Cable voltage drop
gactrx
Solar Expert Posts: 72 ✭✭
Hi have change the position I will put my controller and it's now 26 meters from the PV array junction box. I have 16mm2 two core cable (about 5 AWG) for this. The rated current of the panels is 26 amps and VMP is 73.8 volts.
I'm not sure what figures to use for the voltage drop calculation to check on the distance and if it's ok. The controller is the Classic 150 and I'm charging a 24 volt battery bank. If I put the panels in the other configuration I have it's two strings of three panels which is marginal for voltage.
With the longer distance, will the panels in low light and therefore low voltage output not be as efficient as voltage drop increases
Thanks,
Thanks,
Re: Cable voltage dropAlaska Man wrote: »
Thanks, I did try that but wasn't sure which figures to use. Is it correct to use the rated current and VMP voltage?
Is this acceptable:
Voltage drop: 1.39
Voltage drop percentage: 1.88%
Voltage at the end: 72.41
Is it borderline, great, or average?
Cheers, -
g
That looks good to me. Most try for under 3% drop so at 1.8% you are doing very well.
gww -
Re: Cable voltage dropWith the longer distance, will the panels in low light and therefore low voltage output not be as efficient as voltage drop increases
The light level is irrelevant. The voltage is about the same at all light levels. It's the current that decreases with low light levels.
Also at low current the wire should be even better. You losses are considered at the max current.
gww -
Thanks very much, that sounds good.
Cheers.