Panel Configuration Diagram--Input Needed
semsoblue
semsoblue Registered Users Posts: 12
Guys,
I've attached a diagram of my panel, and the components I'm using in my system. Thinking about making some changes, and I am guessing there are some adjustments that could be made. Let me know what you think.Attachment not found.
    BB. Super Moderators, Administrators Posts: 33,734 admin
    Re: Panel Configuration Diagram--Input Needed
    Each positive cable that leaves the + battery bus should have its own fuse/breaker per wire (or group of wires).
    Use your local electric code for current capabilities of the cables (don't know if you use AWG, mm, or mm2.
    The idea is if there is a short circuit anywhere in your system, the fuse/breaker will open before any wiring catches fire.
    A large fuse on a single string of batteries is usually not done if you have heavy battery interconnect cables.
    Also, do you have the DC battery bank is negative grounding to the building AC safety/green wire ground? This is to prevent the negative bus from becoming "hot" (-12 volts). If you have a floating battery bank, you are supposed to have a fuses on both + and - wiring (2x more fuses /breakers). But many people do not do that.
    With fusing/breakers--They really are never used if all is working well. They are only there IF something goes wrong. Having a dead short on a large battery bank can be very exciting.
    This video (2nd half) shows what 300 amps at 12 volts can do to a nail/screw/bolt in a short circuit:
    If the system uses grid power for charging (not on a generator), I would suggest you get the IQ4 module for your Iota. And monitor your water usage in the flooded cell batteries (too much water usage, back the charging/float voltage down; too little water usage, crank of the voltage a bit).
  • semsoblue
    I've attached another diagram showing the connections between the buss bars and the breakers (the actual breakers I'm using). Do I need additional fusing before these breakers? I'd be using #8, probably about 12-18" between the bars and the breakers. With this setup and these types of breakers, would I still need to ground the negative to the house ground?
    Also, did I understand you to say that the 125A fuse from the battery bank to the buss bars is not needed?
    I do have an IQ4 installed. I charge with the IOTA from the grid, but also from the generator when the community power is down. Does that affect the IQ4 or IOTA? Thanks!Attachment not found.
    semsoblue wrote: »
    I could not tell the Amp Rating of the breakers--But using two pole breakers, you do not "need" to negative ground the battery bus (floating outputs with breakers on both +&- wiring is perfect from a safety point of view).
    For 8 AWG wire, in the US we would run a breaker of 40-50 amps (NEC) to 60-80 amps (ABYC).
    If the total of your DC Branch circuit breakers is less than 125 amps, then you do not need the battery bus breaker.
    if the total of breaker is over 125 amps, then you can use the 125 amp breaker on the battery connection (note, see above charts, 2 AWG cable can carry roughly 95-130 to 280-330 amps--Conservative to not very conservative).
    The IQ4 is useful when the power supply has a, more or less, continuous AC power supply (grid). If you are running the generator only X hours per day--Then the IQ4 does not help much (or hurt). Once the battery is over 80% state of charge (or over 90-95% SOC, your choice), most people would be turning off the genset to conserve fuel.
    The IQ4 will drop the voltage back to "float" voltage if the AC power was on 24x7 and the Iota was set to "Absorb Voltage", the battery would over charge and (for AGM) eventual vent and/or boil dry (flooded cell).
  • semsoblue
    Thanks Bill! I'm considering adding a battery switch, simple on-off, to be able to turn everything off at the panel. As I am using 2awg battery cable, 450ah battery bank, I didn't know which size. Would this work? http://www.solar-electric.com/blseabaswon3.html
    I have always been leary of "twist type" battery switches. From an engineering point of view, easy to have arcing if switched under load. Also, there have been reports that the switches do not really do well if subjected to heavy/continuous current (OK for a starting motor, not OK for a 200 Amp draw by an AC inverter for hours on end).
    If you can swing it--I would suggest a properly rated DC Circuit Breaker for your battery switch.
    http://www.solar-electric.com/installation-parts-and-equipment/midnite/cipr1/high-amperage-inverter-breakers.html
    Just some observations on the Blue Sea switch from someone who has used one for six years with no problems.
    First, understand that they are really a disconnect. Switching them on/off under load is not recommended. If you're paranoid about arcing during capacitor charge on start-up you can install a push button switch in parallel to handle the arc consequences, but it really isn't necessary.
    Second, 200 Amps continuous on a 12 Volt system is 2400 Watts which is more power than a 12 Volt system should have on it. 200 Amps continuous of a 24 Volt system is 4800 Watts which is more power than a 24 Volt system should have on it (my system is fused at 150 Amps - kids managed to blow the fuse this year). These switches are not for 48 Volt systems. The switches are rated for 300 Amps. Normally my system doesn't draw more than 50.
    Third, if you look at the very few instances of failure you'll find they they occur when people ignore the first two points.
    Fourth, I use this because both the switch and the terminal post fuses are inexpensive compared to DC breakers of equivalent strength and can be had fairly easily from most boat equipment dealers (which we have right in town - rather than order and wait for something to arrive).
  • inetdog
    If you search the internet, you can see some horror stories and films of what happens when you run high current through look-alike round battery switches which are NOT Blue Sea. The meltdowns can be spectacular.
    SMA SB 3000, old BP panels.
    inetdog wrote: »
    Oh yes. I pulled one of those no-name (Princess Auto) supposed 500 Amp switches from a system; burnt up without the inverter even being loaded.