PV Circuit Breakers ?
verdigo
Solar Expert Posts: 428 ✭✭
Is there any reason for a combined + circuit breaker from a combiner box to the charge controller. The reason I'm asking is the E Panel I have shows one but the combiner has breakers for individual strings already.
Dennis
Dennis
Re: PV Circuit Breakers ?
Convenient method of disconnecting the array as a whole. That's about it. -
So isc times the number of strings times 1.56 to get the rating for the breaker? -
Re: PV Circuit Breakers ?So isc times the number of strings times 1.56 to get the rating for the breaker?
That should keep the government happy, yes.
Thank you Mr. Coot.