sub panel wire/breaker question
The 12 panels are in 4 strings currently 80' from other equipment and feed the Flexmax 80 at 90-100 VDC, run in 8/2 with ground UF_B, That then goes to the 804 AH GB Industrial battery a few feet away. At the new house I have built a south south summer shade soffitt above the 8' high direct gain window wall which is designed to carry another future string of PV should we ever require. I have installed a 100 amp sub panel at the new house, planned to feed it from a 60 amp breaker in the first panel and supply it with 6/2 UF-B with ground. Since the Inverter we have can only supply 3500 kv, I believe that wiring (6/2) will be adequate, 3500/120vac=29 amps. If we should however decide to add the extra string, and its own CC I might wish to consider a second inverter, In that case would the 6/2 be inadequate? I cannot find any heavier guage in UF-B so what should I do? I only want to did that ditch one last time! Inspections are not an issue out here BTW, and I have tried several times to connect with professional installers in the region and no one seems to be willing to go near a home built system. I suppose they have their own trust issues about giving paid advice. Don't blame them.
Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Re: sub panel wire/breaker question
So the question is: if you double up on the VFX 3524 will 6 AWG wire handle the combined current?
Well 6 AWG is good for about 70 Amps continuous so yes it would, and if there is a 60 Amp breaker on the line that would trip before the wire would fry.
But why do this? In addition to being able to stack VFX inverters in parallel you can also stack them in series, giving you 240 VAC split between two legs which is much like standard household wiring anyway. Then you would run an adequate (8 AWG) 3 wire conductor to the panels from the inverters and no concerns about >30 Amps on it anywhere. Just another way to achieve the same total power.
With 1970 Watts your FM80 will be putting out a bit over 60 Amps to that 800+ Amp hour battery. If I were you I'd max out that array and controller first before thinking about second controllers or inverters. -
As Cariboocoot points out, when you want to push more power through a given conductor, raise the voltage. If you get another inverter and stack it in series to make 240 volts split phase (as Cariboocoot suggested), you can still use your 2 conductor cable, but you lose the split phase and will need a transformer at the house to drop the voltage back down to 120 volts.
In some situations you may be better off with single phase power. 240 volt split phase power likes to have its two 120 volt legs as balanced as possible. The transformer balances the split phase power so that there is only one, single phase leg at the house.
Re: sub panel wire/breaker questionCariboocoot wrote: »So the question is: if you double up on the VFX 3524 will 6 AWG wire handle the combined current?
Cariboocoot I had not thought of that at all AND I LIKE IT! But I did think that I would need to add a second controller for the new string, Is that not correct?Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Re: sub panel wire/breaker questionCariboocoot I had not thought of that at all AND I LIKE IT! But I did think that I would need to add a second controller for the new string, Is that not correct?
An FM 80 can output 80 Amps @ 24 Volts, or basically the power from 2500 Watts of array. -
Yes, well I made space at the shade soffit for 6 ea 245-250 watt panels, ( thinking Solar Worlds) which puts me beyond reach of the FM 80, but I have a spare FM 60 which I think would handle the extra 1500 watts. So as to construction, if I understand correctly That ditch I have to dig needs a run of 8/2 from each array to controllers, ( 2 runs) and one run of 8/3 with ground between the load center and sub panel. I should add the extra array and controller ASAP, and when the funds allow add a second VFX 3524 in series. Basically now all I have to buy is the wire, the 6 panels and combiner as well as the extra cables to the battery of course. Is that what I'm hearing?Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
When I priced uf wire it was similar in price to running conduit with wires in it, and the conduit will give you more options in the future. -
Re: sub panel wire/breaker questionWhen I priced uf wire it was similar in price to running conduit with wires in it, and the conduit will give you more options in the future.
Another thing to consider is if you want to have a battery moniter in your house, or any other gadgets? I was told to put mine in a separate conduit so I didn't get interference from the power wire -
OH s!!!, I had not thought of that either, but that control wire could lay in a 3/4 pvc conduit in the same ditch? BTW thanks!Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Yeah I put my trimetric wire and cat 5 cable for my inverter remote in a seperate conduit in the same trench
- 194 Solar Information links & sources, event announcements