24hr generator vs inverter/charger efficiency?
Audiomaker
Solar Expert Posts: 100 ✭✭
So here's a question for ya...
We all know the advantages of having an inverter/charger/battery setup. The ability to add renewables, the ability have quiet (at times)...etc.
My question though is what is the efficiency (in cost), not counting the equipment costs, of the charge/invert/discharge cycle versus just running a generator 24/7?
The generator "loads" up to charge a bank, so it uses more fuel during those times, plus there are losses in the charger, and in the inverter, plus the #1 loss that I'm focused on which is losses in the charger to battery.
In other words, how many kWh of energy is required to charge a bank to produce that same amount of kWh back to the inverter?
I had always figured that having an inverter setup (paired with a generator auto start/stop) was saving fuel, but as I watch the generator load up, and then taper off down to absorb and float for hours, I start to wonder just how much savings that might be?
Thoughts?
Sean
P.S. I'm certain this has already be over-covered, so apologies.
We all know the advantages of having an inverter/charger/battery setup. The ability to add renewables, the ability have quiet (at times)...etc.
My question though is what is the efficiency (in cost), not counting the equipment costs, of the charge/invert/discharge cycle versus just running a generator 24/7?
The generator "loads" up to charge a bank, so it uses more fuel during those times, plus there are losses in the charger, and in the inverter, plus the #1 loss that I'm focused on which is losses in the charger to battery.
In other words, how many kWh of energy is required to charge a bank to produce that same amount of kWh back to the inverter?
I had always figured that having an inverter setup (paired with a generator auto start/stop) was saving fuel, but as I watch the generator load up, and then taper off down to absorb and float for hours, I start to wonder just how much savings that might be?
Thoughts?
Sean
P.S. I'm certain this has already be over-covered, so apologies.
Comments
-
Re: 24hr generator vs inverter/charger efficiency?
In Africa some years ago, they started a Hybrid power program for villages.
Most of the time, the village would run from a large battery bank+AC inverter. Then in the evenings, everyone home, lights, homework, cooking, etc., they would fire up the diesel genset and power the village and recharge the battery bank. I am not sure, but I think they saved about 50% on fuel vs genset running 24x7 without the battery bank+inverters.
We can hand wave all we want--But I would suggest building a relatively simple model of your electrical loads/pattern of usage, and then cost out the system to run it.
For the moment, fuel is almost 1/2 the cost it was less than 1 year ago, so generators will have a big help right now. And batteries/electronics are pretty much at a peak, and I don't see a big dip in battery prices at the moment (cost of energy is a fundamental driver of any manufactured product--Perhaps folks have seen some weakening of prices?).
And, ignore capital/maintenance costs at your own peril. New battery bank every 3-5 years (or 7-10 for more expensive batteries), new electronics every 10+ years, etc. are huge drivers of costs (buying a "new" solar power system every 6-10 years).
Gensets--How many hours do you expect to get? 6,000 hours on a small Honda eu2000i is possible. There are 8,766 Hours in a year--Looking at almost two "cheap" Honda gensets per year for 24x7 operation. Plus fuel costs.
How much for fuel:- 400 Watts * 9 hours * 1/1.1 gallons per tank = 3,273 kWH per gallon
- 8,742 hours per year * 1/9 hours * 1.1 gallons of fuel = 1,069 gallons per year
- 365.24 days per year * 0.4 kWatt genset * 24 hours per day = 3,506 kWH per year (at 400 watt average load)
- 1,069 gallons per year * $4.00 per gallon = $4,276 fuel costs per year
- 1,069 gallons per year * $2.20 per gallon = $2,352 fuel costs per year (cheap gas)
- $4,276 fuel costs per year / 3,506 kWH per year = $1.22 per kWH
- $2,352 fuel costs per year / 3,506 kWH per year = $0.67 per kWH
- ($4,276 fuel costs per year + $2,000 genset + $365 worth of oil) / 3,506 kWH per year = $1.89 per kWH
- ($2,352 fuel costs per year + $2,000 genset + $365 worth of oil) / 3,506 kWH per year = $1.35 per kWH (cheap fuel)
That is pretty much in the middle of the range of $1-$2+ per kWH that a solar power system seems to cost (every time I have added everything up and divided by power used). Yes, you can get less than $1.00 per kWH for solar power--A few people here have done that--But I would plan for higher cost for budgeting/planning.
Generator costs per year go down if the generator is not used (i.e., use 1/2 the time, about 1/2 the yearly costs).
With solar, works best with ~9 months of the year usage or more... If you use the system 1/2 of the year--The batteries and electronics are still aging and will probably not last that much longer not being used--So, the $/kWH costs actually go up with less usage for solar...
Having a genset running 24x7 is not ideal (noise, smoke, refueling, oil changes, etc.)... But the high initial capital and maintenance costs of solar are not either...
And why I always push knowing your loads and conservation first--No matter your choice of system power--Conservation (insulation, buying very efficient appliances, turning stuff off when not in use, etc.) is still your best investment. Anything else to generate power is probably going to cost a lot more.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: 24hr generator vs inverter/charger efficiency?
That's a lot to digest Bill... working on it
I guess I always figured that running a generator at much less than it's rated load (and load required) was very wasteful.
In an emergency situation, or even in an off-grid situation (as in my RV), I would cringe at the idea that my generator was running only to supply maybe 400w (as low as 100w at during sleeping hours).
This of course has to do with the fact that all generators have a zero load gph rating (which is seldom advertised), but one could assume that it's fuel economy is roughly it's zero load gph + the gph required load the alternator is producing.
At very low loads, the percentage of fuel being used simply to spin the engine of the generator vs gph required by the alternator increases. Whatever that percentage is... is lost energy.
So I looked at it like "ok, if that generator is only making 200w for 8hrs of the evening, but still requires .10gph to operate, then the majority of that is waste.
Yeah... that all makes sense... sorta...
So enter the inverter/charger.
In a perfect world every kw of generator output would be re-stored in the battery bank. We all know that the inverter itself has losses, but it's the charger losses that I'm wondering about at the moment.
For instance (I'll make up some numbers here), if it takes 2kwh of generator power to store 1kwh of DC energy in the bank, then I'm screwed. I don't know what those number are...even roughly.
What I do know is that the charging process is making heat in several places, and that heat is costing fuel, so it becomes an equation of if the heat wasted during charging is less than the wasted energy of a generator running prior to making output...etc.
I'm still chewing on the numbers you presented. In my case, the generator is @ 6000hrs and I expect another 6000hrs from it (Kubota D-105 diesel), and it costs about $1100 to rebuild....just for reference.
I am hopeful that your recollection of the 3rd world village story is correct. About 50% fuel savings equates to about $200/month for me (at current prices), but sometimes I get nervous at the idea that my generator is pumping fuel into heating batteries and inverter/chargers rather than doing something more useful. -
Re: 24hr generator vs inverter/charger efficiency?
For diesels, the conventional wisdom is that you should load them around 40% to 60% of rated load minimum... Or they can wet stack/glaze cylinder walls/build up carbon.
One poster here said that modern diesels (high tech, designed for reduced emissions, etc.) should not wet stack even at lighter loads.
From the olden days, it was a quick and dirty tactic (and probably very dangerous) to fill some 55 gallon drums with salt water and run electrodes in the tank--Basically boil water to keep the genset at 60% rated load.
Figure out what your minimum rated load (and maximum) for your genset should be (sometimes it is nothing more than a guess and use 40% as a minimum load for some calculations and see what pops out).
Diesel cycle is much more thermally efficient vs a normally aspirated gasoline/petrol engine. Gasoline engine fixed RPM gensets typically have their minimum fuel flow very need 50% of rated output capacity. For diesels, their fuel consumption continues to drop below 50% of rated load (very fuel efficient)--But the potential of running below 40% continuous may raise the maintenance/reliably issues... I don't know.
Do I like did above... Figure out your power needs and time frames they are needed. If your loads are very low outside dinner/evening time--A small battery+inverter system + genset for dinner time running/charging (plus solar, if you wish) can be a very viable system.
It really depends on your loads and usage history... Running a diesel at 50-80% fixed load (say irrigation)--A solar + battery bank is going to struggle to match the costs of the pure diesel solution (of course, price of fuel is a wild card). Solar is very expensive in up front capital costs, plus long term costs for battery/electronics replacement.
If your loads are 100 watts for 12 hours per day, 400 Watts for 8 hours per day, and 2,000+ watts for 4 hours per day--Then a mixed battery+inverter+diesel is probably quite viable.
Basically 400 watts from an inverter+battery+solar (if you wish), and the 2kWatts+ from genset.
Doing the paper designs/modeling can teach us a lot. Use the various rules of thumbs to get "close" to an optimum solution--Then look at the results and figure out if there are any things to change/adjust once you have the basic system sizing/information. All before you layout your first $$$.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: 24hr generator vs inverter/charger efficiency?
Just regarding Wet-Stacking of Diesel gensets ...
Have believed for many years that this this characteristic of Diesels has essentially vanished with the advent of Tier 3 and Tier 4 gensets.
Based this only on the observation of the behavior of my Tier 3 Kubota genset, placed on-line in 2007. It ONLY blows any "smoke" out of the exhaust on a cold start-up, and then it is for a fraction of a second. Running at less than half-load for an extended time period, and then almost fully-loading it also shows NO exhaust smoke whatsoever.
On the other hand, the old 1989 Diesel Dodge pickup blows blue-grey smoke when it has been idling for some time (but with coolant and oil at normal operating temp), and as a "ranch truck", it does not see highway use too often. Am certain that this is Wet-Stacking in action.
Am not an SAE Auto Engineer, but think that stacking can be observed by the amount and color of the exhaust, in an otherwise good engine, with good compression and no fuel system problems, etc.
My opinion, FWIW, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: 24hr generator vs inverter/charger efficiency?
My loads are 300w X 12hrs/day, 100w X 8hr/day, and 2000w/4hr day (not really, but closer to that).
I really need that Combox to rest my head. -
Re: 24hr generator vs inverter/charger efficiency?
i too think that wet stacking is less of a problem on newer diesel gen, i know some have a electronic governor to adjust the fuel to the load and keeping the voltage to within 0.5%, if you are trying to run a gen for primary power a 1800 rpm diesel is going to outlast a small inverter gen.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed