How to change a 220vac single phase out put to a 220 split phase
Lapeart
Registered Users Posts: 7 ✭✭
I have a inverter with has a 220 single output but my house uses 220 split phase
Re: How to change a 220vac single phase out put to a 220 split phaseI have a inverter with has a 220 single output but my house uses 220 split phaseSMA SB 3000, old BP panels.
A couple of things to think about...
Many 220 VAC inverters are 50 Hz, not the North American standard of 60 Hz... What is your inverter's output vs what is your needs?
Inverters should be sized to your loads... Peak Watts, average watts, starting surges, etc. Too large of AC inverter, you may have 20-40+ watts of losses just turning the inverter on.
Your battery bank should also be sized to your loads (and how much charging current/energy you can get per day). Too large or too small of battery bank will cause problems.
Adding a transformer to change from 220 VAC to 110 VAC can waste upwards of 5% of your power usage. And if you have 50 Hz inverter, you have to find a 50 Hz transformer (or derate your 60 Hz transformer).
Re: How to change a 220vac single phase out put to a 220 split phaseAnd if you have 50 Hz inverter, you have to find a 50 Hz transformer (or derate your 60 Hz transformer).
A 240V 60Hz transformer cannot in general be used with 240V 50Hz. But it can be used with 200V 50Hz.SMA SB 3000, old BP panels. -
Re: How to change a 220vac single phase out put to a 220 split phaseIf the transformer is limited by core saturation, you will have to reduce the input voltage to use 50 Hz, not just reduce the available power handling capacity.
Of course the 50 Hz Voltage 'standard' is 230 and quite often lower (as per the 220 rating the OP used).
In reality you can indeed use a 240 VAC 60 Hz transformer with 230 VAC 50 Hz. It's not very efficient and the power rating must be lowered as Bill said. You will lose not only the 4-5% the transformer consumes but an additional 12% minimum in power capacity. Most people will never notice this on account of not running near the peak of the transformer's capacity. That helps a lot. -
Re: How to change a 220vac single phase out put to a 220 split phaseCariboocoot wrote: »Of course the 50 Hz Voltage 'standard' is 230 and quite often lower (as per the 220 rating the OP used).
But a separate issue the 20% greater magnetic field can put the transformer at or beyond the saturation flux of the iron core. If this happens, the current can run to six or more times the design current because the inductance of an air coil is much lower than the inductance of an iron cored coil. It is this non-linear and very large current that I am concerned about.
The effect on the core would be the same as running the transformer with 290V 60Hz on the primary instead of 240V 60Hz. Not many transformers are designed that conservatively and I would not risk it without checking with the manufacturer of the transformer in question.
(The saturation of a transformer is related to the V/f ratio of the applied voltage. Check this out on the Mike Holt Forum if you are not convinced.)SMA SB 3000, old BP panels. -
In the real world it works for exactly the reasons I mentioned.
It just isn't great. -
Re: How to change a 220vac single phase out put to a 220 split phaseCariboocoot wrote: »In the real world it works for exactly the reasons I mentioned.
It just isn't great.SMA SB 3000, old BP panels. -
Re: How to change a 220vac single phase out put to a 220 split phaseAll that I am saying is that it may work for all of the transformers that you have tried, but that does not mean it will work for all transformers. And if it does not work, the consequences for the transformer will be catastrophic.
Don't buy junk.
Know what you are buying.
Problem solved. -
Re: How to change a 220vac single phase out put to a 220 split phaseCariboocoot wrote: »Don't buy junk.
Problem solved.
Different problem solved.SMA SB 3000, old BP panels. -
Re: How to change a 220vac single phase out put to a 220 split phaseAlways buy 130V light bulbs, because the line voltage may go above 120V sometimes.
Well I've had a 150 VAC line meter fry from grid Voltage surge so your "130 Volt" bulbs may not always save you. No matter how many problems you think you've got covered, someone always dreams up a new one.
The company I worked for built, among many other things, transformers. Never did one of them get dumped on my desk with the "tell us why this failed" question (that was my job; analyze device failures). They were quite robust and could take enormous amounts of abuse. I would not be at all surprised to find "overseas" autotransformers these days rated as "4kW" which would cook at 3: seems they rated things on a basis of <1 sec application.
So if you have 50 Hz power the best choice is to get a 50 Hz transformer. The second best is to get a good quality 60 Hz unit and understand that you need to derate it 20% and that it will run hotter, shorter, and buzzier. -
And slow down here a bit... The orginal poster has yet to return.
I was guessing that he may have a 50 Hz 220 VAC inverter (220 VAC native output inverters are not very common in the US)--I do not know.
ok i just our the outback auto transformer. anyone have a wiring diagram to configure this -
the inverter is 220 60hz. it a Canadian box -
Re: How to change a 220vac single phase out put to a 220 split phasethe inverter is 220 60hz. it a Canadian box
In that case we've been discussing the wrong thing. No problem getting split phase 220 VAC from that using a standard autotransformer.
The wiring is simple. Transformer has four connections: L1, L2, N1, and N2. The two Neutrals are connected together (and usually grounded). L1 and L2 go to the inverter output @ 220 Volts. 110 VAC will be available from Neutral and either L1 or L2.
What inverter is this, exactly? The power standard here in Canada is 240 VAC 60 Hz, the same as in the USA. We sent little red trucks out to change everyone's motors back in the 1950's and switch from 220 VAC 50 Hz then. No, seriously; we did.
BTW over the years the 'standard' Voltage in North America has been listed as 220 and 240 (with household Voltage being 110, 115, 117, 120, 125, 127 et cetera) and they are usually interchangeable.
Europe has 'adopted' 230 VAC 50 Hz as standard by broadening the acceptable range of Voltage. I think it's -6%/+10% or a range of 216 to 253. Pretty wide range. -
Outback has a nice set of manuals/application notes:
http://www.outbackpower.com/outback-products/integration-hardware/item/autotransformer
- 230 Forum & Website
