Panel Mounting on a pole barn
JohnWilliams
Registered Users Posts: 5 ✭
I am building an off-grid system for my pole barn, which has modest electrical needs at this point (1 KWh/day measured with a Kill-a-watt) but will have higher needs later (eventual small shop). My building is too far away from the electrical pole to be feasible for an underground grid feed.
Initially I have a RV2012 inverter that I kept when I sold my RV. My plan is to eventually go to a XW4024 or 4048 in a year or two so I can get split phase and overload auto gen start and generator load sharing for heavy loads. Will probably look for a 4K Onan from an RV, but that is another thread...
Thus I am sizing the PV so that I can expand to 24 or 48 volts later. I plan to use a MPPT controller so that I can start deploying 250Wish panels. I will start with 2 or 3 panels to give me 750W of PV which is about the max for MPPT at 12V (depending on which controller I pick (Leaning towards Schneider 150-60 for eventual Xanbus with the xw inverter).
Now - the question. I have 2 options for PV mounting. I have 2 metal roof barns with suitable locations, about 100ft apart.
The shop barn (E/W roof with 3/12 pitch, metal) only allows an east facing orientation (due to shading mid afternoon on the west side) at 22 degrees of incline with the panels flat on the roof. Using PVWatts (So. Ill location), this shows 1057 KWh/yr (@ 1kw PV size). I ran PVWatts for 38.8 degrees due south and see 1266 KWh/yr. Roughly 200 KWh more. To do this I would have to elevate the north side of the panel off the roof with some sort of triangular mount. This would make the array much more at risk for high winds from the north. I am guessing this is not worth the risk. So, flat it is at 1057 KWh/yr. Shading is a concern. Now I don't see east shading until 4pm. In Winter may see shading shortly after noon. A worry.
The livestock barn is 100ft east of the shop with E/W slopes also, with a 4/12 pitch, but good unshaded west side exposure year round. So, I could place 1/2 the panels on the east side towards the peak, and 1/2 on the west side. PVwatts shows a combined number of 1083 KWh/yr. That number alone does not cause me to want to place them there, (more difficult install and have to run 125ft of wire underground to the inverter/battery location. However, I have been reading about east/west orientations being beneficial in less than optimal conditions, and the guarantee of no shading has me seriously considering this.
What would you do?
John
Initially I have a RV2012 inverter that I kept when I sold my RV. My plan is to eventually go to a XW4024 or 4048 in a year or two so I can get split phase and overload auto gen start and generator load sharing for heavy loads. Will probably look for a 4K Onan from an RV, but that is another thread...
Thus I am sizing the PV so that I can expand to 24 or 48 volts later. I plan to use a MPPT controller so that I can start deploying 250Wish panels. I will start with 2 or 3 panels to give me 750W of PV which is about the max for MPPT at 12V (depending on which controller I pick (Leaning towards Schneider 150-60 for eventual Xanbus with the xw inverter).
Now - the question. I have 2 options for PV mounting. I have 2 metal roof barns with suitable locations, about 100ft apart.
The shop barn (E/W roof with 3/12 pitch, metal) only allows an east facing orientation (due to shading mid afternoon on the west side) at 22 degrees of incline with the panels flat on the roof. Using PVWatts (So. Ill location), this shows 1057 KWh/yr (@ 1kw PV size). I ran PVWatts for 38.8 degrees due south and see 1266 KWh/yr. Roughly 200 KWh more. To do this I would have to elevate the north side of the panel off the roof with some sort of triangular mount. This would make the array much more at risk for high winds from the north. I am guessing this is not worth the risk. So, flat it is at 1057 KWh/yr. Shading is a concern. Now I don't see east shading until 4pm. In Winter may see shading shortly after noon. A worry.
The livestock barn is 100ft east of the shop with E/W slopes also, with a 4/12 pitch, but good unshaded west side exposure year round. So, I could place 1/2 the panels on the east side towards the peak, and 1/2 on the west side. PVwatts shows a combined number of 1083 KWh/yr. That number alone does not cause me to want to place them there, (more difficult install and have to run 125ft of wire underground to the inverter/battery location. However, I have been reading about east/west orientations being beneficial in less than optimal conditions, and the guarantee of no shading has me seriously considering this.
What would you do?
John
Comments
-
Re: Panel Mounting on a pole barn
My panels are mounted do south on the gable end of the house. If your roof slopes are East and West couldn't you mount them facing South or in a Southerly direction on the gable? Adding one more panel would make up for any loss you would have because they are straight up vertical. I have 4 Panels in the 250W range on one Midnight Classic 150. Two strings of two keeps me under the hyperVOC limit of the C.C. Just a thought.
It's also a protected spot up against the building and under the roof overhang. I don't have to worry about snow. -
Re: Panel Mounting on a pole barn
As an example:
I actually have these mounted with a hinge on the top because it's easy for me to step out and angle them during the summer. Having done this I can tell you I only see about a 250W (One Panel) increase in the power produced when they are 90° to the sun.
Attachment not found. -
Re: Panel Mounting on a pole barn
Have you considered using the livestock barn for the entire installation (including inverter and battery bank), then running 120VAC power the 125' to the shop barn? That would give you much less voltage drop, using a much smaller/less expensive wire gauge. -
Re: Panel Mounting on a pole barnHave you considered using the livestock barn for the entire installation (including inverter and battery bank), then running 120VAC power the 125' to the shop barn? That would give you much less voltage drop, using a much smaller/less expensive wire gauge.
Thought about that but a bit worried about increased fire hazard with batteries in the barn. We have horses that stay in stalls at night in the winter. Also have hay stored upstairs in a loft. I think keeping the power center in the shop is safer overall. I can run THHN 4 or 6 AWG over to the shop and carry a full 60 amps. If I upgrade to 48 volts, that gives me 3K watt capability on 1 controller.
John -
Re: Panel Mounting on a pole barnAlaska Man wrote: »My panels are mounted do south on the gable end of the house. If your roof slopes are East and West couldn't you mount them facing South or in a Southerly direction on the gable? Adding one more panel would make up for any loss you would have because they are straight up vertical. I have 4 Panels in the 250W range on one Midnight Classic 150. Two strings of two keeps me under the hyperVOC limit of the C.C. Just a thought.
It's also a protected spot up against the building and under the roof overhang. I don't have to worry about snow.
South Gable has a large 12ft door that slides all the way across the end and is shaded more than 50% of the day. -
Re: Panel Mounting on a pole barnJohnWilliams wrote: »I can run THHN 4 or 6 AWG over to the shop and carry a full 60 amps.SMA SB 3000, old BP panels.
-
Re: Panel Mounting on a pole barn
And 1/4 the wire diameter (surface area) is 6 AWG smaller (instead of 2 AWG wire, you can use 8 AWG wire).
3 AWG change in wire gauge is 1/2 the square inches/mm of a cut wire (1/2 the amount of copper per unit length of wire).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Panel Mounting on a pole barn
Thanks for the info. I picked 4 AWG (at 75 C degrees heating) or 6 AWG (at 90 C degrees heating) for a max 60 amp run of 125 ft in buried conduit. I am sizing this for a 24v or most likely 48v system. At the start, I will be running my RV2012 with 3 250W Canadian Solar panels. Using a MPPT controller, you would never actually run 60 amps except on a record cold day, right? More like 50-55 amps... What size wire CU should I run? Am I overkill or under-sized?
A second idea is to mount the 3 panels on the shop roof just because it is easier and then when I upgrade to 4000 watts or more, move to the livestock barn. I am really leaning towards 48V, when I do.
This first system is mostly a trial system to help me understand the operational concepts, as well as learn the care and feeding of a battery bank...
John
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed