Battery Bank cabling
Mike at Energy Commission
Mike at Energy Commission Solar Expert Posts: 50 ✭✭✭✭
I have searched to find, how to size the cables for a battery bank, (fusing and interconnecting batteries)? I find many articles and discussions about sizing the array wiring. I have 4- 6v golf cart batteries I want to combine into one 12v bank I have the massive 0/2 cables in series to create 2- 12v batteries, what size cable and fuse for the parallel connection? Thank you very much.
    Re: Battery Bank cabling
    My personal suggestion.
    For one string or two parallel strings, size the battery cables (and fuses) to the maximum sustained load (charging and discharging)...
    If you have a 2,000 watt 12 volt AC inverter, and want to run near 2,000 watts max continuous through it, that would be:
    • 2,000 watts * 1/0.85 inverter 1/10.5 volts inverter cutoff * 1.25 NEC derating = 280 Amp minimum fuse/branch circuit
    If you have three or more parallel strings, I would humbly suggest that you would rate, at a minimum, the bank wiring for 50% of maximum rated load (or charging) current per string.
    From the battery side--The most current you can pull from a flooded cell deep cycle battery "reliably" over all charge, age, and temperature conditions would be ~C/2.5 (recommended design limit for a reliable off grid system).
    A golf cart battery is rated at ~225 Amp*Hours, so:
    • 225 AH * 2 parallel strings * 1/2.5 maximum short term surge = 180 Amps
    • 180 amps * 1.25 NEC derating = 225 Amps "practical" current limit from suggested bank
  • vtmaps
    When you say you want to make the parallel connection, are you referring to "A" or "C" on the diagram? If you are referring to "A", I don't see why it needs to be any different than "B". If you are referring to "C", then Bill's (BB.) analysis is quite correct.
    vtMaps is correct,
    I got a little confused between designing for the Inverter side and the battery side--problem with "generic answers"...
    My recommended "practical" maximum current from a single battery would be:
    • 225 AH * 1/2.5 maximum short term surge = 90 Amps
    • 90 amps * 1.25 NEC derating = 112.5 Amps "practical" current limit from suggested bank
    So, from this bank, should you expect 90 Amps maximum surge/short term current or can you use 180 amps.
    If the batteries share 50% each--then 180 Amps... In practice, batteries and their wiring don't always share at 100%... And worst case would be 100% from the one "good string"...
    So, back to that is the maximum AC or DC load (or charging current) that is expected?
  • Mike at Energy Commission
    thanks, it would be connection A, so now to find tables with those ranges of amps and distances in the 16" range! makes sense about the C/2.5 being the limit for a reliable load. This explains why the wash machine stops a few minutes after starting- I think. This is just one of the reasons I want to bump up to 450 amp hr bank, now to size the cable for A connection.