two separate PV arrays - should I use one or two controllers?
petefink
Registered Users Posts: 6 ✭
just starting design but have been getting conflicting advice. plant to have one 2 x2 PV array (100 watt 12 V panels) at an adjustable tilt from 0 deg to 70deg and another 1 x2 array (same panels) at a fixed 12 deg from horizontal. Arrays are separated by about 30 feet but both are same southern orientation. Plan to have three 1x2 series strings for nominal 24 V each (two strings on the tiltable array and one string on the fixed array). Plan to use one 12 or 24 v battery bank. Should I use one (larger) MPPT controller for both arrays or two (smaller) MPPT controllers - one for the 1x4 tiltable and one for the 1x2 fixed? Or doesn't it make much difference (in which case I'll go with cheapest alternative). Thank you. Peter
Comments
-
Re: two separate PV arrays - should I use one or two controllers?
Welcome to the forum Peter.
So on the tilting mount you will have four 100 Watt panels configured as two parallel strings of two in series. On the fixed mount you will have two 100 Watt panels configured as one string of two in series.
There is no reason you can not parallel all three strings to one charge controller. It should be capable of >20 Amps @ 24 Volts or >40 Amps @ 12 Volts. If I were you I'd go with the 24 Volt system; it's more efficient and one MidNite Kid would handle the job for about $300. -
Re: two separate PV arrays - should I use one or two controllers?
If you are using Vmp-array ~ 35-38 volts on a PWM controller and a 24 volt battery bank--There is no reason to use separate charge controllers.
If you are using Vmp-array ~35-38 volts (or higher) on a 12 volt battery bank, then you need to use an MPPT charge controller...
Basically you want Vmp-array~18 volts for charging a 12 volt battery bank or Vmp-array~36 volts to charge a 24 volt battery bank with a PWM controller.
If you are using an MPPT type charge controller (which can take higher voltage/lower current and efficiently down convert to low voltage/high current used to charge the battery bank), the recommendation is to use one MPPT controller for each "plane" of solar array. The MPPT controller "tracks" the Vmp-array voltage and with two arrays mounted different orientations (or one tracking as in your case), their temperatures will be different and cause a loss of voltage tracking and efficiency (two arrays with different Vmp-array voltage, there is no "one perfect" voltage).
Personally, if costs are important (and they usually are), I would try one MPPT controller on the two arrays and see how it performs. It won't hurt anything.
Also, I moved your post to the "Beginners Forum" (not the Announcement Forum).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: two separate PV arrays - should I use one or two controllers?
thanks for the advice and the move, peter -
Re: two separate PV arrays - should I use one or two controllers?
thanks for the help, peter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed