Adding a volt meter with a switch, basic question
raymate
Registered Users Posts: 15 ✭
Just got a small LED volt meter, looks like they are designed for cars but can handle 4-30v and I want to use it to display the volts from my battery.
It has two wires pos and neg, attached it to my battery terminals to test it, it seems to work fine.
Don't want to have it powered up all the time so want to add a switch to it.
is it a good idea having something like this attached to the battery all the time?
As well as a switch I guess a fuse may be also a good idea?
May get another one to attach to the solar panel, could I just put that across the terminals on my charge controller for the solar input? or again is that not a good idea?
It has two wires pos and neg, attached it to my battery terminals to test it, it seems to work fine.
Don't want to have it powered up all the time so want to add a switch to it.
is it a good idea having something like this attached to the battery all the time?
As well as a switch I guess a fuse may be also a good idea?
May get another one to attach to the solar panel, could I just put that across the terminals on my charge controller for the solar input? or again is that not a good idea?
Comments
-
Say your meter was this one:
http://www.amazon.com/niceeshop-Digital-Display-Voltage-Voltmeter/dp/B00825NB24TYPE : LED;
Power range : DC 4.2 V - 30 V ;
Current consumption : 12mA ;
Accuracy : 0.1V;
Say you have a 200 AH battery bank and it has a 0.05% self discharge rate (average to low average for a flooded cell lead acid battery):- 200 AH * 0.0005 self discharge = 0.1 amps self discharge
- 12 mA = 0.012 amps for meter power (may be less current as input voltage rises)
Yes, you should put a fuse near the + battery/solar bus (1/2 - 1 amp or so, depending on wire gauge) just to protect against a short circuit in the wiring.
On the solar panel--You might want to try the first meter you got... The charge controller will pulse on/off the array (i.e., jump around between 14.x volts battery charging and ~21 volts Voc)--See if this meter gives you "useful" readings in the afternoon as the battery transition into absorb and float. Its readings may jump around a bunch at that point.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I have a several of those going by your description. One has been connected and illuminated continuously for about two years. Another has a push button momentary "on" contact switch. Yet another has an on-off switch, but only because it is in a travel trailer and the brightness of the display was a nightime distraction. Another in a truck, only comes on when the ignition is powered on. All running normally, no noticable discharge.
I never bothered with a fuse in any of the voltmeter circuits. That may be technically wrong. But the skinny wires that come connected to the meters probably make good fuses when the balance of the wiring is 16 gauge and many times larger.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
Mountain Don wrote: »I never bothered with a fuse in any of the voltmeter circuits. That may be technically wrong. But the skinny wires that come connected to the meters probably make good fuses when the balance of the wiring is 16 gauge and many times larger.
Some folks are experimenting with single cell battery monitoring (using a battery bank of 2 volt batteries). Their battery boxes are a rats nest of unfused skinny wires. If one of these wires melts, it might constitute a source of ignition inside a hydrogen filled battery box... How safe is that?
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Thank you all for the replies most helpful, I will add a switch mainly as they are bright, and they are indeed the ones i got. Going to mount them into a bit of plywood, any tips on mounting them so I don't mess it up, Does anyone make a face plate that may take them I actually have 3 of them in different colours along with one that just shows temperature going to have the probe near the battery. I want to have them all lined up in a row on my panel where I have my fuse box and controller etc.
-
I made rectangular openings in 5 mm plywood for some mountings. Another in a plastic wall plate, starting with a blank. My method was to drill large holes with a forstner bit in a drill press. Then I used a dremel tool with a cut off wheel to get a rough rectangular opening and finished with a file.
Re: the fusing.... My mention of skinny wires being fuses was partly tongue in cheek. It's just that I have not seen other instrumentation being fused. Things like the trimetric. Outback FNDC. ???Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
Mountain Don wrote: »I made rectangular openings in 5 mm plywood for some mountings. Another in a plastic wall plate, starting with a blank. My method was to drill large holes with a forstner bit in a drill press. Then I used a dremel tool with a cut off wheel to get a rough rectangular opening and finished with a file.
Re: the fusing.... My mention of skinny wires being fuses was partly tongue in cheek. It's just that I have not seen other instrumentation being fused. Things like the trimetric. Outback FNDC. ???
To some extent the small wires themselves act as fuses, limiting the current from the battery to far less than a hard short would produce. Just make sure there is nothing flammable around the wires.SMA SB 3000, old BP panels. -
Mountain Don wrote: »Re: the fusing.... My mention of skinny wires being fuses was partly tongue in cheek. It's just that I have not seen other instrumentation being fused. Things like the trimetric. Outback FNDC. ???
The positive power wire to the trimetric is most certainly fused. The sense wires from the shunt do not need to be fused because both sides of the shunt are at ground potential.
By the way, a current shunt would work just as well on the positive terminal of a battery as on the negative. The reason we put shunts on the negative side is so that we do not have to protect the wires with a fuse.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
The positive power wire to the trimetric is most certainly fused. The sense wires from the shunt do not need to be fused because both sides of the shunt are at ground potential.
By the way, a current shunt would work just as well on the positive terminal of a battery as on the negative. The reason we put shunts on the negative side is so that we do not have to protect the wires with a fuse.
--vtMaps
If they are just inputs to an op amp, then it should be OK either way.
SMA SB 3000, old BP panels. -
OK, I'm wrong. The trometric wiring diagram does show a fused + lead. I don't own one and my memory is faulty. So I have some inline tubular fuse holders someplace in a box in the shop. It would be a good idea to add one in the meter + line. ..... great thing about discussions here is the learning experience. ThanksNorthern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M
-
I wonder.......
A switch always has some ohms across the contacts of a switch and it does not matter if the switch is closed or open.
In a case like that, would the volt meter read a different voltage if a switch would be used instead of just wiring the meter straight to the power source. -
For a 12 mAmp load current (mostly used to light the LEDs), it will be close enough (I the one I linked too--The volt meter is not adjustable and a few people complained that it was not very accurate).
You can treat this just like a standard cable voltage drop problem...
http://www.calculator.net/voltage-drop-calculator.html
100 feet (one way run) of 22 AWG wiring and 0.012 amps:
Voltage drop: 0.039
Voltage drop percentage: 0.33%
Voltage at the end: 11.961
Hardly affect the digit to the right of the decimal point.
Of course, if you want a more accurate reading--Then use a LCD meter or one that draws its operating power different from the measurement leads.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I also have one of those (same model running 24/7). Yes it is bright, kinda of works as a night light! The accuracy of mine out of the box is about 0.1V off. One thing, the first one ran for 2 years unitl a particularly bad lightnening strike, whereupon it died. I suggest (given the hassle of maching the panel hole for it), you buy a couple to keep one as a spare. Or put a zener/varister/MOV across it. Fusing: a half amp PTC is, what, a few cents. Easy.1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
I wonder.......
A switch always has some ohms across the contacts of a switch and it does not matter if the switch is closed or open.
In a case like that, would the volt meter read a different voltage if a switch would be used instead of just wiring the meter straight to the power source.
The ohmic resistance of the switch contacts will be exceedingly small compared to the ohmic resistance of the voltmeter. You might be able to measure a small number of millivolts across the switch, but more likely microvolts.
The voltmeter will definitely read lower when the switch is open.SMA SB 3000, old BP panels. -
Added in the little volt meters, I put one on the solar panel feed, battery and load out from charge controller. Can someone explain why they all say the same when I'm using the system. I was expecting different values. I have each section with a breaker so if If disconnect the solar panel for example I then see I guess the panel voltage with out any load. If I flip the switch to make the panel live then the voltage becomes the same as the rest of the system. I assume thats correct
Was thinking the load output from my CC would just give 12v it does not, it all seems to work fine but it can be 11,12,13 and 14v
The little meters are cool and give me a good idea of what is going on, but like I say not understanding why they all say the same. But if I isolate them I get different readings. -
If you have a PWM type solar charge controller (and not a MPPT type)--The Vpanel input, Vbatt output, and charge controller will be about the same (within a 1/10th of volt or so) of each other if:
- All is working well (battery in the range of 10.5 to 14.8 volts or so)
- There is light on the solar array.
- Charge controller thinks the battery bank needs charging (PWM controller "turns on" in bulk mode 100% of the time).
- 11 volts on the battery bank is pretty low--Generally, we suggest that you avoid going below ~11.5 volts under load
- 12 volts on the battery bank with no load is ~50% state of charge
- 13 volts is the battery is not being discharged (~12.7 to 13.6 volts is float charging)
- 14 volts is the battery starting to get a good charge on it
- 14.5 to 14.8 volts is what the charge controller will hold at the battery for ~2-4 hours or so to fully charge the battery bank. Vpanel should slowly rise from 14.5 to ~21 volts as the charging current is reduced.
- Vpanel should be pretty close to zero volts at night.
- Load Control should be ~Vbatt voltage unless Load Control turns off (battery near dead, over current from LC terminals, etc.).
If flooded cell batteries, I would get a good hydrometer. Also, assuming the charge controller and everything else is working OK, I would turn off your loads and/or get an extra battery charger on the battery bank and get it fully charged (check specific gravity of all cells, etc.).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
What is the sunlight/current charging current/loads in this pic?
I want to make sure your batteries are getting properly charged.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
What is the sunlight/current charging current/loads in this pic?
I want to make sure your batteries are getting properly charged.
-Bill
In that picture it was shaded (and cloudy today), charge current was not registering on ProStar (too low), no load (apart from a few MAh for the LED temp display unit.
Just did it again, with sun (moved around, but cloudy right now)
With a load of 1.2 Amps, Charge current 0.4 Amps (this load was running for about 15 mins, LED lights)
On the displays I see
Panel 12.4 v
Battery 12.5 v
Load 12.4 v
update, battery now seems charged and is gone in a optimization mode from the CC, no load at this time. and now
On the displays I see
Panel 15.3 v
Battery 14.1 v
Load 14.1 v
Another update as the sun went down I watched the solar panel V and it did indeed went down and down and then was not providing enough power to keep the display running and just cut off, so that does seem to work fine.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed