wire size-panels to charge controller
ldiorio
Solar Expert Posts: 48 ✭✭
hi all,
am in the process of installing 6- 255 watt panels for a 48 volt system(vmp=30.4v,imp-8.4a.voc=37.6v,isc=9.1a)--
about 15 feet from the panels to the combiner w/AWG10 extender cable--then 40-45 feet from the combiner to the charge controller
some say i i could use 10AWG the entire length of the loop--but i ran a voltage loss calc and it says i need 6AWG for a min of 3% voltage drop
pls need opinions on this -i want to reduce the loss as much as i can-i already have 1" PVC run from the combiner to the CC
thanks
lou
am in the process of installing 6- 255 watt panels for a 48 volt system(vmp=30.4v,imp-8.4a.voc=37.6v,isc=9.1a)--
about 15 feet from the panels to the combiner w/AWG10 extender cable--then 40-45 feet from the combiner to the charge controller
some say i i could use 10AWG the entire length of the loop--but i ran a voltage loss calc and it says i need 6AWG for a min of 3% voltage drop
pls need opinions on this -i want to reduce the loss as much as i can-i already have 1" PVC run from the combiner to the CC
thanks
lou
Comments
-
Assuming you will be putting 3 panels in series for 2 strings. You would be running ~90VMP. 90 volts DC at 18 amps for the string.
45' of
4 AWG at 90 volts and 18 amps will be 0.44% drop or a loss of 0.4 Volt DC.
6 AWG will be 0.71% or 0.64 Volt DC drop.
10 AWG gives you 1.8% drop or 1.62 Volt DC.
Do you have any plans or hopes/ ideas of expanding this system at some time? If the definitive answer is no than you can use 6AWG. But if the answer is anything other then a solid no. go bigger. If this were my set up I would be using 2 AWG as I design for 0.25% or less loss when ever I can. I play by telco rules. no more then 1v drop from the source to the load. And we don't consider batteries to be a load. You can beat the numbers for 2 AWG by running 2 conductors per phase of 4 AWG. Depending on the price of wire this may be cheaper than a single run of #2. Or you may be happy with a single run of #4. These are the numbers, you can make up your own mind. -
i figured #10 would not do it
can i run a #10 insul ground
tks
lou
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed