fuses?

fauss
Registered Users Posts: 26 ✭✭
When and where do you use fuses? I'll have 2x100 watt 12v panels a 40 amp mppt with 2x6v golf cart batteries. Off grid shed.
So from my understanding I would need one on the positive in between the charge controller and battery. Since my mppt is a 40 amp would I want a fuse smaller than that?30amp? And what about the load side? Still a newbie.
So from my understanding I would need one on the positive in between the charge controller and battery. Since my mppt is a 40 amp would I want a fuse smaller than that?30amp? And what about the load side? Still a newbie.
Comments
-
At the charge controller consider using Midnite MNEPV breakers. They come in many sizes and mount to a DIN rail. For convenience one on the incoming side (from PV array to charge controller) and one on the output side to batteries is good. Most controllers require connection to the batteries first and then to the PV. using breakers means an easy means of making / breaking the circuit.
Breakers / fuses are there to protect wiring from overloads. So with a 40 amp controller capcity you would size the wire for that amperage and use a 40 amp for the protection device. (MNEPV breakers are rated to full load rating unlike some.)
The breaker / fuse between charge controller and batteries should be as close as possible to the batteries. But not in the same box / enclosure as the batteries.
Do yourself a favor and also install good lightning surge protection, like the Midnite SPD.
Load wiring should also incorporate fuses / breakers.
Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
As per Mt Don, use some Midnite breakers and boxes.
Regarding the breaker between the battery and controller: with a 40 amp controller you should use a 50 amp breaker and cable capable of handling 50 amps... that would be at least #6 copper. The controller's output should not ever be able to trip the breaker.
In the event that the controller faults, it could be a direct short circuit across the battery. That is why you have the breaker.
Everything, without exception, that connects to the battery must have a fuse or circuit breaker.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
For 2 100 watt panels I would use a 20 amp fuse from the panel to the charge controller, because each panel is only going to make around 5 amps. Then put a 30 to 40 amp fuse from the charge controller to the battery since the MPPT will bump up the amps going out to the batteries.
I fuse for the panels I have, not the capacity of the charge controller, but that's just me.
Yeah, use at least 6ga wire to the battery.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Thanks for the responses. More questions. On my panels it says Max Series Fuse Rating. So do use a 15 amp fuse for each or on both after I run them in parallel? Then use a 50 amp fuse on 6 gauge wire close to the battery. (is 4 gauge better?) Also is this the fuse I want going to the battery?http://www.midnitesolar.com/productPhoto.php?product_ID=217&productCatName=Breakers&productCat_ID=16&sortOrder=20&act=p
-
fauss said:Thanks for the responses. More questions. On my panels it says Max Series Fuse Rating. So do use a 15 amp fuse for each or on both after I run them in parallel?fauss said:Then use a 50 amp fuse on 6 gauge wire close to the battery. (is 4 gauge better?) Also is this the fuse I want going to the battery?http://www.midnitesolar.com/productPhoto.php?product_ID=217&productCatName=Breakers&productCat_ID=16&sortOrder=20&act=p
The breaker you show a link for is a din rail polarized breaker. Consider one of these:
http://www.solar-electric.com/installation-parts-and-equipment/midnite/cipr1/stfubr1/pamodccibr.html
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
OK thanks vtmaps I'll pick up on of those. And I'll use as big of wire as my charge controller port can handle. Where do you buy your wire and connectors? Online or at a Lowe's or home depot ?
Different topic. I'll have 2 6v 208ah GC batteries. What kind of charger/tender would you suggest? Sorry for all the random question. -
Will 4ga even fit in the charge controller?
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
oil pan 4 said:Will 4ga even fit in the charge controller?
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
What about between the batteries
-
fauss said:What about between the batteries
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 612 Discussion Forums/Café
- 305 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed