Calc's seem reasonable?

Options
Rkg76
Rkg76 Solar Expert Posts: 35 ✭✭
So far all I have done is purchased some panels ( 10 - 200w 24v panels for $0.80/watt) thought that was a decent deal!?!?

These are the loads I am expecting to run at my offgrid cottage (already have a propane fridge but would like to add an electric fridge as well, need more room for beer!! :)

Now I realize this is an approximation at this point, I will run all this through a Killawatt meter before I finalize things, but wanted to know if I am headed in the right direction here.

We use the cottage from May until October, usually three day weekends and them might spend up to 2 weeks straight there for one stretch during the year. I might go out there for a couple of weekends in the winter but not too concerned about that.
Attachment not found.

Power Hours Days Watt-hours
used at used per per week
Appliance/Loads Watts one time in a day week (DxFxG)

Lights
Bedroom 1 15 15 0.5 3 23
Bedroom 2 15 0.5 3 23
Bedroom 3 15 15 0.5 3 23
Bedroom 4 15 0.5 3 23
Kitchen 11 11 4 3 132
Living Room 11 1 3 33
Dining Room 11 11 4 3 132
Outdoor 15 1 3 45
Bathroom 11 11 0.5 3 17
Hall 11 0.5 3 17

TV 140 140 6 3 2,520
Bedroom Fan 60 8 3 1,440
Bedroom Fan 60 8 3 1,440
Living Room Fan 60 60 8 3 1,440
Satelitte Rec 25 25 6 3 450
DVD Player 25 2 1 50
Coffee Maker 1200 1200 0.2 3 720
Toaster 1200 1200 0.1 3 360
Microwave 900 900 0.2 3 540
Fridge 60 150 24 7 10,080

Inverter Sizing 3738 19,505 WH/Week
1.25 Gross up by 25%
24,381
7
3,483 WH/Day

So does the above seem legit? Am I missing or not thinking about something here?

On a 24v system how many batteries would I be looking at here to run all this? In the summer months based on what I have seen on a full sunny day (which we get a lot of) I would get 7-8 hours of sun on the panels.

Currently just run a honda EU3000is that is often just powering the TV and Sat most of the time (have a 4 year old who likes cartoons!!)

Any input is always appreciated, I am always amazed at the knowledge that many of you have on this forum!

Thanks
Russ

Comments

  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    Sorry looks like copying and pasting from excel doesn't look so nice! I attached the actual file...
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    Cutting and Pasting Columns sometimes looks better if you use "Go Advanced" and the "#" button.

    It pasts {code} and {/code} (using [] instead of {}) -- This will better keep the Tabs and Spaces.

    Here is an example of QUOTE tags (note, I pasted output to NOTEPAD and copied back to get rid of the formatting:
    Month Solar Radiation
    (kWh/m 2/day) AC Energy
    (kWh) Energy Value
    ($)
    1 3.62 329 41.12
    2 4.59 378 47.25
    3 5.22 479 59.88
    4 6.11 535 66.88
    5 6.36 575 71.88
    6 6.47 565 70.62
    7 7.01 629 78.62
    8 6.67 596 74.50
    9 6.62 568 71.00
    10 5.41 485 60.62
    11 3.87 338 42.25
    12 3.35 306 38.25
    Year 5.45 5784 723.00

    vs CODE tags:
    Month    Solar Radiation
    (kWh/m 2/day)    AC Energy
    (kWh)    Energy Value
    ($)
    1      3.62          329        41.12   
    2      4.59          378        47.25   
    3      5.22          479        59.88   
    4      6.11          535        66.88   
    5      6.36          575        71.88   
    6      6.47          565        70.62   
    7      7.01          629        78.62   
    8      6.67          596        74.50   
    9      6.62          568        71.00   
    10      5.41          485        60.62   
    11      3.87          338        42.25   
    12      3.35          306        38.25   
    Year      5.45          5784        723.00    
    

    And here is a paste with formatting directly into the edit window (with WYSIWYG turned on--The A/A button in upper left of edit menus):




    Month
    Solar Radiation
    (kWh/m2/day)
    AC Energy
    (kWh)
    Energy Value
    ($)


    1
    3.62
    329
    41.12


    2
    4.59
    378
    47.25


    3
    5.22
    479
    59.88


    4
    6.11
    535
    66.88


    5
    6.36
    575
    71.88



    6
    6.47
    565
    70.62


    7
    7.01
    629
    78.62


    8
    6.67
    596
    74.50


    9
    6.62
    568
    71.00


    10
    5.41
    485
    60.62


    11
    3.87
    338
    42.25


    12
    3.35
    306
    38.25


    Year
    5.45
    5784
    723.00




    You sometimes have to play around to make it work...

    Anyway, your image post did work.

    3.5 kWH per day is a good sized load... And would be fairly expensive to run off of solar 100% of the time--Although, during summer does make it a bit more doable.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    The fridge is a big part of the 3.5 kWH/day which I don't necessarily need to have and I calculated as it running 24/7 even though we are not there 4 days a week and it would likely just be keeping drinks cold. So could probably put it on a timer or something so it is off when we are not there??
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    Anyway, using Winnipeg Mn. Canada in PV Watts with fixed array set to -15 degrees from latitidue or ~35 degrees from horizontal (summer setting):
    Month      Solar Radiation (kWh/m2/day)
    1      3.01     
    2      4.07     
    3      5.27     
    4      5.74     
    5      6.32     
    6      6.35     
    7      6.43     
    8      6.05     
    9      4.62     
    10      3.58     
    11      2.42     
    12      2.57     
    Year      4.71      
    

    Pick May through September wiht 4.62 hours minimum sun (run generator some more during last month):

    Battery sizing for 1-3 days of storage (pick 2 days as optimum) and 50% maximum discharge (for longer battery life):
    • 3,483 WH per day * 1/0.85 inverter efficiency * 2 days storage * 1/0.50 max discharge * 1/24 volt bank = 683 AH battery bank @ 24 volts

    To charge such a battery, we recommend from 5% to 13% rate of charge from solar:
    • 683 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.05 rate of charge = 1,286 Watt array minimum
    • 683 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.10 rate of charge = 2,572 Watt array nominal
    • 683 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 3,344 Watt array "cost effective maximum"

    And, assuming a minimum (long term average) of 4.62 hours of sun per day:
    • 3,483 WH per day * 1/0.52 overall system efficiency * 1/4.62 hours of noontime sun per day = 1,450 Watt array minimum

    So, the recommended array for a "nominal 2 day battery with 50% max discharge" and an array that would carry you from February through September would be around ~1,450 to 3,344 Watt array--With ~2,572 being a really nice "nominal array" that would give you:
    • 2,572 Watt array * 0.52 system efficiency * 3.58 Hours of sun in October = 4,788 WH of sun per day

    So, that would still exceed your minimum daily estimated power requirement.

    I am still not sure if you calculated the numbers exactly correct... I will have to take a closer look--But a 3.3 kWH per day system is a pretty nice amount of power for a "near normal" off grid home, running efficiently.

    If you were going "bare bones", you could look at 1,000 WH (1 kWH) per day, and see what you would dump.

    Now--For off grid systems that are used less than ~9 months a year, a smaller off grid system with "generator support" may be a possible option.
    Poster ChrisOlson (and others) has some good advice here for "swimspam" :

    Choosing a good generator
    genset alternator failure (and if your generator is not generating AC? What to look for/do--Thread started by "Unicornio" from Spain)
    Demonstration of Generator Support (A couple inverters that will share AC loads with the generator--smaller generator with large load support)

    End result--you get what you pay for.

    Basically, use the battery+inverter for nights and daytime "minimal" loads. And use the generator when more power is needed (cooking, evenings at home with everything turned on).

    With Generator Support, you can use a smaller generator too--The Off Grid inverter (with generator support feature) will let you use a relatively small genset and supply surge power as needed.

    Larger generators are more fuel efficient (kWH per gallon of fuel), but if all you need is ~1,000 watts or less of continuous power (running lights, TVs, computers, fans, etc.) on average--A smaller genset can save you fuel costs overall.

    I.e., Running a 1,600 watt Honda eu2000i at 400-1,000 watts for something like 9+ hours ot 5+ hours per gallon--Vs running an 8 kWH diesel set at 1,000 watts at closer to 1/2 gph (plus seriously under loading the generator which can create its own problems) or using even more fuel with a gasoline genset running at light loads.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    Thanks Bill!

    Did you notice I had already added a 25% inefficiency factor to my required daily watts? Or had you seen that? In other words my true calc would have shown approx 2,800 watt hours per day

    Russ
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    Refrigerators are a wild card... You can get some that are down on the 1.2-1.8 kWH per day average range (hot weather more, cold weather less).

    If you can use a chest freezer setup as a refrigerator, you can get down towards ~0.250 kWH per day... Of course, most spouses do not accept moving baskets around for refrigerator use.

    If you are there near full time--Then an electric fridge is probably going to be a good solution (with larger PV system). If not, then a propane fridge may be the better way to go (at least until you move their full time).

    For most systems, it the smaller loads that run 24x7 that really drive up overall power consumption (fridge, freezer, computer running 24*7, DVR's, Sat Receivers, etc.). Turns out that running a 1,500 watt microwave 20 minutes per day is not nearly as costly.

    Power usage is a highly personal set of choices--Just trying to make sure you have the right information for you to make your decisions--not trying to force you down any particular road.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    Russ,

    Sorry, I did not--There are several levels of "losses"... So, we have to be very careful where we plug them in. So--If you did a 25% for your electrical power, then, yes, all my above calculations can be sized down by 0.75 for the "correct" results.

    I try to explicitly put the deratings in the math, instead of in the data---Depending on how the power is used/generated/etc... The losses can be different.

    For example, my calculations assume pretty much that all power is generated by solar during the day and dumped into the battery bank. And that all power is used at night from the battery bank.

    If you have signicant power usage during daylight hours (say water pumping for irrigation, clothes washing, computer work), then battery usage could be less (less battery losses, smaller battery, etc.).

    Then on the downside--If you assume that you want to go through two days with heavy overcast (and computer is for work, so cannot stop use during poor weather, kids still need clean clothes, etc.), then all energy pretty much is coming from the battery bank--So worst case is still the best to plan too.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    Never any plans to move there permanently....it is a boat access place only and I am still 25 years out (at least!) from retirement. I just like the idea of producing my own power without the generator, even though in reality if I was just thinking about the money I would not even bother with solar power....I might spend $25 a weekend running my generator but I don't want to run it at night and would prefer to hardly run it at all!

    I have spent $1,600 so far on the panels and overall was thinking I would spend around $8k (doing the install myself).

    I am sure I could convince the wife to use a chest freezer as a second fridge no problem so that will be something to look at for sure!

    Russ
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    If you are going to use an Energy Star Refrigerator, you probably should plan on a ~3.3 kWH per day system capability.

    And, normally, you would never plan on using 100% of your predicted power per day--Probably closer to 65-75% of predicted power as your "base load"... This would allow for some overcast and when the kids start drawing more power than you planned.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Steve961
    Steve961 Solar Expert Posts: 93 ✭✭✭✭
    Options
    Re: Calc's seem reasonable?

    Russ:

    Bill did a good job explaining your options for a more energy efficient refrigerator. You're next highest loads are your TV and fans. You could save another 3,600 watt hours per week by moving to more energy efficient versions of these. Here are some examples:

    Casablanca 54-in Panama DC Snow White Ceiling Fan with Remote at 32 watts

    Samsung 50” LED TV at 52 watts (typical)
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    What would you consider the optimal battery bank set-up using your approx 680 amp hour bank, my initial plans were to just buy the cheaper 225 amp hour GC2 from Costco or a Sam's Club
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    Thanks Steve...those are just estimates I used, and I estimated high, I actually have a 32" LED so I am likely less then the 52 watts that you suggest is typical, and I have already purchased the fans, just not installed yet but they were quite expensive as far as fans go and are supposed to be energy star rated (not that that means too much)
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Options
    Re: Calc's seem reasonable?

    russ, your calcs are almost bang on mine for full time use.
    start with th gc2's, if you are going fla's, as you need a learner set.
    check out the 19 and 26 inch toshibas, they can get you down to 15 w, depending on model. our 19 even has a built in dvd but needs powered speakers vs built in 3 inch ones that even at 100% you had to sit within 2 ft to hear ...
    teaching tip, for the kids, if they want too much power to waste, put in a smaller fuse and wen it blows, you can explain what they did et and put the small one in again... Wife did that with the vacuum instead of the gen, ka blewy, Hey, what did I do?.... lucky we had another fuse.
    costco has some great 110v, 2w, listed as 4w, led chandelier lights in 3 packs ~ 21 bucks

    have fun
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?

    So if using GC2's at 225 amp hours I would need to run about 12 of them in three sets of four to get what I need at approx a 680 amp hour battery bank?
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Calc's seem reasonable?

    Yep--You got it (3*225AH=675AH for 3 parallel strings).

    You are between the rock and a hard place--Getting "cheap" training batteries that will last ~3-5+ years -- But 3x parallel strings is a lot of cells to check water level in (36 cells).

    Vs getting more expensive (larger) cells/batteries and getting it to 2 or 1 strings (24 or 12 cells to check for 24 volt battery bank). And they may last 8-10 years (+/-) with "better batteries".

    It is not uncommon for a new off-gridder to kill their first set or two of batteries--And/or a couple of years down the road to figure out that you need a larger or smaller battery bank. You would hate to make those mistakes 2-3 years into a 10 year bank.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Rkg76
    Rkg76 Solar Expert Posts: 35 ✭✭
    Options
    Re: Calc's seem reasonable?
    BB. wrote: »
    Yep--You got it (3*225AH=675AH for 3 parallel strings).

    You are between the rock and a hard place--Getting "cheap" training batteries that will last ~3-5+ years -- But 3x parallel strings is a lot of cells to check water level in (36 cells).

    Vs getting more expensive (larger) cells/batteries and getting it to 2 or 1 strings (24 or 12 cells to check for 24 volt battery bank). And they may last 8-10 years (+/-) with "better batteries".

    It is not uncommon for a new off-gridder to kill their first set or two of batteries--And/or a couple of years down the road to figure out that you need a larger or smaller battery bank. You would hate to make those mistakes 2-3 years into a 10 year bank.

    -Bill

    So based on this what do you think you would suggest...going with 12 GC2's that I could get for around $1,500 and have 3 parallel strings or spending closer to double that for 8 375 amp/hr L16's and running 2 parallel strings...I am thinking the 12 GC2's would be best at this point given I could buy another 12 and still be at the same price as the 8 L16's if I ended up killing the first 12 prematurely. I guess I am trying to figure out the cost/benefit of running 2 vs 3 parallel strings.

    As always any input is welcomed!

    Russ