, so I cannot do the calculations for that wire or breaker. A 12 volt system would need a larger breaker than a 24 volt system. 4 ft of 6 gauge wire and a 50 amp breaker will be adequate for a 12 volt system.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Battery bank is 260 AH at 12 volts and with this application I see no more panels added.
-
bc buck said:Battery bank is 260 AH at 12 volts and with this application I see no more panels added.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
vtmaps Posts You will have a charge rate of almost 10%. Sounds like a well balanced system.
Thanks to every one on this forum.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed