6.5kw solar system with a 20kw briggs standby generator
![jer19545](https://w1.vanillicon.com/1921a824c5464418fc8896889ee617f2_100.png)
jer19545
Registered Users Posts: 4
i have a 6.5kw solar system by sunpro, & a 20kw briggs straton natural gas standby generator. the question is when the power goes out & the solar is producing electricity, will the generator transfer switch crank the generator? i've been told yes, no, & maybe. anybody out there know for sure? thanks john
Comments
-
Re: 6.5kw solar system with a 20kw briggs standby generator
Welcome to the forum John.
The only one who can tell you if your gen will automatically start when the power is out is the installer. Or possibly not as this should have been outlined for you to begin with.
There are several different types of system. For example if this is a straightforward grid-tie system when the grid goes down the inverter stops producing; the generator starts and supplies all power. It will not be coupled to the solar.
But if this is a hybrid system then when the power goes out the batteries take over. If they get too low the gen should start to provide both load power and charging. In some cases such a system could have "gen support" where the inverter and generator can both provide power, although given the generator size this would likely be unnecessary.
The transfer switch doesn't "crank the generator" per se; it will provide a signal to the gen that grid power has been lost and it should start. When it has the transfer switch will engage the loads to the generator. This is if it is auto-start. -
Re: 6.5kw solar system with a 20kw briggs standby generator
Welcome to the forum John!
First question... Your 6.5 kWatt solar system is a Grid Tied Inverter based system (solar panels + GT Inverter, no battery bank).
These system work in parallel with the Utility Power... When you have 120/240 VAC and 60 Hz power, the GT inverter "syncs" with the AC mains and simply pumps energy into your home's power lines--Which goes to support local AC appliances, and if there is extra power, goes out the AC mains and turns your utility meter "backwards" (assuming you have a Utility Net Metering agreement and the correct utility meter).
If you lose utility power, the GT inverter system will shut down too. No AC utility power, no GT solar power.
Now--You toss in an AC generator. You have two places that the generator transfer switch can be installed relatively to the GT Inverter's connection.
The "standard" installation would be:
AC mains + GT Inverter -> Transfer Switch -> Generator + "protected loads" (loads that the generator runs.
A second method would be:
AC mains -> Transfer Switch -> Generator + GT Inverter + "protected loads" (loads that the generator runs.
The AC mains would go down (so with GT solar), then the transfer switch starts the genset and then connects the sub panel with the protected loads. Generator voltage/frequency, if withing the GT inverter's specification, will allow the GT inverter to sync and start feeding power to the grid... And then the fun begins...
First, the voltage/frequency/waveform needs to be qualified and stable for >5 minutes by the GT inverter before it turns on. The frequency is +/- 0.5 Hz or so--And many generators can drift outside of that frequency tolerance range... So, the GT inverter may never "turn on" if the generator frequency wanders too much (not all generators can hold these tight frequency tolerances).
Second, the GT inverter turns on and starts feeding ~5-6 kWatts or so into the protected sub panel. If your loads are greater than the GT inverter's output, all is "OK". However, if the loads are less than the GT inverter's power output, the extra power will try to "run backwards" through the generator. That is not a good thing.
The generator could over speed (and shut down the GT inverter for fine minutes/fault the genertor), could over voltage (shut down GT inverter for five minutes/fault generator), or start feeding current backwards through the alternator/regulator (and possibly let the magic smoke out of the generator).
At this point, I do not know if a good/safe/reliable method to make a pure GT Inverter + Generator play together unless you are going to somehow actively manage your loads to prevent the GT inverter from backfeeding your genset.
There are other methods that can be done to make solar+generator play together nicely... But that usually involves a "Hybrid" AC inverter (GT+off grid capable AC inverter) and battery bank. This can be expensive and may not be cost effective if your power failures are rare/short term.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: 6.5kw solar system with a 20kw briggs standby generator
thanks, one question when the power goes out the gt inverter stops producing a/c, the generator starts producing a/c, the gt inverter knows not to produce a/c till the commercial power is restored? how????????? -
Re: 6.5kw solar system with a 20kw briggs standby generator
sorry, i didn't answer your first question. gt inverter, no battery. i'm going to assume the gt inverter will tie in to the line side of the transfer switch & the generator to the load side. -
Re: 6.5kw solar system with a 20kw briggs standby generatorthanks, one question when the power goes out the gt inverter stops producing a/c, the generator starts producing a/c, the gt inverter knows not to produce a/c till the commercial power is restored? how?????????
It all depends on where the GTI connects to the wiring:
GRID --- GTI ---- TRANSFER SWITCH/GEN INPUT ---- LOADS
Grid goes down, transfer switch changes loads from grid & GTI to gen output. -
Re: 6.5kw solar system with a 20kw briggs standby generator
right now, the generator & transfer switch are not yet installed, the GTI is connected to a 30amp 240v breaker in the mail breaker panel. the question is when the generator & transfer switch is installed, will i connect the GTI to the line side of the transfer switch. i have a licensed electrician that will connect the generator, i'm just tiring to get me head wrapped around this install. i'm looking for the questions to ask the electrician. thanks john -
Re: 6.5kw solar system with a 20kw briggs standby generator
You don't want the GTI to connect to the generator as per Bill's explanation.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed