The washing machine problem

I've read over just about every thread on washing machines on this site and others. My problem is i can't find any information on the inrush current so i don't know how to size the inverter it runs on. I see lots of listings per load but I really need to know how large of an inverter it takes to run one. I looked at some of the smaller portable ones, they look nice like the panda portable washer or a pulsator type washing machine from sonya but i have no idea what the motor surge is. Pretty sure 12/24 volt models do not exist. Anyone have luck running them and if so how big and with what?
Comments
On the other hand, that same voltage drop could cause the electronic controls on a modern washer to shut down where a purely mechanical timer would have ridden through without problems.
I guess what I am saying is that just seeing the specifications will not be enough to tell you what will or won't work.
I tested its peak current draw back when I first got my washer in 2006, I don't recall it being more than 500 or 600 watts.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
At that time the monitoring system i used was quite sensitve and captured surges and peaks pretty well.
http://zoneblue.org/cms/page.php?view=off-grid-solar
My 600W 5000 BTU A/C unit measures 22.6 Amps during start-up. A Kill-A-Watt meter is far too slow to capture the reading.
A Dewalt Emglo air compressor, with a 1.2 HP 120VAC motor that easily runs from a 15A grid powered outlet, spikes at 53.8 Amps during start-up. Consequently, I can't run it from either of my inverters, or from a 2400 Watt (3KW peak) rated generator.
The testing I performed on a previous top loading washing machine can be seen here: http://www.alpharubicon.com/altenergy/altwashclothes2manytoyz.htm It ran easily from an 1800W inverter.
Our latest washer & dryer are front loaders. The washing machine does have a soft start feature, unlike the last one. It will be run from an inverter exclusively as soon as the weather cools down enough to run wire in the attic!
So you will need 1500watts, which will need a 12v DC/AC 2000watt inverter. I've installed these for 2 off grid homes.
All inverters vary though, even with name plate. (I.E) I own a few of the sunforce 12V 2000watt peak surge/1000watt continous AC inverters, I've measured that they never meet the 2000watt peak.In my case the inverter peak surges at 1800watts, which is much less than the name plate surge, and the inverter heats up after a few minutes on continuous loads and can only deliver a consistent 900watts, not 1000watts.
Thats why the washer calculation summarizes that the surge current is 12.5 amp, even if you can find a washer that may have a surge peak of 8.5amp . 12.5amp is the average load calculation for the plethora of washers available on the market.
So if we calculate AC loads adjusted according to the 25% overcurrent protection, the inverter is always safe guarded and shouldn't (in theory) over heat no matter the physical demand VS the manufacturer name plate.
1500 X 1.25 =1875watts, in this case the inverter should never over heat unless the inverter is signifcantly under rated to the manufacturer name plate.
And they go and go and go. Nothing to break. No belts, cluctches, gears nothing.
http://zoneblue.org/cms/page.php?view=off-grid-solar
For Grid Systems the Branch circuit for washer is calculated at 12.5amps ( for both motor 8amps, and pump 4.5 amps), thats just how its calculated. Its just a measurement for over current protection.
If it was just the motor which the circuits for gas dreyers are rated at 8 amps, it would be better descriptive, but there are times between cycles with washers where even for maybe 10 seconds there could be a peak surge of 1200watts, even with direct drive systems, that work in combination with a pump.
The calculation doesn't change for off grid because inverters requiring over 10 amps require some sort of over current protection device inline.
Also following these calculations equipment tends to last longer from the washer/inverter, etc. Building to the bare minimums equipment does tend to fail sooner.
Not really. what you presumably are referring to is the 1500 VA for the laundry receptacle which is used to calculate service and feeder load. This is added to the general lighting loads and small appliance loads, and then demand factors are added in. This is just for the "laundry receptacle" required by 210.52(F) and isnt necessarily for the washing machine. This may sound nit picky, but the point is that this figure isnt meant to say anything about the specific amp or watt draw of the washing machine.
Thank you for the clarification, I concur with that statement.
However lighting loads, are seperate branch circuits from, appliance circuit loads.
Differences corresponding to NM-B(white 15amp), NM-B( yellow 20amp), NM-B (orange 30amp)
Calculating VA for laundry/washing loads would mean no more than 1junction/recep boxes a dedicated for washing machine (technically it should be a dedicated 1 pole circuit, no different than a 2 pole 30amp for electric dreyers, (or dedicated circuits for fridges, micro waves, and garbage disposals greater than 1/2hp).
So if I'm not misconstruing NEC laundry/washer circuit should infact be dedicated.
http://zoneblue.org/cms/page.php?view=off-grid-solar
Mine are about 10+ years old and I turn of the electrical power to them when not used... They use something like 9+ watts when "off"--And use almost as much turned off as doing a couple washes a week (9 watt load is 1.5 kWH per week vs ~1.0 kWH per week for two wash/dry loads).
-Bill
I'm not argueing I'm agreeing with you. For a branch circuit appliance, I have to calculate for the maximum an appliance can use on that branch circuit.
There is a lot to account for. Much of the larger washers for grid are up to 5cu/ft of volume with large barrel drums. Over 5cu/ft its considered commercial grade, and those calculations are much higher than what we see in residential applications.
I do agree that your unit is highly efficient. I just calculate for the maximum allowable. Thats all I am saying, if there is room for additional loads on a 2000watt inverter..Great, good investment.
F&P is also famous for its "dish drawer" dishwashers.
But i get the impression that many more companies are going that route, so id just be doing a little research on the brands available near you.
http://zoneblue.org/cms/page.php?view=off-grid-solar