battery interconnector cable
System
Posts: 2,511 admin
What is the best gauge cable to connect two 105AH sunxtender batteries that will be next to each other in the same battery box?
Lou Dalessandro
Lou Dalessandro
Comments
-
Re: battery interconnector cable
You really need to supply the load that the batteries will be supporting... If the maximum load is 1 amp, a 3 amp fuse and 16 gauge wire would be fine.... If you need to supply 400 amps for starting diesel motor with glow plugs--16 awg wire is not enough.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: battery interconnector cable
The load to be supported is six 19watt compact fluorescent bulbs.
Lou DalessandroBB wrote:You really need to supply the load that the batteries will be supporting... If the maximum load is 1 amp, a 3 amp fuse and 16 gauge wire would be fine.... If you need to supply 400 amps for starting diesel motor with glow plugs--16 awg wire is not enough.
-Bill -
Re: battery interconnector cable
Here is a good link for wire current carrying capacity:
http://www.interfacebus.com/Copper_Wire_AWG_SIze.html
To figure out how much current you will need, use Power=Voltage * Current
So Voltage = 10 volts (minimum voltage a 12 volt battery will supply)
Power = 6 * 19 watts = 114 watts
current = P/V = 114 watts / 10 volts = 11.4 amps
NEC (US National Electric Code) requires a circuit to run at only 80% of capacity:
Current NEC = Current / 80% = 11.4 amps / 0.8 = 14.25 amps
NEC will allow 15 amps on 14 awg wiring... (note temperature of room, if conduit is used, etc. can affect your choice of wire)
For safety, you will also need to use a fuse/DC Rated Circuit breaker at the battery to prevent fires if there is a wiring short or lamp ballast failure... A 15 amp fuse/breaker should be used here.
Now, the above is a minimum design... Other issues that you should be aware off--if you are using an AC inverter to power the lights--then you would need to account for efficiency... Somewhere between 60-80%--that would change the current requirements from 15 amps to 15/0.6=25 amps rated wiring/fuse... Or ~10 awg wiring...
Next, you need to worry about how long the wires are... If the wire is running a few feet from the battery to an inverter--than this is not a big deal... You can use the wire gauge recommended...
However, if the wire is running 200' from the solar/battery building to the home at 12 vdc (no inverter), then the voltage drop can be pretty significant (and may prevent the lights from working correctly).
Here is an Excel spread sheet that allows you to estimate voltage/power drop for a run of wire (remember, a 200' run is actually 400' of wire)...
http://www.wind-sun.com/smf/index.php?topic=1477.0
Lastly, you also need to address the size of the battery charger too... If the battery charger is rated, for example, 30 amps, then the interconnect wiring will need to be rated for that current too.
At some point, if you will be doing a lot of solar/wiring for your home or cabin, you may want to pickup a copy of the NEC so you have the actual charts and requirements for home wiring.
Does this help or confuse?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: battery interconnector cable
Thanks!
Lou Dalessandro
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed