Wiring 42 12 volt 35 AHr Batteries in a 12 volt configuration
hermit
Solar Expert Posts: 25 ✭
These batteries were gifted, what to do with them? Make my shed a source of power. I have a 3000w 12v inverter with 2 sets of inputs (2+ AND 2-) I have bus barred 3 sets of 14 parallel batteries. Question which is the best way to hook up these 3 sets of batteries to each other for both charging and for the inverter. The reason why there are 14 X 3 is that what fits on the shelf. I used aluminum bus bar. The inverter needs to be hooked up with 2 positives and 2 negatives. Do I tie all strings at both ends together both on the positive and negative sides, or do I tie 1 end of string to the opposite side of string then again to the opposite side of the string to the other string (kind of like series but not positive to negative) or tie the 3 strings together with just 1 positive on 1 side and 1 negative on the other side. The answer will determine which way I hook up my charging. Then which would be the best way to wire up the inverter which needs 2 positives and 2 negatives? I know this parallel configuration is bad for charging and troubleshooting but this is what I have. Thanks for you input.
Comments
-
These batteries were gifted, what to do with them? Make my shed a source of power. I have a 3000w 12v inverter with 2 sets of inputs (2+ AND 2-) I have bus barred 3 sets of 14 parallel batteries. Question which is the best way to hook up these 3 sets of batteries to each other for both charging and for the inverter. The reason why there are 14 X 3 is that what fits on the shelf. I used aluminum bus bar. The inverter needs to be hooked up with 2 positives and 2 negatives. Do I tie all strings at both ends together both on the positive and negative sides, or do I tie 1 end of string to the opposite side of string then again to the opposite side of the string to the other string (kind of like series but not positive to negative) or tie the 3 strings together with just 1 positive on 1 side and 1 negative on the other side. The answer will determine which way I hook up my charging. Then which would be the best way to wire up the inverter which needs 2 positives and 2 negatives? I know this parallel configuration is bad for charging and troubleshooting but this is what I have. Thanks for you input.
First of all, my advice is to forget this configuration. The operational problems of 42 lead acid batteries in parallel are just too great to contemplate.
If you insist on doing it anyway, read the information at smartgauge.co.uk, The page How to correctly interconnect multiple batteries to form one larger bank will give you some idea of the problems involved.
The "ideal" four battery solution shown there can be extended to 8, 16, or 32 batteries without much trouble (but a spaghetti pile of long wires and a maintenance nightmare?!), for 42 you will have to compromise some.
Is there any way that you can use a 48 volt system instead? That would reduce the complexity of the battery wiring but you could only use 10 strings of four batteries each and keep the other two as spares. I would not really recommend that either, but it would be better than 42 in parallel!
And before you start, do you know enough about the history of the batteries to be confident that they are good? If they sat for months without being charged they could have lost much of their capacity.SMA SB 3000, old BP panels. -
If they were given to you for free then for sure - give it a try why not? It's a pity you have to go in an all-parallel 12v configuration but then I suppose if you're stuck with a 12v inverter you have no choice. If possible use heavy copper bars to link all the + terminals together and all the minus terminals in a long "train rail" configuration. As for attaching them to the batteries you want to have as little electrical resistance as possible at the terminals and since the batteries were free I would just solder them securely to the battery terminals. Now with all 42 batteries connected like sleepers on a railway line with the copper tracks above them connect the loads and charging points at the diagonaly opposite ends of the setup;)
-
Sell them to a recycler or buy alot of fuses and a sprinkler system with a dialer for the fire department."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Ditto on the go 48 volt arrangement, 12v will potentially leave cells overheating and evaporating regularly.hybrid: xw6848 pro with two mppt60, 6 kw pv
17 cell 280ah LiFePO4 storage 14 kw
gridtie: sunny boy sma 2x 5k
gridtie: fronius ag5100 5k
Gateway / Insight Local
xw4548 backup -
The batteries are 3 years old and taken from one of our decommissioned facilities. The batteries are Discovery AGM VRLA`s. If it was easier to get a higher voltage inverter I would but usual order time is 2 to 6 months. Maybe I should be a little less aggresive on the number of batteries in this installation.
-
FYI if you went 48V @ 35Ahr you would get ~ 800Watt hr of usable power per 48V string, not very much power, about enough to run a single 40w light for 20 hours and be able to reuse the battery continuously. If those are UPS batteries they may not be designed for many discharges before starting to fail...
hth
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Generally, the max parallel batteries you can successfully get away with are 3. You are looking at 14 times what can be expected to reliably work. Sorry, it's a no go.
Even wired for 48 volts, you're over 3 times what can be expected to work. Try to sell them now as used but working batteries - - - or keep them and prepare to sell them for scrap. -
I've found a nearby battery wholesaler that accepts old batteries for recycle in trade for new ones. It worked out to be about 20-30 cents per pound. With almost thousand pounds of batteries, you might get a couple of 6 volt deep cycle batteries in exchange! Might even get a couple of 12 volts. Working with many small AGMs in UPSs, I cannot imagine the pain (and maybe danger) of keeping so many old ones working together.3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter.
-
I cannot imagine the pain (and maybe danger) of keeping so many old ones working together.
At least fuse groups of three or four batteries maximum.
SMA SB 3000, old BP panels. -
Free isnt so cheap. I think I will listen to the words of wisdom and save grief. Thanks for the replys.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed