Hello all, I currently have an 85 watt kyocera charging batteries, inverted then supplying all my lighting. I am now wanting to produce more power and supply my wall sockets. However, moneywise watt for watt the larger panels (200 watt) are cheaper. I am aware of the differing voltages, but wondered why some inverters only allow strings of exactly the same panels. Why can't they be mixed, (or indeed can they?). I was hoping to add 1 more 85 watt 12 volt panel rig them both for 24v and add a 200 watt kyocera @ 24v and link them up giving me 370 watt at 24 volts? (adding more at a later date). Thanks all.

dan the man

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Solar Panel Ratings

    Basically, it is a matter of cost vs efficiency with mixing panels (and, to a degree, it depends on the solar charge controller)...

    A solar panel puts out (roughly) a fixed voltage when the sun is shining and a variable amount of current directly porportional to the amount of solar radiation striking the panel (brighter sun, more current).

    Looking that the basic electrical equations:

    Power = Voltage * Current

    So, if you have two panels in parallel, the one with the lowest voltage (at maximum power) will pretty much set the voltage point, and the two currents will simply add:

    12 volt 5 amp panel + 24 volt 2.5 amp panel (60 watts + 60 watts = 120 watts) when connected in parallel become:

    12 volts * (5 amps + 2.5 amps) = 90 watts -- or you have lost about 30 watts from the 24 volt panel because of this...

    And, if you connected them in series, the current supplied will be limited by the smaller panel:

    (12 volts + 24 volts) * (2.5 amps) = 90 watts -- again, a loss of 30 watts

    Of course, nobody would normally connect a 12 volt with a 24 volt panel together--usually the differences in voltages and currents are much less (and the "losses" are less too)... I just used the above as an example.

    In the case of mixed 12 and 24 volt panels, you could (depending on controller and battery voltages) connect two 12 volt panels in series (for 24 volts) and connect those in parallel with one 24 volt panel:

    (12+12v)*5a + 24v*2.5a = 120 watts... Or full power from all panels.

    There are more details to discuss with MPPT controllers (maximum controller voltages and currents) and such--how much detail do you wish to go into?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Options
    Re: Solar Panel Ratings

    dan,
    you can do it if you somewhat match up the voltages and that is not a match. what's worse is that you won't be able to use the 200w kc200 at 24v because its voltage is NOT high enough to be of use in a 24v system. the vmp has to be much higher than the top base voltage of the batteries and that is not going to be 24v, but more on the order of 29v depending on the battery type used. then there are other losses too through wiring and even the controller itself. hot temperatures also can lower the output voltage seen from pvs.
    do know that just by adding another pv doesn't mean you can put it to to ac outlets in your house. you need an inverter that can tie to the grid which is no small expense along with other items like switches and such. the solution is to have different looking outlets you can wire in dedicated to just your inverter.
  • System2
    System2 Posts: 6,290 admin
    Options
    Re: Solar Panel Ratings

    Thanks bill and neil for your replies. with regards to the mixing of panels, an example of what i meant was that ive seen certain inverters saying to use only module strings of the same type as in for example, if you use a sharp 65 watt you can only use sharp 65 watts for the whole string. I am aware that i require a good inverter my current one needs replacing, been researching a new one for about 4 weeks now, but there are so many to choose from. I was nearly sold on the powermaster combi sl, but the 1500 price tag put me off a little. it has a charger for the batteries which i don't really need and probably accounts for about a third of the pricetag. I am now contemplating the studer aj2400. Is this a good idea? reading up on all the performances it seems one of the better ones.

    the studer si looks pretty good but again i think the pricetag goes into making such a large surge power- again something i don't really need.

    Bill, i'm a little confused with the 24 volt panel being unsuitable for a 24 volt system. i understand the p=vi had to use it a lot lately, but i think the 24 volt panel mentioned, though 24 volt has an open circuit voltage of about 29? am i getting my wires crossed?

    with regards to the panels, is it better for me to stick to the same ky 85 watt panels? even though watt for watt they cost more? many thanks again.

    dan the man
  • System2
    System2 Posts: 6,290 admin
    Options
    Re: Solar Panel Ratings

    sorry forgot to mention, i am in the uk, i have a steca pr2020 controller charging 5 12 volt batteries (1 elecsol 270, and 4 37 ah akasa gels). I invert this currently with a 600 msw inverter (which is rubbish- hence the new one i want), and that supplies all my lighting very easily (don't even notice a drop in battery voltage at the end of the night, as i don't use very much). alot of power i produce is wasted as the batteries are pretty much fully charged within an hour or two. So i want to put this extra power to use around the house and then supplement what i have with a few more batteries and panels. i know this won't fully cater for my needs, but i am still grid connected for my big energy drinkers, and it will make a difference. i can currently connect a lead to my inverter and run it to some appliances <600W. However as it is modified it makes my lights and certain equipment buzz (hence the studer aj2400 pure sinewave).

    Dan the man
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Solar Panel Ratings

    Dan,

    Actually, it was Niel that typed about the 24 volt panels... But I can probably answer the question.

    Think of the solar panel as a battery with a certain load and voltage profile (IV curve). And you have the load, typically a lead acid type battery. Between the battery and the solar panel is the solar charge controller.

    Working backwards, the Lead Acid battery needs certain voltages (with supporting current) to charge quickly and fully. Also, flooded cell lead acid batteries can use a function called equalization which is a higher voltage that causes hydrogen and oxygen gas to form on the plates which ensures that each cell is fully charged, and the movement of the bubbling gases mix the electrolite which can stratify (acid is heavier than water and tends to sink in flooded cell batteries--particularly tall batteries).

    If you look up the tables for lead acid batteries, at a particular voltage they will list a required voltage for that mode (bulk charging to quickly recharge, float charging at a lower voltage to keep a battery charged without outgassing, and equalize, the highest voltage)... Also, as a lead acid battery gets warmer, these voltages drop, and as it gets colder, these voltage requirements rise.

    So, for example, to equalize one brand of 12volt battery, they ask for 15.2 VDC at 80F... If it is colder, that voltage will have to be higher, if it is warmer, the voltage will be lower.

    Now, there are several types of solar controllers out there. And they usually will need some voltage drop across them to cause current to flow and for them to function correctly. Say that 2 volts DC drop is a good minimum requirement. Now, you are looking at needed a solar panel that can output 17.2 volts DC. And that has to be 17.2 VDC at maximum power point--if that was 17.2 VDC open circuit, that is with zero current flow, so that does not help us.

    Also, as I said before, solar panel voltages drop with with increasing panel temperature. Those ratings are for 77F (25C?) ratings, and if you ever left anything black out in the sun for an hour, the temperature of those panels will increase dramatically.

    For example, a Kyocera KC80-02 (80 watt 12 volt panel) has a Vmaxpower = 16.9 Vdc... At 95F, that panel will only about about 13.2 volts... Not near enough voltage to bulk charge (say 14.2 vdc) or equalize a room temperature battery--let alone even run the solar charger properly.

    For a 24 Vdc battery system, all of the voltages need to double (except the controller which still only need a couple volts minimum)--So we are looking at needing 30.4+2=32.4 Vdc to equalize and 28.4+2=30.4 Vdc to charge a room temp battery.

    The KC 200 GT panel at 32F Vmaxpower is ~36 volts, but at 95F, it is 20.7 volts--way to low to charge a 24 volt battery with any standard solar charge controller...

    By the way, a great place to get the basic solar panel specs for almost any manufacturer is from Xantrex's solar planning site for their GT inverter:

    http://www.xantrex.com/support/gtsizing/index.asp?lang=eng#calculator

    You can also plug in temperatures to find out operating conditions and it give PTC (closer to actual ratings) specs.

    It is not that the KC 200 is a bad panel, it was just not designed, by itself, to charge a 24 VDC battery bank with a simple solar charge controller.

    There other charge controllers out there that are MPPT type controllers... These can take solar panel strings with much higher voltages and efficiently convert them down to the needed battery voltage.

    For example, use two KC 120's in series and you can charge either a 12 or a 24 volt battery bank with a MPPT type controller. For larger systems the MX-60 is a very popular (and not cheap) model.

    Also, Wind-Sun has a bunch of other MPPT controllers you can read up on (buying and shipping to UK may not make much sense).

    http://store.solar-electric.com/chco.html

    I will stop here for now--the post is long enough and I have to do some other things.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • System2
    System2 Posts: 6,290 admin
    Options
    Re: Solar Panel Ratings

    many thanks bill, I think i understand it now. better to series connect two 12 volt panels. could you advise me on the inverter situation? many thanks

    Dan the man
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Solar Panel Ratings

    Dan,

    Just to make it clear, just putting two "12vdc" panels together is not always the answer either... If you are using a "simple" solar charge controller, finding/wiring solar panels whose Vmaximumpowerpoint voltage matches the sum of the "worst case voltages over temperature and current" sum of battery voltage, controller drop, and wiring voltage drop.

    That is why when you look at 12 VDC panels, it is important to look at their Vmp and see that for battery charging designed panels, you may be looking at 19-20 vdc (not the 12 vdc on the panel name plate).

    Also, as you have seen in other threads, you have to look at the maximum voltage of the solar panel (Vopencircuit) at the coldest temperature you would expect in your area--connecting two 12 VDC panels together on a cold/sunny day may exceed the controller's input voltage range.

    Regarding inverters... I know that Europe has many manufacturers (and requirements) that would make more sense for you to purchase locally sold equipment that what is typically available in the US--So I will suggest a unit for you to read about (functions, user manual, etc.) so that you can better see what options are available as you look around... Also, there are others that would have better experience with inverters than I (by brand and model)...

    So, Xantrex and Outback are a couple of major manufacturers here in the US that make some interesting products.

    The SW series has about all of the options possible for an inverter (I am sure that Outback and other vendors also have similar products)... It can use AC line, has a battery charger, generator controller, can switch from AC input to its own "pure sine wave" inverter (like a UPS), it can sell power back to the utility, and lots of programmable options.. There are also 230 VAC @ 50 Hz models too. Its idle power is ~16 watts, but it also can scan for loads and have a standby draw of 1 watt...

    The only thing it does not have is an integrated wind/solar charge controller (you have to buy and install that separately).

    http://www.xantrex.com/web/id/47/p/143/pt/25/product.asp

    Of course, our host here sells many types of inverters here... Here is a long talk about inverters, the good and not so good, and the details to help you decide what to buy and install for your needs.

    http://www.solar-electric.com/solar_inverters/inverters_for_solar_electric.htm

    -Bill