newbie help / suggestion
kc6cnn
Registered Users Posts: 22 ✭
Is there a sticky somewhere that explains all of the calculations needed to figure battery bank size, panel size, etc.
I was trying to figure out what my needs would be and how to meet them, but keep getting confused on watts, amps, voltage calculations.
Thanks
Gerald
I was trying to figure out what my needs would be and how to meet them, but keep getting confused on watts, amps, voltage calculations.
Thanks
Gerald
Comments
-
Re: newbie help / suggestion
Gerald,
Just ask the question right here in your thread. I/we will go through the calculations based on your needs.
I think it will make more sense to you if we discuss your system vs a generic version. Many of the choices for battery voltage/hardware/etc. will be different based on system size/power needs/location of install. To discuss a "generic" installation will get even more confusing because of discussions of the options/variations.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: newbie help / suggestion
like they said on Dragnet Just the facts, M'am, just the facts... so start with a list of the items you want to run and the watts they use and the time (hrs) they are used
ie 4 CFL lights at 9 watts = 36w x 4 hours = 144 Whrs.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: newbie help / suggestion
I am thinking that would be useful sticky as well. The general consensus is to buy a kill-a-watt meter and determine your load requirements, then do some conservation, then build a balanced system based on what you use with the idea that your gonna want to use more as time goes on. My problem is that as a DIYS kind of guy with limited time and resources I would never get anything done that way, so with the knowledge that almost all loads have an off and on switch I figured I would just shoot for a 3 KW or so system built with expandability in mind and just go for it all the while reading thousands of threads to hopefully apply all of that expertise to do what I have in mind, which might change at any given moment. A short concise sticky with formulas, rules of thumb, and safe practices would be great, but there would always be something left out. There just aren't any short answers with this stuff. -
Re: newbie help / suggestionIs there a sticky somewhere that explains all of the calculations needed to figure battery bank size, panel size, etc.
I was trying to figure out what my needs would be and how to meet them, but keep getting confused on watts, amps, voltage calculations.
Thanks
Gerald
i don't mean to sound rude, but how did you get to be an extra class ham and say something like that? -
Re: newbie help / suggestion
I was mildly dyslectic when I was a kid... So I know how the V/I/A/W etc. all floated around on the paper for me (as well as numbers and words).
I probably got much better in math from high school Chemistry (and Physics) classes when I was "forced" to carry units through all of my calculations. It made reading the equations much easier and understanding conversions/catching missing/wrong numbers&units much easier too.
I wrote a post recently about how I try to make the math more understandable on the forum.Thank you Rob... I really did try and figure out how to make the equations "readable"... To compare other ways of writing equations:
174 Watts * 5 hours per day * 1/0.85 inverter eff * 1/24 volt battery bus = 42.6 Amp*Hours @ 24 VDC
Why do I use 1/0.85 and 1/24? Because we recognize the numbers... Plugging in straight numbers would look like:
174 Watts * 5 hours per day * 1.17647 inverter fudge factor * 0.04167 volt-1 battery bus = 42.6 Amp*Hours @ 24 VDC
That is a silly representation. Another would be:
(174 Watts * 5 hours per day) / (0.85 inverter eff * 24 volt battery bus) = 42.6 Amp*Hours @ 24 VDC
Which is the correct way to write the equation--With Parens to ensure the correct order of operations. But I think it sort of "groups" variables together in non-useful relationships (i.e., is Inverter Eff and Battery Bus Voltage somehow related--Not really).
And if I took out the "words" and did it the way my Math and Science Teachers taught:
(174W * 5H) / (0.85 * 24V) = 42.6 AH
It gets the units right (always useful cross check for engineering/sciences)--But sort of difficult to really get a "feel" of what is happening in "real life" system.
Then there is the "algebra" version:
P = Average power in Watts
T = Hours per day of average power
E = Typical inverter efficiency (in percent)
B = Battery Bank Nominal Voltage
C = Bank capacity in AH @ battery voltage
C=(P*T)/[(E/100)*B]
Where:
P=174 Watts
T=5 Hours
E=85%
B=24 volts
C=Results in AH
C=(174W*5h)/[(85/100)*24V]=42.6AH
Liking my "English Math" sentences any better yet?
Equations written as above are much easier to put in a spread sheet--But I think do a poor job of conveying the ideas behind why the equation does what it does.
And I now see way I was a "C" student in middle school math. :roll: English too... Another story (or not).
-Bill
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: newbie help / suggestionI was mildly dyslectic when I was a kid... So I know how the V/I/A/W etc. all floated around on the paper for me (as well as numbers and words).
I was also dyslexic as a kid. I owe my ability to read to the efforts of my mother who joined the support group D.A.M. (mothers against dyslexia).
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: newbie help / suggestion
he can talk for himself and don't need the 2 of you to make up possible excuses for him.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed