controller amps max
ws9876
Solar Expert Posts: 453 ✭✭✭
If a KID controller has a 30 amp max and you have 48v solar array then you have about 1500 watts max,no???? So if you have your load output to an inverter of 3000 watts you still cant draw more than 1500 watts..??
Are you going from the Kid to the inverter without a battery? I assume that you have a battery and that you might be able to draw 3000 watts for awhile (depending on the battery).
ws9876 said:If a KID controller has a 30 amp max and you have 48v solar array then you have about 1500 watts max,no???? So if you have your load output to an inverter of 3000 watts you still cant draw more than 1500 watts..??
ws..,IMO, it is not a good idea to connect an inverter to the Load terminals of any CC. Most inverters have fairly large-value capacitors on the DC input. When this load is switched on, form the output of the KID, the large inrush current can cause the an over current condition, and could possibly blow the output fuse in the KID.
Also, the relatively lowi-ish current rating of the KID's Load circuit will probably limit the Surge rating of the inverter.
... My read on things, FWIW. Vic
with a battery bank 48v
the KID manual shows the load coming from the CC. It shows a light bulb as a representation. -
if you didnt connect the inverter to the LOAD then where would you connect the inverter??
solved the inverter always goes directly off the batt terminals..
Well to a CB or fuse then battery.Off grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat
Yes, the CC and inverter connect together and then to the battery, BUT, it is good if there is little as possible cable from batteries to the inverter and CC. OR, very little cable from CC to battery and maybe more length to the inverter. This helps to keep the inverter drawing more from the battery and less from the charge controller itself... Especially if the CC's current limit might be a bit slow to respond to the inverter's need for surge current.
For instance, if you had say, 50 feet of cable from battery terminals to the CC and inverter, connected both at that 50 feet away point, then the battery would be so decoupled from the inverter and battery that all of the surge and higher frequency current that the inverter needs to operate would be coming from the CC. When battery cable is short, the battery makes a GREAT low resistance feed point and filter so the inverter and CC have less "talking" with each other, current wise. They both have to talk to the battery to give and receive their power and current. Sort of like that anyway.
Glad I read this thread. I didn't know the inverter connects to the battery AND CC. Makes sense now. Would you put a low voltage cut off in between the inverter and battery? I assume most cc's have one...right?
fauss said:Would you put a low voltage cut off in between the inverter and battery?fauss said:I assume most cc's have one...right?
- 654 Solar Water Pumping