Using A Starting Battery With Deep Cycle To Start A Refrigerator
solarpowerwindandstu
Registered Users Posts: 5 ✭✭
Hi i'm looking for some advice on a battery system, can a deep cycle/starting battery be used in a system of 12, 6 volt golf cart batteries? Would the starting battery make it so it's easier on the main batteries for starting a compressor if i hook the inverter running the refrigerator to the starting battery?
Welcome to the forum,
If you have 12 golfcart batteries in a 12 volt system, that means you have 6 parallel strings. That is an unstable and unworkable design for a system that cycles frequently. If you need that much storage you should be using a single string of 2 volt batteries, or raise your system voltage so you can have fewer parallel strings.
A starting battery is not the solution and may actually make your problems worse.
btw, how have you interconnected the batteries? When you have that many strings you should use a bus bar to combine the batteries... except that you shouldn't have parallel batteries to begin with.
One type of battery will try to discharge through the other.
Don't do it.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
vtmaps said:Welcome to the forum,
oil pan 4 said:One type of battery will try to discharge through the other.
Don't do it. -
solarpowerwindandstu said:oil pan 4 said:One type of battery will try to discharge through the other.
Don't do it.
If one cell in one string develops shorted plates, you can go into thermal runaway and have a fire. To prevent that, you must have a fuse or circuit breaker in each string of batteries. This adds more potential points of failure and makes it even more difficult to keep the batteries balanced.
Even if you had impossibly identical batteries, and impossibly perfect wiring, parallel batteries are still unstable. If one battery is slightly warmer than another (inevitable), it will draw more of the charging current. That will make it warmer which will allow it to take more current which will make it warmer which will make it take more current which will make it warmer... that's called positive feedback... sort of like balancing a pencil on its point. Mathematically the pencil is balanced in equilibrium, but it is an unstable equilibrium. In the real world it will lean infinitesimally to one direction, and then the forces on it pull it further in that direction.
vtmaps said:solarpowerwindandstu said:oil pan 4 said:One type of battery will try to discharge through the other.
Don't do it.
--vtMaps -
solarpowerwindandstu said:maybe have 6 different systems that have separate panels so the batteries are apart, would that work? then I can put in a voltage controlled relay so when 1 battery gets to 50% it will switch the inverter to another.
If you do that, give some consideration to whether the switch is make-before-break or break-before-make. If the switch is break-before-make, the inverter will be unpowered briefly during the switch. If the switch is make-before-break, the inverter will be continuously powered, but the charged battery will be briefly connected to the discharged battery. This could lead to some unpleasantly high currents through the switch and potential arcing if the switch is not rated for that application.solarpowerwindandstu said:I got a really good deal on 6v batteries is there any safe and viable way to use them effectively for a 12v system?
- 227 Forum & Website
- 618 Discussion Forums/Café