Need help putting solar RV components together
John
Registered Users Posts: 1
I'm putting together a small solar system in my tent camper. I have few questions about size cable, fuses, circuit breakers and layout. This is a list of materials I have:
* 1 kyocera 140 watt panel with MC4 connection and 100' 10AWG solarline cable.
* 1 Morning Star/Tristar MPPT-30 AMP controller.
* 2 Trojan T-105 batteries and 6AWG wire with connectors.
* 1 MidNite/BigBaby circuit. box and 1 12A & 5 30A CKT. breakers.
* 1 Samlex 1500 inverter and 2/0 welding cable.
* 1 Tri-Metric TM-2025-RV battery monitor and #18 wire.
* 1 500 AMP Shunt
My questions:
1-My 2/0 cable is too large for the Connection on the inverter?
2-Where do I place the circuit Breakers?
3-Where do I get a simple diagram for this system?
* 1 kyocera 140 watt panel with MC4 connection and 100' 10AWG solarline cable.
* 1 Morning Star/Tristar MPPT-30 AMP controller.
* 2 Trojan T-105 batteries and 6AWG wire with connectors.
* 1 MidNite/BigBaby circuit. box and 1 12A & 5 30A CKT. breakers.
* 1 Samlex 1500 inverter and 2/0 welding cable.
* 1 Tri-Metric TM-2025-RV battery monitor and #18 wire.
* 1 500 AMP Shunt
My questions:
1-My 2/0 cable is too large for the Connection on the inverter?
2-Where do I place the circuit Breakers?
3-Where do I get a simple diagram for this system?
Comments
-
Re: Need help putting solar RV components together
Look to page 17 in this document for questions 2 and 3
Re the 2/0 wire, what does the manual say?
hth
OOPs forgot to attach this http://www.midnitesolar.com/pdfs/epanelManual.pdf
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Need help putting solar RV components together
Welcome to the forum John.
I hope you realize that one 140 Watt panel puts out about 7.9 Amps, will lose most of its power through 100 feet of wire, and even if it didn't is not sufficient to recharge the 225 Amp hours of Trojan batteries. Nor is a 30 Amp TriStar needed for such little current. I would hope you are planning on upping the panels to three and putting them all in series to overcome those problems.
Question #1: there's no such thing as wire that is too large unless it won't fit the terminals or costs too much. 2/0 will handle about 200 Amps and your 1500 Watt inverter should draw 150 at maximum power & minimum Voltage.
Question #2: you need over-current protection (fuses or breakers) between the charge controller and battery and between the battery and inverter. Sized according to the wires needed to handle the expected current.
Question #3: the instruction/installation manuals for both the charge controller and inverter should contain important information about wiring as per manufacturer's specifications. Usually you can get these on-line before you buy anything so you know what you're getting in to. -
Re: Need help putting solar RV components together
Is your plan to put all those breakers in the "BigBabyBox"? According to the specs, it will only handle 4 breakers.Paul -
Re: Need help putting solar RV components together
John, looks like you've chosen quality components. But as Cariboocoot says, sizing is a bit off.Cariboocoot wrote: »Question #2: you need over-current protection (fuses or breakers) between the charge controller and battery and between the battery and inverter. Sized according to the wires needed to handle the expected current.
I have two T-105s, you're right, there's no way a 140W panel will charge them. I'm shooting for four 158W panels, though I think three would work most of the year. My two panels are doing fine right now during the height of summer, though. I'm only drawing 40-45 amp-hours per day. -
Re: Need help putting solar RV components together
You don't actually have to use an inverter at its maximum capacity. In fact most people don't. Reduce its size if you have no intention of increasing system capacity and/or if a smaller inverter will consume less for itself (tare loss).
Otherwise the maximum current hit any battery bank wants is about 25% of capacity momentarily (AGM's can take more). So a 225 Amp hour bank of flooded cells can expend about 56 Amps. Call it 50 for the conversion factor and tare and you get about 600 Watts on a 12 Volt system. The longer it is sustained the faster it is drained. A couple of hours at that rate and it will be dead (draw is not linear remember).
Just a rule-of-thumb; nothing concrete. -
Re: Need help putting solar RV components togetherCariboocoot wrote: »You don't actually have to use an inverter at its maximum capacity. In fact most people don't. Reduce its size if you have no intention of increasing system capacity and/or if a smaller inverter will consume less for itself (tare loss).
Otherwise the maximum current hit any battery bank wants is about 25% of capacity momentarily (AGM's can take more). So a 225 Amp hour bank of flooded cells can expend about 56 Amps. Call it 50 for the conversion factor and tare and you get about 600 Watts on a 12 Volt system. The longer it is sustained the faster it is drained. A couple of hours at that rate and it will be dead (draw is not linear remember).
Just a rule-of-thumb; nothing concrete.
I'm looking at a Xantrex 1000W true sine inverter. Don't plan on ever drawing 1000W from it, but need something to run my 600W food processor and couldn't find a decent 800W true sine. I'm currently using a 400W Cobra, but mostly use a little 150W inverter. My average draw is pretty low, rarely goes above 100W, and usually far below that. -
Re: Need help putting solar RV components togetherI'm putting together a small solar system in my tent camper. I have few questions about size cable, fuses, circuit breakers and layout. This is a list of materials I have:
* 1 kyocera 140 watt panel with MC4 connection and 100' 10AWG solarline cable.
* 1 Morning Star/Tristar MPPT-30 AMP controller.
* 2 Trojan T-105 batteries and 6AWG wire with connectors.
* 1 MidNite/BigBaby circuit. box and 1 12A & 5 30A CKT. breakers.
* 1 Samlex 1500 inverter and 2/0 welding cable.
* 1 Tri-Metric TM-2025-RV battery monitor and #18 wire.
* 1 500 AMP Shunt
My questions:
1-My 2/0 cable is too large for the Connection on the inverter?
2-Where do I place the circuit Breakers?
3-Where do I get a simple diagram for this system?
Make sure you look at the back of the inverter... The DC input terminal of samlex's SA-1500-112 inverter has a 9.5 mm tubular hole with a set screw. When using stranded cable, the cable end should be terminated with a pin type of terminal lug with width of lug < 9.5 mm and these pin connectors are not cheap or easy to find for 2/0 cable, I learned this the hard way unfortunately. I recommend getting samlex's PST-1500 version instead.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed