On the Evergreen panels the naws site says do not use for battery systems:
See below:
Evergreen ES-190 Solar Panel
For Grid Tie Systems
26.7 Volts @ 7.12 Amps
Not for 24 Volt battery
The Vmp seems ok for a mpp controller. Why not for battery systems?
I am using 12ea 95 Photowatt panels with a similar Vmp and a BSBP50 charge controller in an off-grid system that has been operating for several years, but would like to add panels and the PW panels are no longer available. The B grade evergreen 170,180 and 190 watt panels are pretty inexpensive.
See below:
Evergreen ES-190 Solar Panel
For Grid Tie Systems
26.7 Volts @ 7.12 Amps
Not for 24 Volt battery
The Vmp seems ok for a mpp controller. Why not for battery systems?
I am using 12ea 95 Photowatt panels with a similar Vmp and a BSBP50 charge controller in an off-grid system that has been operating for several years, but would like to add panels and the PW panels are no longer available. The B grade evergreen 170,180 and 190 watt panels are pretty inexpensive.
Comments
-
Re: Evergreen ES series
I would say that they mean it's not for charging 24 volt batteries, as the voltage is too low for that job, and not for 12 volt batteries without a MPPT controller, as the voltage is too high, therefore low amps, wasting power. However, with MPPT such as the MX-60 they would be perfect for a 12 volt battery system.
Wayne -
Re: Evergreen ES series
Would they not be OK if wired in series to over 53.4 volts then through a MX60 for 24 volt system. ? Or would this waste energy ? -
Re: Evergreen ES series
Short answer no... This is one of the reasons that MPPT controllers are so neat... They are much more flexible and work to spec. over a wide range of conditions (and much better that "simple" PWM controller--for larger systems >~200-400 watts typically)...
You just need to go through the calculations to make sure that min/max voltages and currents are within requirements (as seen on other threads here--not always a trivial exercise).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Evergreen ES series
I think Bill means - - no, it would not be a waste of energy - - if you're using an MPPT controller.
In series, charging 24 volt battery through an MX-60, they should be the cats meow -
Re: Evergreen ES series
Maybe I should have invested a few more $$$ in my sentence... Wayne was much more eloquent than I.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Evergreen ES series
I understand now. The Vmp drops to 23.3 at "normal" operating temperatures:
Nominal Operating Cell
Temperature Conditions (NOCT)4
P m p (W) 129.0 136.7 140.1
Vm p (V) 23.3 23.8 23.9
I m p (A) 5.53 5.75 5.86
Voc (V) 29.8 30.3 30.5
Isc (A) 6.20 6.46 6.59
TNOCT (ºC) 45.9 45.9 45.9 -
Re: Evergreen ES series
Actually, assuming a 95F day and temperature rise in still air, the Vmp could be down towards 21.5 volts DC for that panel...
Xantrex (array sizing calculator) appears to assume, roughly, a 40C (73F) rise on a hot day--and from my measurements of operating voltage for my array--I would have to guess they are pretty close. They predicted my operating voltage on a hot day to within a 0.5 volt...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed