westbranch
Solar Expert Posts: 5,183 ✭✭✭✭
I am wiring up an Epanel and need to add a couple of breakers & #6 ga. wires for my PV input, as per the Epanel manual.
The AC transfer switch is wired with THHN , so I was looking for that but I cannot source it locally.
Will RW90 be acceptable?
Similarly can I use #4 STW battery cable for the run to the Classic? the STW is slightly flexible rather than stiff, not floppy like car stereo wire of same size,
I am assuming that there would be minimum stress at the attachment points.
From US Wire & Cable
STW
Extra hard service cord. Thermoplastic constructed jacket. 600 volt, weather resistant for outdoor use.
It feels slightly (like) rubber coated as does CabTyre
The AC transfer switch is wired with THHN , so I was looking for that but I cannot source it locally.
Will RW90 be acceptable?
Similarly can I use #4 STW battery cable for the run to the Classic? the STW is slightly flexible rather than stiff, not floppy like car stereo wire of same size,
I am assuming that there would be minimum stress at the attachment points.
From US Wire & Cable
STW
Extra hard service cord. Thermoplastic constructed jacket. 600 volt, weather resistant for outdoor use.
It feels slightly (like) rubber coated as does CabTyre
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Comments
-
Re: Which type of wire to use in Epanelwestbranch wrote: »The AC transfer switch is wired with THHN , so I was looking for that but I cannot source it locally.
I think THHN is not available in Canada. When I bought Generac, which was made in the US, the wiring was THHN.westbranch wrote: »Will RW90 be acceptable?
I used RW90 for all my wiring. $2/meter in Home Depot. -
Re: Which type of wire to use in Epanel
I mentioned THHN to the guy at a commercial installers office here and he knew what I was after but no supply in 6ga. Others have RW90 in 4 ga and 8 ga but not 6...
ps we are in a HD desert, closest is 3 hr drive, one way.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Which type of wire to use in Epanel
Insulation type doesn't really matter in an enclosed installation. -
Re: Which type of wire to use in EpanelI think THHN is not available in Canada. When I bought Generac, which was made in the US, the wiring was THHN.
I used RW90 for all my wiring. $2/meter in Home Depot.
Use whatever has 90C rated insulation. These are 90C insulation types copy/pasting from the electrician2.com code calculator: AE cable, MC cable, NM cable, TBS, SA, SIS, FE, FEPB, MI, RHH, RHW-2, THHN, THHW (dry location), THW-2, THWN, USE-2, XHHW (dry location), XHHW-2, ZW-2. Most THHN sold in AZ are the slick easy-run type - very hard to bend. Wire and Cable 2 Go is cost competitive to contractor supply shops with heavy gauges bought in bulk (at least $1000 order total). -
Re: Which type of wire to use in Epanel
I spoke to a friend that works at EB Horsemans, the local electrical Wholesaler yesterday about THHN/W.
He looked it up and found that it is meant for TRAY use, hence why it is so rigid... and the specs are the same, 90* rated, just that the THHN has thinner insulating material, and a slipperier coating for pulling through conduits.
His recommendation (also) was use RW90 as it is designed for colder climates, that's why it is so common around here.
ECS wire states:
Single copper conductor with low temperature moisture resisting cross-linked polyethylene insulation
For open wiring and raceways (except cabletroughs and ventilated flexible cableway) in dry or wet locations.**
Rated 600 volts.
Meets CSA C22.2 N° 38-05
Minimum recommended installation temperature: minus 40 degrees Celsius (with suitable handling procedures).
Maximum conductor temperature: 90 degrees Celsius.
Sure wouldn't want to be doing that work at -40 (same temp on both scales)
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed