I am running a 50 ft romex 12 volt wire to the inverter for my desk top computer and monitor but tries to start but wont?
what can I do to fix this problem? Thanks
what can I do to fix this problem? Thanks
Comments
-
Re: Can't get desk top computer to work with inverter?I am running a 50 ft romex 12 volt wire to the inverter for my desk top computer and monitor but tries to start but wont?
what can I do to fix this problem? Thanks
. -
Re: Can't get desk top computer to work with inverter?
What BC04 said... It sounds like your DC cabling is not cable of bringing the needed current to the AC inverter. For example:
300 watts * 1/0.85 inverter efficiency * 1/10.5 volts inverter cutoff = 33.6 amps @ 12 volts DC
33.6 amps * 1.25 NEC derating = 42 amp branch circuit+breaker/fuse
Using the NEC (national electric code), you would need >~8 awg cable to carry that amount of current safely.
12 AWG cable carrying 33.6 amps 50 feet, using a generic voltage drop calculator, will have ~6.4 volts drop at the DC input to the AC inverter.
Of course, if you are not using a 12 volt battery bank, the calculations will be different, and the voltage drop will be less.
In general, with power systems, the AC inverter and Battery bank should be located very close to each other using heavy cabling (sized for the DC current) and use a fuse/circuit breaker to protect against short circuits. The "long wire runs" would then be sent out at the higher 120 (or 230) VAC circuits. Sending low voltage/high current DC is difficult and would use a very large diameter copper cable to keep voltage drops manageable.
Welcome to off grid solar power design... These "gotcha's" are every where. We suggest that you tell us your loads/power needs, and we walk through a paper design (or three) before buying the hardware to make sure all is done correctly/safely first.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Can't get desk top computer to work with inverter?
Welcome to the forum.
Desktop computer & monitor = 200 Watts. 200 Watts on 12 VDC = 16 Amps (not including inverter consumption or conversion loss). V-drop on 12 gauge across 50 feet with those specs: 2.6 Volts or 21%. By the time the power gets from the battery to the inverter the Voltage isn't high enough and the inverter won't run.
Solution: shorter distance or larger wire. I'd suggest the shorter distance, as with the example above you'd be running at least 2 AWG to keep the Voltage above LVD on the inverter. 50 feet of that would be quite expensive. -
Re: Can't get desk top computer to work with inverter?
Well Thanks to all of you fine folks out there I now know what to do thanks again:O) this thread is done.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed