Cant put load on system
machineman
Solar Expert Posts: 129 ✭✭✭
Just got up to my cabin and seems I can't put a load more than a few lights on my system or it will crash. Voltage is good >26VDC. If I turn on the fridge the voltage drops to zero and the inverter shuts down. I have a Magnum 4024 inverter and 8 6V batterys totaling 440 amp hours at 24VDC. Is my inverter dead or my batterys?
Off Grid Cabin, 24V 440ah 6V GC battery bank, Xantrex MPPT60-150 CC, Magnum MS4024 inverter-charger, >1200w Solar bank
Comments
-
Re: Cant put load on systemmachineman wrote: »Just got up to my cabin and seems I can't put a load more than a few lights on my system or it will crash. Voltage is good >26VDC. If I turn on the fridge the voltage drops to zero and the inverter shuts down. I have a Magnum 4024 inverter and 8 6V batterys totaling 440 amp hours at 24VDC. Is my inverter dead or my batterys?
If the batteries were left too long without charging they will be sulfated and probably not recoverable. At least check the SG and the water level to see if you have an obvious problem like one bad cell in your battery bank.SMA SB 3000, old BP panels. -
Re: Cant put load on system
The Voltage drops to zero measured where and how? AC Voltage? DC Voltage?
You need to put a meter on the batteries and see if they are actually dropping or if the inverter input is showing low Voltage; it could be bad wiring between the two causing excessive V-drop.
If it is the AC output that just drops then we need to know if the inverter is staying on or a fault is triggering it to shut off. If it is on and has zero AC output Voltage under load then the inverter has died. If a heavy load is triggering a fault shut down of the inverter you have to determine what the fault is. -
Re: Cant put load on system
Could also be bad electrical connections to the batteries (loose/dirty/corrosion)--If it is the DC voltage collapsing.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Cant put load on system
I see the voltage drop to zero on my trimetric and the inverter shuts off probably because it reaches the Low voltage cut. The flooded batterys are over 5 years old and my water maintenance hasn't been that good. But I only visit this place one weekend a month so the solar has been keeping them charged while Im gone. If I measure the voltage on each battery it ranges from 6.5 to 8.0 volts. I have 2 banks of 24V in parallel and I've tried each bank by itself hooked up to the inverter and same issue. So if its the batterys then more than one of them is messed up. Or the inverter cant handle a load anymore than a few light.Off Grid Cabin, 24V 440ah 6V GC battery bank, Xantrex MPPT60-150 CC, Magnum MS4024 inverter-charger, >1200w Solar bank
-
Re: Cant put load on system
Reading 8 Volts on a 6 Volt battery is a clear indication of a problem: it means one of the batteries in that string is very low which forces the Voltage on another (or all others) high. 8 Volts indicates a possible shorted cell.
Flooded cells = get the hydrometer out and check each one for SG. I suspect you will find significant imbalance on more than one.
Inverters don't suddenly drop from being able to handle full output to being able to handle only partial output. Batteries do. Most likely given the age and symptoms the whole bank is scrap metal. -
Re: Cant put load on system
6.5 to 8 volts on batteries--Something is wrong. The 8 volt battery may have, for example, an open cell (if this is voltage during charging) and the 6.5 volt battery near dead (or 1/2 charged--don't know from what you have here).
Or, the 6.5 volt battery may have a shorted cell--Together they add up to 14.5 volts volts--A very reasonable charging voltage. But the 8 volt battery would be getting "way over charged" (equivalent to 16 volts on a 12 volt battery bank).
You may have to mix/match batteries to get a single string that will keep you going for a while. If you had a DC Current Clamp DMM, you could tell if the problem is an open or shorted cell (almost no current flow, or a lot of current flow).
I have "cheated before" by setting a DMM to 2 volt (or 200 mVolt scale) and measure the voltage drop across a battery interconnect cable. The voltage drop will be proportional to the current flow--And if you have the same length jumper in different strings--The are your "current shunt/power resistor" to measure voltage drop on between string.
A cheap hydrometer (if you can get one locally at an auto-parts store--a glass float version if they have it) will help you weed out bad cells/batteries too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Cant put load on system
Measured the SG. 2 Banks of 4 6V batterys in parallel. I've tried both banks separately and same voltage drop out issue under load. Clearly there is one bad battery in bank 1 but bank 2 has same issue if isolated from bank 1.
Bank1
1180
1150
1250
1230
1230
1230
1235
1235
1245
1240
1235
1235
Bank 2
1260
1225
1250
1265
1270
1260
1250
1230
1225
1265
1250
1265Off Grid Cabin, 24V 440ah 6V GC battery bank, Xantrex MPPT60-150 CC, Magnum MS4024 inverter-charger, >1200w Solar bank
-
Re: Cant put load on systemmachineman wrote: »Bank1
1180
1150
1250
That battery is in trouble. It has a problem with that first cell.1230
1230
1230
1235
1235
1245
1240
1235
1235
These three are far from charged with minor cell imbalance.Bank 2
1260
1225
1250
Another battery in trouble; the middle cell is very low compared to the first.1265
1270
1260
Best battery in the bunch, and it shows the others are dying because this one clearly is not and they were all part of the same charge routine.1250
1230
1225
Another with significant imbalance.1265
1250
1265
Second best, and as before indicative of over-all failure.
Have you got a 12 Volt charger you can use to try and bring pairs up with? The total imbalance for Bank 1 is 0.070 and for Bank 2 0.045. Bank 1 should not be charged as a unit if possible, and Bank 2 is pretty dicey.
Don't get your hopes up. -
Re: Cant put load on system
I've tried isolating Bank 1 and only running on Bank 2 and have the same issue. I know the batterys are tired but is Bank 2 alone bad enough to cause this issue? I want to troubleshoot this thing so I know what parts to bring up next time I visit. Still not convinced yet that the invert doesn't have a problem.
Thanks,Off Grid Cabin, 24V 440ah 6V GC battery bank, Xantrex MPPT60-150 CC, Magnum MS4024 inverter-charger, >1200w Solar bank
-
Re: Cant put load on systemmachineman wrote: »I've tried isolating Bank 1 and only running on Bank 2 and have the same issue. I know the batterys are tired but is Bank 2 alone bad enough to cause this issue? I want to troubleshoot this thing so I know what parts to bring up next time I visit. Still not convinced yet that the invert doesn't have a problem.
Thanks,
Use Bank 2.
Check Voltage at battery terminals and at inverter input.
Load inverter with something it can handle and recheck Voltage at both points.
Increase load and check Voltage at both points again: you're looking to see if the two points change equally or if the inverter input falls off more drastically.
Load the inverter until it faults while watching Voltage at batteries. Do the same thin while watching Voltage at inverter.
If the inverter is shutting down for low Voltage then when it does so the input V at the inverter (and at the batteries if it isn't due to wire loss) should actually be low as read by the DMM. If it isn't, the inverter is not 'interpreting' the Voltage correctly and is at fault.
At this point I don't want to say this is the third Magnum failure I've heard about in the past three months. -
Re: Cant put load on systemmachineman wrote: »Still not convinced yet that the invert doesn't have a problem.
The inverter may well have a problem, but if it does, then you have two different problems, because your battery bank is frigged.
The only way to properly check your inverter is with a known good battery bank, and that's something you unfortunately do not have.
I strongly suspect that when the batteries are replaced you'll find the inverter will work fine.
I went through basically the same thing when my 3 parallel strings of 11 year old batteries were finally dieing. Light loads were still fine, but anything heavy sagged battery voltage badly, and of course the inverter shut down, as it should.
Wishing you best of luck. -
Re: Cant put load on systemCariboocoot wrote: »
At this point I don't want to say this is the third Magnum failure I've heard about in the past three months.
I rather hope it isn't an inverter problem as I also have just installed a new Magnum MSH4024M and would hate to think it unreliable. It *seems* well made and is silent.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed