Recently installed a brand new bank of 16x Rolls S-480 375Ah @ 20hr and SG 1.280 @ 25°c as stated on their spec sheet.
On the battery sticker, it appears that these batteries were filled with 1.265 SG electrolyte.
After charging and EQ, it seems obvious that the SG will never reach 1.280, 1.265 seems to be their real maximum.
I was wondering what should be the real capacity @ 20hr of these batteries to properly set my battery monitors (WBjr/BMK). On the S-480 spec sheet, Rolls asks to lower this capacity by 5% to match a SG of 1.265. So to me, real capacity is 356Ah/20hr if SG is 1.265.
I don't understand why Rolls claims for 375Ah if they cannot reach 1.280, why not simply write 356Ah at 1.265/25°C?
Could someone confirm from experience if I'm right or wrong.
Thanks for any input,
Erik
Comments
-
Hi Erik,
YES, you are correct. Rolls does spec most of their RE batteries this way -- I have never seen any of their RE batts with anything other than 1.265 SG as the fill electrolyte.
At least, now, they do spec on the battery spec sheet, that the Capacities and other related data is as if the SG was 1.280, and to derate the Capacity, and run times, etc by reducing them by 5%, due to the usual electrolyte SG of 1.265.
They do this, IMO, because, there has long been Capacity wars among battery manufacturers. Some, actually increase the SG of the electrolyte (a bad thing, to me), and many have slightly increased the Reference temperature from 25 C to 27 C. And, this is just for RE batteries. Some batteries are pushing 1.300 SGs to get a bit more Capacity.
The reason that my sig states that the 4KS25 "1350 AH" batteries are 1280 AH.
Personally, think that Surrettes are a fine battery, and still spec/recommend them. Am glad, however, that they have started noting reality, on the data sheets. And, Surrette specifies everything anyone would want to know about their batteries, on those spec sheets ... number of plates, plate dimensions, separator and envelop thicknesses, electyrolyte reserve capacity, dry weight, wet weight, OH, plus, CCA, MCA Reserve Time ... everything. Try getting that info from Trojan, or most others!
FWIW Good Luck, ... Mush, Mush!! Have Fun, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Hey Vic, hope you're fine!
So, finally, 1.280 is just for marketing and 1.265 for real life. That's what I thought.
Anyway, as you said it's not a problem, I prefer to have it at 1.265 for longevity and two strings give me 712Ah which is enough for my needs and better suited to my 3.2kw array.
Did you take a look at the capacity/temperature curve? After checking it, I've set the WBjr capacity temp compensation to 0.5% per °C which is more accurate than it was with 1% classic default setting for my temperature.
I would like to keep this bank for 10 years and want to have it right from the begining (I hope).
No more mushing, too old!
A+
Erik
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed