Wiring question-need a pro
Still working with my friend on his system. He wants to install a square d qo load center/main breaker in his utility room(rated to 48V DC). This would require two positive wires from the battery buss and one ground from the battery buss. I need to know how to calculate the proper size ground wire. Thanks for the help and if more info is needed, please ask.
  • WaterWheel
    WaterWheel Registered Users Posts: 383 ✭✭✭
    Is that SquareD load center designed for DC?        If not it won't do well with the large arc DC can produce.
    48v Rolls 6CS 27P
    edited January 2016 #3
    they  are certified for MAX 48 Volts DC...as are the "QO" CBs
  • Vic
    YES,   BUT,  ONLY for breakers with Handle Ratings between 15A and 70 A,  inclusive,  And  only for QO,  QOU,  and QOB breakers.
    Do NOT use the Tandem breakers  --  the QOTs  --  as,  they have no DC rating at all.
    Expect that these QO breakers would not quite be acceptable with a 48 volt nominal battery voltage (IMO).
    AS I read the SQ D specs,   Vic
  • Vic
    By the "ground"  believe that you are referring to the battery negative ?   The battery DC Negative cable and the DC Positive cable should be sized such that the circuit breaker adequately protect these two cables from damage,  during a Fault.
    There are Ampacity Tables that will give you a good idea about correct conductor sizing.
    Is this a DC-only system?  That is,  NO inverter of AC power distribution?
    If so,  seems to me,  that you could run a maximum of a 70 A breaker as the Main.   And,  if the plan is to feed DC to each side of the QO load center,  that you would need two battery negative cables that land on the Neutral Buss.
    I am not a Code exoert,  so there are probably other things to watch out for.
    One other thing,  is that there are not really any standard DC outlets,  and perhaps few DC rated light switches.
    Perhaps I have assumed way too much.   Thanks for any clarification,   Vic
  • King-01
    King-01 Registered Users Posts: 28
    Vic,
    I am referring to "ground" as the negative leg. Pos and Neg battery cables are protected by Mersen class T fuses. The Square D load center/main breaker is located in the house, separate from the other protective systems/battery room. This is a 13.8V system DC only system.
    I assume that it is "code" that would necessitate having two "ground" legs instead of only one.
    Using UL listed RV light switches. Haven't gotten to the outlet part yet, suggestions are appreciated.
  • Xizang
    Xizang Registered Users Posts: 50 ✭✭
    edited January 2016 #7
    I'm watching with interest regarding 12 VDC outlets and light sockets.   Not keen to seeing cigarette-lighter sockets everywhere, there must be an acceptable 12 VDC electrical outlet that can't be confused with 120 VAC.  Likewise lighting sockets and LED/flourescent lamps.
    This is the best I've found, to be used in nice cabins, yachts, and quality homes...
    https://www.bluesea.com/products/1478/360_Panel_-_12V_DC_Socket_and_Dual_USB_Charger
  • King-01
    I'm running Sylvania LED 12V MR16 GU5.3 bulbs in both recessed lighting cans and light bars. These put out sufficient light and can handle the voltage generated during battery equalization (15V) but normally run at 13.8V. The Tech at Sylvania confirmed an even higher operating voltage since they are chip regulated.
  • Xizang
    WHERE can they be purchased?
  • King-01
    I buy them at my local Lowe's store and an electrical supplier that I have an account with.
  • Vic
    King-01 said:
    Vic,
    OK on the Class T fuses.    As long as those are sized to protect the cable that they feed,  this should be fine.
    Regarding the QO Load Center;  Then,  that Main breaker should not be larger than 70 Amps to meet the specs for DC ratings.   That 70 A breaker can be a QO double pole breaker.
    And,  OK on the DC switches that you are using.
    If you are using a two pole main in the load center,  then you should run a pair of battery Negative cables to the load center Neutral buss,   IMO.
    Most smallish DC systems do not need inspection,  and the code provisions that apply to safety are good guidelines to try to reduce the likelihood of   fires   and so on.
    It does look like you are off to a good start on the system.   Good Luc,   Vic
    Anderson connectors are very common. The small ones (Power Pole models) are good to 15 amps.
    http://www.solar-electric.com/installation-parts-and-equipment/wiring-cables-and-connectors/anhicupoco.html
    And if you want, HAM Radio guys have lots of "interesting" solutions:
    http://www.westmountainradio.com/kb_view_topic.php?id=ST166
    http://www.aesham.com/ham-radio-accessories-powerpoles/
  • Ethan Brush
    Ethan Brush Solar Expert Posts: 235 ✭✭
    I question whether it is worth going with 12V distribution, even for a small system.  Have you checked out the morningstar 300W suresine inverter?  I can understand having a 12V panel for a few select loads such as a laptop if you use it a lot, cell phone charger, fridge.  But you really cant go wrong running general stuff off that great little inverter.
    I too really like the MorningStar 300 Watt TSW inverter... It is much easier to wire up for even smaller loads. Here is the inverter Ethan talked about:
    http://www.solar-electric.com/inverters-controllers-accessories/inverters/moin/mosu300wasiw.html
    WIKI only has 2 plug in types listed, but a lot of connectors (already mentioned)...https://en.wikipedia.org/wiki/DC_connector
  • King-01
    He is working on his off grid cabin with minimal power requirements
    edited January 2016 #17
    Roughly, you are only talking about adding ~15% to your panel/battery capacity to make up for the inverter losses.... If it makes wiring/sending power farther distances easier, it is not a big penalty.
    Today, many of the AC appliances are very energy efficient (sometimes even more energy efficient than the 12 VDC versions). Not like 20+ years ago where AC Appliances wasted a ton of power (I have an old stereo that takes 20 Watts turned off just to run the clock/memory).
  • Ethan Brush
    IMO, going 12V to everything isnt worth it.  Everything is more of a pain, funky parts, expensive/limited bulbs and fixtures..  You may find yourself deciding to plug in a lamp somewhere and not have a 12V bulb, not having the right cord end.......Or what about when your friend comes there and wants to charge his cell phone or other electronic widget.....Maybe that electric shaver......Just stuff to think about.