Trouble getting to 100% SOC
Dan_
Solar Expert Posts: 61 ✭✭✭✭
8 Interstate GC2-HD 208Ahr 6v in series charging from generator hooked to Outback FX3048 (panels arrive next week)
First time managing batteries so learning the ropes. Have been charging and monitoring SG for full and if not upping the absorb time. I typically take 50-60Ah then charge. Last absorb was 4 hours at 59.2v but got only to 51.2v and 1.265 SG (Interstate says 100% is 1.285 and 51.84v)
Should I up to 5hr absorb? What am I doing wrong? Haven't got the batteries to 100% since I've had them (2mos), are they damaged now? Glad I'm learning on the cheap batteries
As always, thank you for your guidance
First time managing batteries so learning the ropes. Have been charging and monitoring SG for full and if not upping the absorb time. I typically take 50-60Ah then charge. Last absorb was 4 hours at 59.2v but got only to 51.2v and 1.265 SG (Interstate says 100% is 1.285 and 51.84v)
Should I up to 5hr absorb? What am I doing wrong? Haven't got the batteries to 100% since I've had them (2mos), are they damaged now? Glad I'm learning on the cheap batteries
As always, thank you for your guidance
Comments
-
Re: Trouble getting to 100% SOCLast absorb was 4 hours at 59.2v but got only to 51.2v and 1.265 SG(Interstate says 100% is 1.285 and 51.84v)
-
Re: Trouble getting to 100% SOC
Sorry if I wasn't clear. What I meant was that I did 4 hours of absorb with a setpoint of 59.2 then let the batteries rest and tested the SG and voltage. They read 1.265 and 51.2v.
Interstate says a resting no load voltage of 51.84 approximates a full charge (6.48v per) -
Re: Trouble getting to 100% SOCSorry if I wasn't clear. What I meant was that I did 4 hours of absorb with a setpoint of 59.2 then let the batteries rest and tested the SG and voltage. They read 1.265 and 51.2v.
Interstate says a resting no load voltage of 51.84 approximates a full charge (6.48v per) -
Re: Trouble getting to 100% SOC
Just did a 5hr absorb at 59.2 . Tested after 30min rest. Voltage reads 52.2 (still needs stabilizing?) And SG is now only 1.250 some cells closer to 1.225
Near end of charge there was about 4A still going in to batteries. Is that about normal?
I need to call Interstate tomorrow to double check I'm looking at the right data -
Re: Trouble getting to 100% SOC
Well, the information is a little different this time. With the difference in the cells .25 SG level your probably going to have to do a Equalization. That is done at 61-62v for a hour at at time and then you check the SG level. This you do for as long as your still getting a rise on the lower cells SG level. GC-2's are are easy and you should see results in a hour or so. Your batteries are relatively new so it may be they have not completely formed their plates. You also have to watch the temperatures and not let them rise above 110 - 115 F. You also need to check the electrolyte level and add any water before you start.
If you don't understand this , post back. -
Re: Trouble getting to 100% SOCBlackcherry04 wrote: »You also need to check the electrolyte level and add any water before you start.
1. The electrolyte will expand as the temperature rises, but more important
2. The electrolyte will be full of gas bubbles which will raise the level.
You do not want to overflow the electrolyte in any cell during the process.
Also, since the batteries will be getting quite warm, make sure that your hydrometer readings are temperature compensated.SMA SB 3000, old BP panels. -
Re: Trouble getting to 100% SOC
Electrolyte levels are all good, just below or at bottom lip. Have not had to add any water in 2 months (charging every 3 days though).
Before this I was even charging at 61.2 as recommended by Interstate. Weird to have zero water loss
Can an eq be done with the batteries at any soc or only when full? I assume full is best but having issues getting there
Why didn't SG come back to previous reading? Too much absorb time? Still not enough? Higher voltage needed? -
Re: Trouble getting to 100% SOCElectrolyte levels are all good, just below or at bottom lip. Have not had to add any water in 2 months (charging every 3 days though).
Before this I was even charging at 61.2 as recommended by Interstate. Weird to have zero water loss
Can an eq be done with the batteries at any soc or only when full? I assume full is best but having issues getting there
Why didn't SG come back to previous reading? Too much absorb time? Still not enough? Higher voltage needed? -
Re: Trouble getting to 100% SOC
If you are not using any water--You may still be under charging them. Are they bubbling a little bit when they get fully charged?
Also, have you confirmed the charging voltages with a good DMM at the battery bank (and not just the meter on the charge controller)?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Trouble getting to 100% SOC
Here are the Interstate specs for GC2 HD http://www.interstatedealers.com/pdf/201535.pdf
57.6v bulk (not sure what that means since voltage is variable and increasing during bulk)
61.2v absorb
62.4v eq
I am using a Victron BMV-700S battery monitor which I've tested against a reliable multimeter. Outback FXs reading was high though but has been calibrated down with mate.
I've definitely done fewer than 30 cycles on the batteries. Is there a recommended process for new batteries to get plates to form? Haven't yet charged with caps off to check for bubbles but will next time. When charging at 61.2 though I can smell what I assume to be electrolyte gassing. Just weird not to see levels drop. -
Re: Trouble getting to 100% SOC
The battery specs are, as usual, not for solar use.
To be sure the battery is at full capacity you want to discharge/recharge repeatedly. Not partially on either side of the cycle: take them steadily down to at least 75% SOC and recharge fully. A bit of a problem if you're having trouble hitting 100% SOC. Always check charge state with a hydrometer; do not judge by Voltage alone.
The Interstates are not a good choice for RE because like Trojan and Surrette they want a rather high Absorb Voltage and that can be difficult to achieve in the limited amount of time available from the sun. -
Re: Trouble getting to 100% SOC
You won't get much of a answer why the Absorb is higher than the Bulk. I emailed them once because I thought it was a misprint. One of their engineers answered back that it was higher because of the Pure lead content of the HD plates. The plates are very thin, but there many more of them than a regular GC-2. I got those batteries as a trade-in on a new set I installed, they were less than a year old. I did as coot advised, I started to cycle them and did a couple EQ's on them and they were fine. I sold them and as far I know they are still working fine.not sure what that means since voltage is variable and increasing during bulk
I think the email was posted in a thread here several years ago. If you search there 100's
http://forum.solar-electric.com/showthread.php?10710-Absorption-voltage&highlight=Interstate+batteries -
Re: Trouble getting to 100% SOC
Interesting to read through that thread. I have contacted Interstate similarly and havent gotten the answers I'm looking for. Just about what I expected though given they're the cheapest option.
Hydrometer I've been using is East Penn temp calibrated. Should I even trust Interstates SG figure for 100% though?
So my issues are just related to the batteries being new and I should just cycle them more? Doesn't seem like I should go higher than 5 hours absorb...or should I? -
Re: Trouble getting to 100% SOCInteresting to read through that thread. I have contacted Interstate similarly and havent gotten the answers I'm looking for. Just about what I expected though given they're the cheapest option.
Hydrometer I've been using is East Penn temp calibrated. Should I even trust Interstates SG figure for 100% though?
So my issues are just related to the batteries being new and I should just cycle them more? Doesn't seem like I should go higher than 5 hours absorb...or should I? -
Re: Trouble getting to 100% SOC
Everyone's input is much appreciated thank you.
I read some discussion in other threads about discharging the batteries deeply to develop their plates when new. Is this advisable or should I stick with 30-40% DOD?
Is 1.265 the 100% mark or 1.285 as interstate claims?
I've done a few 2-4 hr 61.2v absorbs in the past. Any potential plate damage? -
Re: Trouble getting to 100% SOCEveryone's input is much appreciated thank you.
I read some discussion in other threads about discharging the batteries deeply to develop their plates when new. Is this advisable or should I stick with 30-40% DOD?
Is 1.265 the 100% mark or 1.285 as interstate claims?
I've done a few 2-4 hr 61.2v absorbs in the past. Any potential plate damage?
As to the SG, different batteries are provided when new with different SG electrolyte, and in some cases the documentation that accompanies the batteries does not catch up with changes in the supplied SG.
Some battery manufacturers also supply "tropical" versions of the same battery with a lower initial SG to compensate for the faster battery deterioration in high temperature environments. Or "cold weather" models with higher SG to provide more current capability in cold weather.
Too much vigorous "boiling" of a battery can cause deterioration of the positive plates and irreversible loss of electrode material, decreasing the capacity and shortening life. It becomes even more likely if the battery temperature is allowed to rise too high during EQ. Even cool gentle EQ (almost just extended Absorb) can cause water loss requiring more frequent refilling of the batteries.SMA SB 3000, old BP panels. -
Re: Trouble getting to 100% SOC
Just gave the bank a 3.2hr absorb at 59.2v. I opened the caps and indeed bubbles were coming to the top. SG before charge was about 1.210, after charge average cell SG is 1.240 (still very far away from the supposed 1.285 full). I was going to let the absorb go 4 hours but the current going in stayed steady at 4A for 10min so I turned off the generator. No load voltage reads 51.8v (which incidentally interstate says is 100%)
Thinking about doing an EQ at 62.4 for an hour tomorrow -
Re: Trouble getting to 100% SOC
I sure hope that SG reading of 1.400 is a typo.
Don't Equalize unless there is a significant discrepancy in SG between cells and you've already got at least some at "full". -
Re: Trouble getting to 100% SOC
Haha yes typo sorry
What I meant was 1.240 on average. One cell measured as low as 1.230 and one as high as 1.245 but most close to 1.240 (which still seems awfully low)
I'm still not sure if I have a faulty hydrometer, a faulty set of batteries or some fault with my procedure (doesn't seem like that). -
Re: Trouble getting to 100% SOC
1.240 is still too low, and the 'spread' of 0.015 between cells indicates a need for EQ.
Go for the equalization charge. -
Re: Trouble getting to 100% SOC
Alright will do
Looked up the warranty on the batteries and its 12mo free replacements so I still have 9mo to take them back if needed -
Re: Trouble getting to 100% SOC
Consumed 9Ahr since the last charge yesterday and just now did a 1hr EQ at 62.4v. I was curious whether the plastic battery casing would heat up at all but did not one bit; they were cooler than ambient air.
EQ seems to have evened out SG, all cells now read very close to 1.250
I bet if I was charging daily with shallower discharge (and then shorter absorb time) I'd probably be able to top it off to 100% but still yet to see it. Still no panels (hopefully this week though). Hate running the generator so only do it every 3 days or so
What's an appropriate ending amps to look for with GC2s. So far I've seen high 3s and 4A before time ran out. Some say 1-2% bank ahr so according to that either 2.1 - 4.2A -
Re: Trouble getting to 100% SOC
With Interstate GC2s I have found I need to use the recommended high voltages to get them to 100%. Running them with a grid interactive inverter didn't help either in the sell mode. As of late I have been charging, equalizing, and discharging to desulfate and get them equalized. Taking my limited experience into account they don't seem to be overly gassing using the recommended high voltages and don't seem to reach 100% soc unless I do use the higher voltages.
Just my 2 cents. -
Re: Trouble getting to 100% SOC
Much appreciated helpful to have other GC2 experiences. So by high voltage do you mean 7.65v per or 7.4v per or? -
Re: Trouble getting to 100% SOC
Currently 7.65 on absorb using end amps at 3 volts, but like you I have some uneven cell SOC readings I am trying to remedy and like you I didn't properly commission my bank. -
Re: Trouble getting to 100% SOC
Gave the bank a 3hr absorb today, ending amps were 4.5. Checked SG in two batteries. Within one all three cells read 1.250 and the other battery all 3 read 1.235 or thereabouts. Discrepancy probably because I haven't got the damn thing to full.
Finally got my panels. Have 2800w but have only setup 720w temporarily until I get poles in the ground. Only using about 500whr per day. Fingers crossed for finally getting to full and no more gasoline! -
Re: Trouble getting to 100% SOC
Been charging from solar the last few days. Wonderful to charge in silence and listen to the batteries bubble.
Everyday it seems like it's getting a full charge (I have end amps at 2) but SG is only at 1.260 (temp corrected). I believe some manufacturers consider this full or close to but Interstate says 1.285. Might have to up the voltage as verdigo does -
Re: Trouble getting to 100% SOC
The problem with Interstate is they have a lot of conflicting information out there. If the batteries were filled with 1.280 electrolyte then you'd have no problem getting to 1.285. On the other hand even with a EQ and massive over charge, I'v never been able to get 1.265 past 1.280. They are not clear about if their numbers are loaded or resting.
I found this today in what they term deep cycle batteries. To me their voltage is off and the SG levels sure are.
Attachment not found. -
Re: Trouble getting to 100% SOC
Looks like a generic chart to me: resting Voltage and SG.
Interstate unfortunately has batteries that are like Trojan and Surrette: high Voltage compared to mainstream. 15+ Volts for Absorb! Not a good thing for your basic 12 Volt system with a typical inexpensive inverter that will be screaming "over Voltage" every day at that level, never mind EQ.
One reason why I don't like Interstate batteries. -
Re: Trouble getting to 100% SOC
No way I will be buying cheapo GC2s again but they're so tempting given the price and local availability. Interstate seems specifically bad. How can a battery company be clueless about their batteries?
I was suspect as well about the electrolyte numbers given. Attached is their spec sheet though
I'm having a discrepancy between what my Victron battery meter (shunt) is reading vs what the Outback FM says. Currently 2.18A shown at the shunt but FM says 3A. I don't have the outback dc meter too expensive. Should I not use the end amps feature because of this?
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed