6v or 12v Battery. Confused
Zakarume
Solar Expert Posts: 143 ✭✭
Was getting bored today and was looking at different batteries for solar. I have theses right now http://www.trojanbattery.com/product/t-105_plus/. There are 8 of theses wired in series/parellel for a 450 AH 24v battery bank. I am now seeing these https://www.batteriesexpressinc.com/...int-srm-29.htm. It says they are at 210 AH battery. If i read this right then 6 of these would be 630 AH 24v battery bank and be bigger than mine. Would this be correct? Would it be better than what i am using now? It says it is a Deep Cycle battery, but it is confusing me
1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
Comments
-
Hi Zak..,
There is a Typo on the site that you Linked. There is NO AH Capacity noted, at all. The Reserve Capacity is minutes of run time @ 25 A. Instead of listing this Reserve Capacity in Minutes, they mistakenly list the RC as AH.
In looking at the Interstate site, there is NO AH Capacity listed for this battery either.
It might be about 100 AH, but suggest that you RUN AWAY!
In general, buying the lowest voltage battery that you can will give better results, IMO. Because, if a battery goes bad, and you must replace it, you will be throwing away fewer good cells, usually. And higher voltage batteries have less capacity for a given weight, so, you would wind up with more parallel strings, which is not goos.
Just my opinions, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
I'm new to this RE thing but traditionally, RE batteries usually come in 6V and 2V offerings,with plenty of good reasons. Marine batteries are invariably deep cycle batteries too but aren't manufactured for use in RE applications and typically would not stand to the test. The ones which can double as RE batteries are typically way more expensive yet once again rarely appear in offerings of greater than 8V per battery. I'd say you're better of with your T105-RE batteries (distinctly different from the T105 batteries). Notice the RE suffix? It's common nomenclature you'd find these days and it specifies that the batteries are engineered for RE applications.Semi off-grid
255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)
300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)
-
I'm new to this RE thing but traditionally, RE batteries usually come in 6V and 2V offerings,with plenty of good reasons. Marine batteries are invariably deep cycle batteries too but aren't manufactured for use in RE applications and typically would not stand to the test. The ones which can double as RE batteries are typically way more expensive yet once again rarely appear in offerings of greater than 8V per battery. I'd say you're better of with your T105-RE batteries (distinctly different from the T105 batteries). Notice the RE suffix? It's common nomenclature you'd find these days and it specifies that the batteries are engineered for RE applications.
If you just look at the weight of the T105 compared to the T105RE, you will see that it has a lot more lead in the plates for long term stability.
Cranking batteries have more thin fragile plates to be able to deliver high current "off the top". But if you discharge them too far the plates will suffer cumulative damage. Same if you chronically overcharge them.
Hybrid (and most Marine batteries, even if they say Deep Cycle) batteries have fewer thicker plates and the active chemicals on the plates are structured to withstand a deeper discharge, but still not the cycle life of a real RE battery.
RE/Deep Cycle batteries have a higher internal resistance than the other two types, but are designed to deliver a lower current through many more discharge/charge cycles for longer life. In some cases the chemical composition of the active material on the plates may be different too.
SMA SB 3000, old BP panels. -
It was just confusing as to why they say i is deep cycle when overall it is not. Just got done watching a youtube video and it explained it better also
Link is here https://www.youtube.com/watch?v=xELqluPUsuQ1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter -
Hi Zak..,
There is a Typo on the site that you Linked. There is NO AH Capacity noted, at all. The Reserve Capacity is minutes of run time @ 25 A. Instead of listing this Reserve Capacity in Minutes, they mistakenly list the RC as AH.
In looking at the Interstate site, there is NO AH Capacity listed for this battery either.
It might be about 100 AH, but suggest that you RUN AWAY!
In general, buying the lowest voltage battery that you can will give better results, IMO. Because, if a battery goes bad, and you must replace it, you will be throwing away fewer good cells, usually. And higher voltage batteries have less capacity for a given weight, so, you would wind up with more parallel strings, which is not goos.
Just my opinions, Vic
Using six volt batteries, you can get a 24V bank using just four in series to get 24 volts and two strings in parallel to get more capacity (550AH).( If you were starting from scratch, I would recommend a 48V battery bank instead, using all eight batteries in a single series string.)
If you try to get the capacity you need at 24 using 12V batteries, you will end up with four series pairs in parallel, and that is generally accepted as a bad idea. It will be hard to get even current distribution over the four strings during both charge and discharge, and that will reduce battery life and require more maintenance attention from you.
You can see a good discussion of batteries in parallel at this site. The rest of the technical pages on the site are great too.
SMA SB 3000, old BP panels. -
I just looked at the Trojan site and it shows both RC (although not explicitly labelled as that) and the AH at 5 through 100 hour rates. The 225 AH at twenty hours (C20 = 225) looks right for this 6V battery.
Hi inetdog,
If the above was responding to my statement that there IS NO AH rating in the Linked site's data, I was referring to the Subject battery from Batteryexpress.
It is THAT battery that has NO AH rating stated. It is THAT battery that has the Typo, where Reserve Capacity is stated in AH, rather than the correct Reserve Minutes.
And it was that battery that I was referring that Zak.. RUN AWAY FROM, NOT, his existing bank of Trojan batteries.
As noted in my previous post, there IS NO AH Capacity listed for the same battery on the Interstate site either. So, seems that that battery merits no attention for RE use, FWIW.
Should have been more specific that I was referring to the Interstate Battery SRM-29, and the site with the bogus R C Data was Batteryexpress ... FWIW, Thanks, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed