Fuse 35 watt system?
zapthecat
Registered Users Posts: 1
Greetings all, I just put together a home grown solar project to power outdoor landscape lights & was wondering if this should be fused or not. It consists of 2 banks of 5 solar panels, all wired in parallel. Specs are: Pmax 3.5w, Vmp 18v, Imp .19A, Voc 20.7v, Isc .21A. So figure 35w total, battery is 12v 12ah SLA, and I'm using a 5amp pwm solar controller from eco-worthy. Everything works, I'm just wondering if I need to add circuit protection via fuse(s) and if so how to calculate the values and where to toss them in the circuit. Appreciate any replies. Thx.
Comments
-
Welcome to the forum ZaptheCat!
First, the battery is the source of high current in most off grid systems... So, you should have a fuse/circuit breaker based on the wiring leaving the + battery bus... If you have a 1 amp load, you should have at a minimum 1.25x 1 amp = 1.25 fuse rounded up to 2 amps -- With heavy enough wire to both carry 2 amps, and not have too much voltage drop from battery to the lights.
If you use a voltage drop calculator, say 1 amp, less than 1/2 volt drop maximum and send the power 20':
http://www.calculator.net/voltage-drop-calculator.html
18 AWG wire:
Voltage drop: 0.26
Voltage drop percentage: 2.17%
Voltage at the end: 11.74
For the charge controller:
10 x 0.19 amps * 1.25 NEC wiring derating * 1.25 solar derating = 3.0 amps minimum branch circuit rating (fuse/wiring).
Keep wire run from charge controller to battery bank relatively short... Ideally, you want around 0.05 to 0.10 volt maximum drop from controller to battery bank (want charge controller to accurately measure battery bank voltage). Voltage drop calculator--Using 14 AWG wire, 3 amps, 4 feet:
Voltage drop: 0.061
Voltage drop percentage: 0.51%
Voltage at the end: 11.939
Of course, with a 14 AWG wire, you could go as high as 15 amp fuse/breaker.
Lastly, there is fusing of the solar array itself... For larger panels (100's of watts), we generally have to fuse/breaker each panel if there are three or more panels in parallel... One shorted panel is fed by the rest of the good panels--Need a fuse/breaker to protect the wiring from over heating the shorted panel.
With your very small solar panels, I am not sure what the series fuse rating for those panels is--You probably would not worry about fusing these small panels...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed