primary neutral
The lower wire on my single phase grid service is the neutral...hot on top 7200 volts. surprisingly small wire..
anyway that neutral is tied to all the grounds on the poles ,un insulated and copper right into the dirt.
If the neutral could be described as an overflow wire for excessive or unbalanced current then why cant you get a shock from the
un insulared and easy to touch ground wires attached to the neutral.????
    Re: primary neutral
    ws9876 wrote: »
    You don't need large wire for high Voltage; you need it for high current.
    No circuit path. Birds can light on that 7200 Volt line (which also may not be insulated) without problem because they don't create a circuit between it and the other half of the power line. Likewise the 'neutral' is bonded to ground so there's no path between it or ground and the other side of the power - the 7200 Volt line - when you touch it.
    This is why we use 240 VAC split-phase: it makes household wiring simple with only one breaker required to shut off the 120 VAC lines.
  • DanS26
    DanS26 Solar Expert Posts: 273 ✭✭✭
    Re: primary neutral
    Maybe this will help.....
    http://en.wikipedia.org/wiki/Electricity_distribution
    23.16kW Kyocera panels; 2 Fronius 7.5kW inverters; Nyle hot water; Steffes ETS; Great Lakes RO; Generac 10kW w/ATS, TED Pro & Emporia System monitoring
  • inetdog
    Re: primary neutral
    But birds with long wingspans, like the California Condor sometimes touch both wires at the same time.
    SMA SB 3000, old BP panels.
    Re: primary neutral
    inetdog wrote: »
    We have the same problem with the pterodactyls here.
  • DanS26
    Re: primary neutral
    Try this....take a multimeter out to your utility pole....set it to record AC millivolts.....touch one contact to the grounding wire coming down the pole.....and stick the other in the ground anywhere.
    You will read voltage and it will represent the resistance in the ground return wire to the utility substation. The measurement will be small and that is why you do not get shocked. Now if the amount is a few volts then that means that the utility return line has higher resistance. If the resistance (ie volt reading) is very high then the utility should be notified.
    Do this same test on the GEC on your house wiring....voltage is always there...although in small amounts. The reason is that electricity will take all paths to source.
  • ggunn
    Re: primary neutral
    inetdog wrote: »
    Fried condor, yum! :D
    Re: primary neutral
    Up North , here iin BC it is Osprey that suffer that fate due to a likeness to roost on the cross bars:confused: