Need Advice on Grid Tie Setup
wilsonbh
Solar Expert Posts: 57 ✭✭✭
I have a nice span of roof (standing seam metal roof) facing south that is 34' wide. I'd like to install some solar panels in this space. The area is wide (34') and about 22 feet deep. My goal is to get to 3kW of power production in this space. Is this possible? I'm thinking I might be able to place 10 panels in this area. Thoughts?
Billy
Merritt Island, FLORIDA
Billy
Sure is possible.
A nice solar panel spec size to follow is the solar world SW290M or SW285M for mono crystalline.
You should be able to fit 12 panels comfortably and easily with the NFPA set backs as a requirement. -
Agreed pretty easy to do that one, Your fire code setbacks will control the usable space, the local code department should be able to help there.
Generally, how much space is needed for fire code setbacks?
It depends but here in AZ they require a 3 ft setback from the ridge line, The best answers will come from the local AHJ. -
Front eve does not require 3ft set backs.
Side eves and ridge require 3' set backs.
Uniform Plumbing code also requires that plumbing vents do not get covered by solar array. So if you have plumbing vents the panel must be off set. -
System without net metering
Sir,
We have installed 100 kWp of SPP in different locations in our organisation in India. The configuration is as follows
Each module is 250 Wp. The strings are connected to form and array which in turn feeds 20 kW and 10 kW inverter of Delta make. From the ACDB, the cable is connected to the main LT panel at the substation. There is no battery backup for the SPP and there is no net metering as well.
I want to know the scenario when the SPP generates power more than the requirement of the facility building. Whether the power is fed back to the grid?
Whether the system can be called as a “grid-tie”system? Please help on this aspect.
Regards,
Melvin Koshy -
Melvin,
Your system is a "Grid Tied" system in function (that is how those inverters work). If the load of the facility always exceeds the power generated by the solar array + GT inverters, then it will never back feed the utility.
Of course, you cannot guarantee this unless you know the loads well enough (i.e., these are "base" load that are always one and do not cycle, turn off for holidays, and technically, if you have a power failure, the loads come back on before the 5 minute timeout of the GT inverters).
If you have a "typical" utility connection/local distribution system, the utility interface is "bi-directional"--You can back feed the utility. There are in some cases utility protection devices that measure the direction of power flow and turn off in the case of the back feed (safety as there are sometimes parallel current paths in the distribution system to share loads/backup in case there is a failure in one distribution leg, etc.... But this appears to be rare--at least in the US). In some cases, the reverse power flow detection may be installed if there is a large backup generator in the facility (I believe is it sometimes done--Not my area of expertise).
Another issue--In the "olden days", the mechanical utility meters used for logging power were bi-directional. The meter would run "forward" if you consume power, and "backwards" if you generate power to the grid. Newer meters may:- Meter may not run backwards--So you may not get any credit for power "sold" to the utility.
- Meter may run forwards if back fed power--So you may get charged for power you sell to the utility.
- Meter may fag/report reverse power flow to the utility--Utility may choose to take action against the company for feeding power to the utility.
- Meter may attempt to figure out that you have GT Solar--In the US and other countries, the utility can (worst case) disconnect your power if you have any solar power GT connected to their utility power--Whether you back feed or not.
- Meter may have peak power/peak VA logging--For commercial billing in US, there are "reservation charges", basically peak 15 minute power usage in the last 1 or 12 months... Roughly equal to 1/2 the bill. For locations with large solar array, the solar back feed can be higher than the loads, and actually drive up the cost of utility connection (utility does not "care" which direction power/VA flows when calculating bill).