Want to ask the questions from another angle ito charging and cabling
South Africa
Solar Expert Posts: 295 ✭✭✭
Hi, I am quite confused at the moment, for too many cooks are spoiling the broth.
So I am coming to the experts.
Questions are always from a load perspective, worked back to batts and inverters. I find myself on the other side at the moment.
Picked up a inverter that can generate max 1400w (so I assume 2800w peak for a few seconds) with no cables.
Included in the inverter, is a 20amp charger.
And no manual that I could find.
Question 1: What is the cable thickness I need to install if the inverter is 2 meters from the batteries?
Question 2: How many 100ah batteries (24v) can one charge with a 20a charger, using AC power?
What are the maths?
So I am coming to the experts.
Questions are always from a load perspective, worked back to batts and inverters. I find myself on the other side at the moment.
Picked up a inverter that can generate max 1400w (so I assume 2800w peak for a few seconds) with no cables.
Included in the inverter, is a 20amp charger.
And no manual that I could find.
Question 1: What is the cable thickness I need to install if the inverter is 2 meters from the batteries?
Question 2: How many 100ah batteries (24v) can one charge with a 20a charger, using AC power?
What are the maths?
5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied.
Comments
-
Worse case math:
- 1,400 Watts * 1/0.85 inverter eff * 1/21.0 volts typical inverter cutoff * 1.25 NEC circuit derating = 98 amp minimum branch circuit rating (wiring+DC breaker/fuse)
- 23 volts minium battery - 21 volt inverter cutoff = 2.0 maximum wiring drop
- 2,8000 Watts * 1/0.85 inverter eff * 1/21 volts = 157 amps @ maximum load
When using a voltage drop calculator, make sure you use the method they recommend--Some calculators use the "one way wiring run" (assuming 2x actual electrical wire length), and others use 2x one way length.
I am not sure if your location uses mm diameter, mm2, or AWG (American/other wire guage).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you.
Will this be accurate: http://www.bulkwire.com/wireresistance.asp
I get (rounded) 10mm2, or AWG 7 required for 2m.5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied. -
For that calculator, it looks like you need to use the round trip distance (4 meters for you?).
If you can afford/fit heavier cable (and/or shorter distance), I would suggest. that. The numbers I gave for the calculation would give you the smallest wire that should work.
Add a fuse/circuit breakers, a few connections and such, I would suggest going on the conservative side. Go one or two size larger cable than the minimum diameter to give you a bit of head room (allow for aging, battery bank slowly losing capacity, high temperatures, etc.).
-BilNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I forgot to answer the 20 amp charger question... 5% to 13% typical rate of charge--10% rate of charge is recommended for "tall" case batteries (and many storage battery mfg. minimum recommended rate of charge):
- 20 amps * 1/0.10 rate of charge = 200 AH battery bank nominal
- 20 amps * 1/0.05 rate of charge = 400 AH battery bank maximum
- 1,400 Watts * 1/0.85 inverter eff * 1/24 volts nominal * 8 hour discharge rage = 549 AH @ 24 volt "nominal" for 1,400 Watt continuous load
- 1,400 Watts * 1/0.85 inverter eff * 1/24 volts * 5 hour discharge rate = 343 AH @ 24 volt maximum short term power (smaller battery bank)
- 2,800 Watts * 1/0.85 inverter eff * 1/24 volts * 2.5 hour discharge rate = 343 AH @ 24 volt battery bank for starting loads (i.e., well pump)
US GEL type batteries are usually rated to a 5% maximum rate of charge.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Ageing etc ... do you guys know that most UPS people are NOT aware of all of this?
Using 4m total lenght, 98amps, it says AWG8, I am going for AWG6, and if I cannot, AWG7.
Why, the Brad Harrison / Anderson connector crimping tool is the key. :-)5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied. -
Most UPS batteries are replaced after a couple of years. Or after a major outage.
For off grid folks, that would be a bit on the expensive side.
Also, UPS batteries are usually GEL or AGM type--Which do much better for surge loads (some are rated as high as C*4 discharge rate--I.e., can be taken flat in 15 minutes).
Of course, those UPS systems are usually designed to only run long enough to safely shut down the computer (outage at home) or to get the diesel genset up to speed and stable.
For most off grid folks, they want to run primarily from battery banks for ~10 to 20+ hours at a time (say 5-10 hours a day/evening for ~2 days straight) and have the batteries last 5-8 years (or more). And with limited number of charging hours per day (sun is up only so long)...
Pretty much a different operating environment vs UPS type setups.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I see fuses are easy: http://www.bdfuses.com/fusesnwires.php
80amps or less fuse needed for AWG 6 cable.5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied. -
Most UPS batteries are replaced after a couple of years. Or after a major outage.
Of course, those UPS systems are usually designed to only run long enough to safely shut down the computer (outage at home) or to get the diesel genset up to speed and stable.
For most off grid folks, they want to run primarily from battery banks for ~10 to 20+ hours at a time (say 5-10 hours a day/evening for ~2 days straight) and have the batteries last 5-8 years (or more). And with limited number of charging hours per day (sun is up only so long)...
Pretty much a different operating environment vs UPS type setups.
-Bill
I would have agreed with you Nov last year. Last real load shedding we had was back in 2008.
Then Dec and Jan 2015 came ... suddenly no batteries, no UPs'es and (wow) no solar inverters.
Now people want to run for min 3 hours ... and I believe we can prepare for longer.
So I thought, after losing a deep cycle batt that shorted and a friend of mine walked into a server room where a UPS was busy smoldering, it is time to be wiser.
Most UPS are cheapies imported from elsewhere and most are cheap 2000va upwards with minimum 2 x 100ah batteries, sometimes up to 8 batts.
So idea is to start sorting the cabling and protect the batteries.
Ps. Our grid:
It is reported that IF they start tomorrow morning it may take min 10 years to fix just the grid whilst building more power stations. By 2025 ish, most of the current stations will be end of life.
And the 2 new ones ... still not operational ... 4 years behind with NO end in sight.
5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied. -
10 years. The US government took 3 years from a depression to the end of wwll.
10 years means I have a job until I retire.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
One last question:
Battery AH: 100ah
System volts: 12v
Inverter efficiency: 0.85
Max Daily discharge: 0.50
= Nominal Daily Discharge: 510w
Am I correct in saying that a 100w load on the inverter, could be powerred for +-5 hours?5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied. -
Roughly.
Note the batteries have less apparent capacity the faster you discharge them.
We use a 20 hour discharge rate for our rules of thumbs.
5 hour discharge to 50% is a 10 hour equivalent discharge rate.
Your 100ah battery may look like a 90ah battery at the 10 hour rate.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed