100 amp service panel upgrade for PV install
browayjr
Registered Users Posts: 1 ✭
So getting ready to purchase 13kw solar w/ 2 x 7.6 sokaredge.
We need 2 x 40 amp breakers = 80 amps.
Here's my issue. The property has 100 amp service. With 100 amp panel. We want to replace the old zinco 100 amp panel anyways.
My thought was to purchase a 200 amp panel and downgrade the main to 100 amps. With this setup my solar will not exceed the 120 rule for the bus bar rating.
So I just wanted to open up a discussion and see if anyone with experience has any reason this shouldn't pass inspection!
Is that anything in nec guidelines that won't allow this?
We need 2 x 40 amp breakers = 80 amps.
Here's my issue. The property has 100 amp service. With 100 amp panel. We want to replace the old zinco 100 amp panel anyways.
My thought was to purchase a 200 amp panel and downgrade the main to 100 amps. With this setup my solar will not exceed the 120 rule for the bus bar rating.
So I just wanted to open up a discussion and see if anyone with experience has any reason this shouldn't pass inspection!
Is that anything in nec guidelines that won't allow this?
Comments
-
That is a common solution and likely what i would do. Note that a 100 amp breaker is a different frame size than a 200 so most likely you will buy a main lug panel and buy a 100 amp 2 pole and backfeed it as your main. Dont forget the hold down screw for the backfed main.
-
Make sure your building department/permit folks will sign off on this... And your utility may have some issues too (make take them some time to "approve" your planed changes).
And you may think about a 150 Amp main breaker... That would should allow you an 80 amp GT array branch circuit and still be under the 120% rating of a 200 amp box--Plus give you some additional main service capacity over your existing box.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Make sure your building department/permit folks will sign off on this... And your utility may have some issues too (make take them some time to "approve" your planed changes).
And you may think about a 150 Amp main breaker... That would should allow you an 80 amp GT array branch circuit and still be under the 120% rating of a 200 amp box--Plus give you some additional main service capacity over your existing box.
-Bill
Note: response is considering square D equipment. I am not as familiar with other brands.
-
You have a lot of inverter for your 13 kw of solar. What I might do is knock your 7.6 inverters to a couple of 6's. Then if you look at your max current connected to your AC panel we would be talking about 62.5A (25+25)*1.25. With your service upgrade go with a panel that has a 200A main breaker and a bus rating of 225A, install your PV breakers at the opposite end of the bus and you are good up to 70A of PV inverter output.
-
ARTsolar said:You have a lot of inverter for your 13 kw of solar. What I might do is knock your 7.6 inverters to a couple of 6's. Then if you look at your max current connected to your AC panel we would be talking about 62.5A (25+25)*1.25. With your service upgrade go with a panel that has a 200A main breaker and a bus rating of 225A, install your PV breakers at the opposite end of the bus and you are good up to 70A of PV inverter output.
-
solar_dave said:ARTsolar said:You have a lot of inverter for your 13 kw of solar. What I might do is knock your 7.6 inverters to a couple of 6's. Then if you look at your max current connected to your AC panel we would be talking about 62.5A (25+25)*1.25. With your service upgrade go with a panel that has a 200A main breaker and a bus rating of 225A, install your PV breakers at the opposite end of the bus and you are good up to 70A of PV inverter output.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed